An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
1). Busy companies: The company is so busy, it doesn’t need the work. It will add 70% to 100% profit, and if the customer accepts the estimate, it will move that high-margin customer to the front of the line. This often happens in the worst heat of summer when overburdened ACs and heat pumps quit and the dead of winter when furnaces give up. This is a good reason to consider pre-emptively replacing your system once it’s about 15 years old and/or has had major repairs.
If you are using existing ducting, it will have to be inspected. Proper ducting loses around 2% to 5% of your energy. Old, leaking ducts can lose 50% or more. A contractor will need to have the ducts inspected and replace any parts ahead of time. If you are changing the size of your HVAC system because of significant changes to your home, you might need to replace the ductwork regardless.
The three major functions of heating, ventilation, and air conditioning are interrelated, especially with the need to provide thermal comfort and acceptable indoor air quality within reasonable installation, operation, and maintenance costs. HVAC systems can be used in both domestic and commercial environments. HVAC systems can provide ventilation, and maintain pressure relationships between spaces. The means of air delivery and removal from spaces is known as room air distribution.[3]
Hello, I read your comment and I know it was two years ago but I hope you see my message. I am trying to figure out what to do as I was told that there is some cat odor in the finished basement. I think with the air conditioning running that it may carry odor. The litter boxes are always kept clean. I wonder if odor can be trapped in the ducts, if Air Duct Cleaning could help, but it is quite expensive plus I'm concerned that it may not help. Please elaborate as to why you think it doesn't work that well. Do you have any other advise? Did you work in the field of Air Duct Cleaning? Thanks so much!

If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.
Rheem's RRNL features a scroll compressor with fewer moving parts and less noise than traditional reciprocating compressors. A louvered compressor compartment protects the compressor from the elements and from debris that can shorten the life of the compressor. The Classic series continues to be one of their best sellers, with the addition of the Comfort Alert diagnostics module integrated to assist technicians in the event your system needs repair. 2-5 tons, 13 SEER, 80% AFUE.

I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
All information provided is provided for information purposes only and does not constitute a legal contract between Wilson's Heating & Air Conditioning and any person or entity unless otherwise specified. Information is subject to change without prior notice. Although every reasonable effort is made to present current and accurate information, LinkNow™ Media makes no guarantees of any kind.

Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]


The Environmental Protection Agency says that “duct cleaning services typically – but not always – range in cost from $450 to $1000 per heating and cooling system, depending on the services offered, the size of the system to be cleaned, system accessibility, climactic region, and level of contamination” and type of duct material. Consumers should beware of air duct cleaning companies that making sweeping claims about the health benefits of duct cleaning – such claims are unsubstantiated. Consumers should also beware of “blow-and-go” air duct cleaning companies. These companies often charge a nominal fee and do a poor job of cleaning the heating and cooling system. These companies may also persuade the consumer into unneeded services with and/or without their permission. (If you have knowledge of a practicing “blow-and-go” air duct cleaner, contact your local Better Business Bureau to report the company, and your local, federal, and state elected officials to demand legislation.)

CIBSE publishes several guides to HVAC design relevant to the UK market, and also the Republic of Ireland, Australia, New Zealand and Hong Kong. These guides include various recommended design criteria and standards, some of which are cited within the UK building regulations, and therefore form a legislative requirement for major building services works. The main guides are:
Those of you who read our posts regularly know that we built our reputation as a U.S. Veteran-Owned business that prides ourselves on giving people straight, honest answers to their questions...and there’s no question that makes people cringe more than asking, what does a new HVAC installation cost? Oddly enough, most contractors keep their air conditioning installation cost a closely guarded secret, as if the knowledge of how much it should cost will somehow change your decision when you have to buy a new AC. What I will tell you, is that the fair price of an HVAC installation will vary greatly based on the type of heating and air conditioning system installed, as well as the options needed or desired (Ductwork included? Zoning system?). In this article, we’ll discuss the five system features that affect HVAC installation cost, fair price ranges you can expect to pay for your new system, we will then perform an example calculation of how you can calculate a fair price, and finally, what you can do to keep from getting ripped off on your new HVAC installation price.
Since most states and municipalities don’t license air duct cleaners, you need to check their professional credentials instead, such as NADCA membership. EPA recommends all duct cleaners follow NADCA standards. Member companies must keep at least one technician on staff who has passed a NADCA test. “They have to pass rigorous testing to earn the certificate, and our code of ethics is very important,” Vinick says.
We bought 2 top of the line Lennox HAC for $29,000 less about $3,500 rebates, thinking they would at least last 10 years. Well, after 6 years, the system leaked. We are paying $1,700 to fix that leak. We thought at least it is still under warranty - yes BUT - the warranty covered $15 & the rest we were up for ,even though they advertise 10 year warranty. We are trying to sell & move out of high cost southern Calif & have looked at 20+ places in Arizona. Most of the houses we looked at were built from 1998 to 2005. We asked if the HAC was original & in most case it was - even though the highs were 115 to 120 & the lows 90F - versus where we live the highs run 85 to 95 & the lows are in the 60s. I asked the repairman WHY ours went out at 6 years. He replied that they just do not build them the same anymore. In Arizona, I did not see any Lennox - mostly Trane or Carrier. We had Fujistu in Australia which were fantastic - nothing went wrong in the 9 years we had them. Also, they had full induction motors not like the energy consuming 2 stage motors in Lennox. Maybe the Japanese built Fujusita still builds quality & the warranty is meaningful?
fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.
The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.

