In most modern homes with up-to-date heating and air conditioning systems, filters are changed regularly through the year, so you may not even need to hire a professional. However, keep your eyes open for the accumulation of dust, dirt, dander and mold. If you see it despite regularly changing your filters it could be an indication you need a high-pressure cleaning.
Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.

The University of Virginia - 2005 / The Wharton School of Finance - 2016 / U.S. Naval Aviator 2005-2015. At All Systems Mechanical air conditioning and heating, we believe that the experience our clients have is every bit as important as the products they receive. Simply put, our results speak for themselves, and we'd be happy to help. If you're in the market for a new AC or furnace, make sure that you get a fair price! Try our online calculator; click the tab on the top of this page for more information.
I call to follow up at the end of the next day and she said that she has not been able to get in touch with the owner.  By this time, I am starting to get frustrated because I am starting to get the run around.  I question her if I am even on the schedule or if they attempted to schedule a crane.  She says they are extremely busy and that she does not know.  So I say, basically I have waited over 2 weeks and you have not put me on the schedule and I am at the end of the install line.  No answer.  I tell her to talk to her boss and find out what is happening, and I will think about what direction I want to move in at this point.  
They work less jobs, thus increasing profits – think about it…if they got only half of the jobs, then they only pay half of the money required to pay employees, expenses, etc., but still have the same amount of net profit. In fact, if you do the math, they actually make more profit that their competitors do…twice as much, once you factor in their savings form only doing half of the jobs at the same amount of profit (Total Revenue – (half the normal expenses) = twice the profit). In other words, they save money by doing half of the jobs as others, for the same profit, thus increasing their overall profits.

The sky is the limit. I am a big fan of adding zoning systems, but realize that this will typically add $2,300 to $3,500 (or more) to the price. “Why a price range, isn’t it just a part?” No, the part then has to be installed, and the customized ductwork required will vary based on the difficulty of the job and layout of your attic. It is very labor intensive, and most people don’t do it right. It should also include a bypass damper and ductwork! Simply put, the more you add, the more it will affect your HVAC installation cost.
As one of the duct cleaners that do it right it disgusts me to hear the horror stories some of my past customers have had with the companies using scare tactics, bait and switch schemes, and just plain intimidation to make a fast buck. The Ductz franchise as a whole has gone behind other "duct cleaners" in the last year to the tune of almost three-quarters of a million dollars. All of this expense could have been avoided had the customers been able to do some background research before hiring. NADCA is a great organization and should be a minimum requirement for finding a duct cleaner. Other great questions include "How long does the service take?" (2 techs, 4-5 hours for a small house, 7-9+ hours for a two system house), "Do you clean the entire system including all trunk lines and the air handler (blower motor and evaporator coil)?", "How do you validate the job you have done?" (before and after picture reports work great). Beware of duct cleaners that say their process will solve all your air quality concerns. Duct cleaning is one of several steps to take to rid your home of unwanted dust, dirt, mold, and other allergens.
I know it has to have a new concentric venting system installed, I believe it needs new plenums ( mine are rusty but both of these require extra work , so someHVAC persons are saying I do not need either!! RED FLAG THERE. Also, it will need a new drain using PVCP ?? Piping run maybe two, depending on where my evep coil drain is conected (here in TN they use to run them in with the septic lines, now they cannot be run through that way), Lastly I am not where or what these things do beides hold water but I was told It needs a filter rack and new filter base safety pan. THATSSS it that is all I know about this stuff aside from the fact that nothing up there is to code thus far LOL. !!

Important Tip: Don’t just pay attention to the high-end of the price range! – which is what I know you are all looking at, but also look at the low range. If a contractor is cheaper than this, ask “why?” Usually it is because they don’t have liability insurance, workman’s compensation insurance, are unlicensed, all of the above, or worst yet, they don’t use HVAC technicians. You are spending a lot of money.  Make sure that they are licensed (In California, check here at CSLB License Checker) and insured.

I need a complete system replacement , before I was trying to get an evaporator coil replaced , of course the price is between $2200 an $2800 , then get told it probably will over tax my ac unit within months , so now and like everyone else what do you buy 14 ,15 16 17 seer units ,price and how do we know its reasonable  why can't there be '" a estimated price ,in the ball park, a range of prices ,so we can at least go from their .....  Now it's from 7500 to 15000. Frustrating  from the start so everybody good LUCK.   Draw a # from the hat    Unregulated  and who do you BELIEVE, just like on NCIS go with your gut feelin   
One of the best ways to know if your ducts or vents need to be cleaned is to just check them. Your eyes will be able to check for indications of mold, dust or pollen buildup. You might also be able to smell the presence of mold, which would be a clear indicator. Ductwork will have some buildup of dust, since the return registrars pull air back in. However, this doesn't mean your ducts have too much debris, and you can easily clean them with a duster or vacuum.
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. My mom is located in Arizona and they trust J&M Restoration air duct cleaning company, they have an A+ BBB rating, they used EPA approved sanitizing agents, their technicians are NADCA certified, and the company is certified by the Institute of Inspection, cleaning and Restoration. Make sure to shop around and get written estimates first.

It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
A house breathes just like you an I.For example every time your clothes dryer comes on it automatically creates a negative pressure inside the home.So if air goes out of the living area it has to be replaced.....now look above the ceiling fan ....you see the cover...underneath that is a hole straight to your attic....Now the stuff on your ceiling fan you call dust...call it insulation,rat fecies or anything else that is in your attic that could be pulled in your due to a negative pressure.
An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.
I just bought a home, and the sellers clearly never had the air ducts cleaned. This is, unfortunately, typical of their neglect of the home, so I am not surprised. I was cleaning around the wooden floor registers, and I took the registers off. I found nests of some sort...all kinds of really gross stuff!! I am calling now to schedule duct cleaning for my new home. Anyway, it is very easy to check to see if you really need duct cleaning. Remove the floor registers and use a flashlight if necessary to see if there is dust or debris in the ducting. If these look bad, I'd definitely have the system cleaned. I would also do it after a construction project, after installing a new furnace, etc. I have found that once I had my previous system cleaned, it seemed to remain spotless for 3 years. So it seems that if you just change your filters on time (I have an iPhone alert set for every 3 months), the system will stay clean for years. Hope this helps!
Duct cleaning is a band aid, like washing you hands is. Under your description, why wash your hands more than once? If it gets cleaned once, it shouldn't get dirty again. Well that is, unless they touch something dirty. Keeping your hands completely clean is virtually impossible. Same as keeping dust out of your home. You clean your ducts and over a 3-5 year span they get dirty again. Also, duct cleaners are not licensed but should be certified by NADCA(National Air Duct Cleaning Association).
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.

An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.

Lennox, on the other hand, is probably the most expensive unit out there and I can’t stand them.  In our (humble?) experience, they have a horrible logistics chain, making repair parts difficult to come by (sometimes taking weeks), poor customer service, and the parts cost three times as much. That’s not what this article is about, so read more in: Carrier vs. Lennox Furnace Review.
Equipment used to clean ducts varies widely. The cheaper the equipment used the more you are just wasting money. This is why it's typically not worth doing. In some situations it may be beneficial, but only after determining and investigating the duct system. This should be done by a licensed HVAC contractor and not a duct cleaner that typically do not hold and HVAC license. (Duct cleaners aren't required to be licensed in HVAC in many areas.)
Here in Atlanta we get 6 to 10 $49 coupons in the mail weekly…I have always consider them a complete scam….just had my master bathroom& bedroom and guest bath completely remodeled down to the studs…Had my 3 returns nearest the area sealed to prevent sheet rock dust to spread…it worked and I personally cleaned all 7 returns when a 5 HP , new Rigid shop Vac($99 from HD)…took one hour and I found little evidence that “I need my ducts cleaned” Had quotes from $400 to $600…I use the best air filters for my air handler and change it every 2 to 3 months…..any dust is trapped in it and I believe the Air Duct folks are all cons….
HVAC services is our go to contractor when it comes to our HVAC needs. Back in 2013, we were dealt some unforeseeable home projects, as our  HVAC was failing and needed to replace the whole system, e.g. Furnace, Blower, A/C, Condenser, Vents, etc... We reached out to a few HVAC companies (Contra Costa Heating and Air, EP builders, High Performance Heating and Air) so we could compare the bids for the job. We have had some issues with past contractors and after thoroughly screening a few of the above mentioned HVAC contractors, we awarded the bid to HVAC services because of their superior customer service and very reasonable pricing.
Well, I had the cleaning done. The handler is definitely much quieter. It was explained to me that with the coils clean, the condensation will be able to sweat off instead of sticking to the dust and dirt, therefore the humidity (lots of humidity in florida) will be removed better. I feel as if it was worth it, but, I will definitely change that filter every 3 weeks or so from now on. I don’t want to pay that cost again.
Asking how much an HVAC installation costs is kind of like asking, “how much does a new car cost?”  Well, are you buying a Porsche or a Honda? Is it a 911 or just a Boxster, and are you going to get the leather seats? Likewise, are you going to get a Carrier or a Goodman air conditioner? Does the ductwork need to be replaced? These are all questions that will affect your HVAC installation cost, so let’s take a closer look.
A small number of products are currently registered by EPA specifically for use on the inside of bare sheet metal air ducts. A number of products are also registered for use as sanitizers on hard surfaces, which could include the interior of bare sheet metal ducts. While many such products may be used legally inside of unlined ducts if all label directions are followed, some of the directions on the label may be inappropriate for use in ducts. For example, if the directions indicate "rinse with water", the added moisture could stimulate mold growth.
I live in a 1950's ranch house in the South. The prior owners were smokers. Based on recommendations from one of the local conservation organizations, I decided to have a home energy audit done. As part of their findings, they recommended additional insulation in the attic and duct cleaning and sealing. This turned out to be a very problematic process. In terms of the ducts, it was necessary to remove the metal grates. However, these grates had been painted over many times and shoe molding covered the bottom of the grates. The vendor was not able to remove the grates without damaging them in the process. Because these grates dated back to the 1950's, it was difficult to find appropriate replacements. The ones I finally discovered were correct except they were 1/4" wider. This meant that the shoe molding had to be carved out. The duct cleaner could not provide any assistance with this problem. It took me a month of long evenings replacing the vent covers myself, carefully chiseling out the shoe molding and repainting. In terms of the extra installation in the attic, the same vendor used blow in insulation. Unfortunately, they did not recognize that the 13 floodlights whose mounting extended into the attic were not designed to be buried under insulation. The problem manifested itself in terms of expensive flood light bulbs failing continually. So, I had to have all of the light housings replaced. Yet another unexpected expense. Despite the expense, pain and suffering, I cannot report any improvement in my heating costs or the "quality" of the air. To be fair, I do not have any allergies and did not undertake this for air quality improvements but rather heating efficiency improvements.
Very interesting article. I searched articles about services for cleaning ventilation systems. But I have some questions. For cleaning ventilation system used special products for cleaning. Can I know in company manager about, which type of cleaning products they use? Your family members may be allergic in some components. It’s very big problem. And one more problem it’s how to choose the right company in Internet. Sometimes I don’t have much time to find a company in my town and I use the Internet. But I find a lot of company. It is very popular services, for example, Stanley Steemer – https://www.stanleysteemer.com/ or my local not very popular service, for example, AllstatesAirDuctPro – http://allstatesairductpro.us/. Can I understand the company is professional or not, only looking through the website? What must I check on the website? Who has helpful information? I will very grateful for your help. Links I add for understanding my problem. They are random and not for advertising.
My mom just received service from this company. She paid $609 to have her frion replaced. After two uses the AC stops working. A young rep comes out to the house again and notifies her that her entire AC unit and furnace need to be replace for just shy of ten grand, though when her frion was refilled she was told that her system should last another five years. When they came back to tell her how her entire system needed to be replaced, they were generous enough to offer her a $300 credit on the nearly $10,000 estimate of replacing the entire system that was working fine until they touched it. My best assumption would be that there is a mishap with the system is due to their negligence. Id suggest using another company other than these scam artists.
EPA does not recommend that air ducts be cleaned except on an as-needed basis because of the continuing uncertainty about the benefits of duct cleaning under most circumstances. EPA does, however, recommend that if you have a fuel burning furnace, stove, or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning. Some research also suggests that cleaning dirty cooling coils, fans and heat exchangers can improve the efficiency of heating and cooling systems. However, little evidence exists to indicate that simply cleaning the duct system will increase your system's efficiency.
×