If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.
If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.
So, whether you need an AC repair or you’re in search of a new heating and air conditioning system—or you need a new water heater now–you can count on our team in North America. We’re experts in AC and plumbing repair, and offering top-notch AC and plumbing service is what we do best. Call Service Experts 24/7/365 at 866-397-3787 or request an appointment online today, and don’t forget to check out our coupons page for savings on your AC or plumbing repair service.
I call to follow up at the end of the next day and she said that she has not been able to get in touch with the owner.  By this time, I am starting to get frustrated because I am starting to get the run around.  I question her if I am even on the schedule or if they attempted to schedule a crane.  She says they are extremely busy and that she does not know.  So I say, basically I have waited over 2 weeks and you have not put me on the schedule and I am at the end of the install line.  No answer.  I tell her to talk to her boss and find out what is happening, and I will think about what direction I want to move in at this point.  
For more than 60 years Stanley Steemer has been perfecting our hot water extraction method to clean carpet with unparalleled results. Take control of the environment in your home and enjoy a cleaner, healthier living space for your family. Every carpet cleaning is Certified to remove an average of 94% of common household allergens. We remove the dirt you can see and the allergens you can't. 
I hope that those customers you have with breathing problems don't follow your advice too closely. You are doing them a disservice. Dirt in your ducts does not always stay there, depending on what the contaminants are. I bet you tell your customers not to worry about mold either- just to kill it with bleach. Educate yourself before opening your mouth- You may kill someone someday with your opinion.
Did not realize cost had gone up so much for this service. Two years ago I had furnace and ducts cleaned at my old house and it was under $400. Now the cost is $700 for this house. I will keep looking for someone to offer a lower price, check them out, and have it done. Or will find the paperwork to see who did it before. I liked this article and did learn some things. Thanks.
Concrete Blocks -- Concrete blocks are used in foundations and are often found in full basements. Insulating the spaces in the blocks is not the way to insulate them as the heat energy will travel along the concrete itself. The best way to insulate with concrete blocks is to use insulated concrete blocks, which have polystyrene incorporated into them.

If you don't agree with duct cleaning, fine. If there are some things that HVAC people can do to make the system need cleaning less often fine, but to suggest that I need to GO TO JAIL????? If you need to knock others to make yourself look better....... If duct cleaning is such a scam, why are their governing bodies like NADCA (which I do NOT belong to),several manufacturers of equipment, and national restoration franchises (I'm not a franchise either) who provide this service? I guess the whole world is stupid and only HVAC people are smart. I suppose I am scamming them when I clean puff backs, water damage, fire damage, and clean their carpets too? Or did I wake up one morning and say "ya know, it is great to be a hard working, honest owner operator, but I would love to provide a service that unlike everything else I do is a con and rips off the 90% referral business I busted my butt to earn"


The key to the continued and efficient operation of your heating and cooling system is periodic maintenance. Cleaning the air duct vent system, and servicing you heating and cooling equipment will keep the system operating at its peak performance. Air ducts are cleaned for two reasons. One: to prevent debris from entering furnace and air conditioning components. Two: to prevent debris from cycling through the home. The air duct cleaning contractor needs to employ cleaning methods which successfully removes debris, and ensures that debris does not enter the occupied space. Most contractors can verify the results of the cleaning through video or pictures.
Duct system installation and repairs affect HVAC installation cost. If you’re installing a new forced air heating or cooling system, your home must have ductwork – if you don’t have ducts installed, a new duct system will need to be designed and installed. Your existing duct system may require air sealing to eliminate air loss, helping your new heating and cooling system operate efficiently.
I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
All of you have dentists, you have doctors, you have preachers, you have mechanics. You don’t have to know everything about everything but you have to have people in your life that you can trust. Don’t just open up the phone book and pick a mechanical (HVAC) contractor. Call your friends and family and ask for referrals. There are no black and white (scam or not a scam) answers here.

Furnace Circuit Board -- The furnace circuit board controls a variety of functions. It not only handles the regular operation of the furnace, it also monitors the furnace's various safety circuits. Over time, vibrations from the furnace can weaken solder point and cause them to separate. Dirt and debris can cause short-circuits that damage the board. Failure of the circuit board can cause a variety of effects ranging from the fan not turning on to the complete shutdown of the furnace.
I am a service technician [since '92].....and as to double filtering.....I have never recommended it. Granted.....it would be noticeably helpful if the fiberglass filters are the main ones used [which I also never recommend.....as long as system can deliver appropriate air flow with a pleated cotton filter...and any decent service tech can check the air flow for proper cfm]. Any particles small enough to pass through a pleated cotton filter are going to pass through a second filter as well....unless the second filters are so tight that the system is starving for air flow. Has anybody ever accidentally put two filters in their automatic drip coffee maker? What if cars used two fuel filters or air filters? I have told some homeowners to try using second filters at each register [the black thin filter material cut-to-fit....same type used in many window air conditioners].....but I only suggest this when I know they will still get at least 400 cfm per ton of air flow [350 absolute minimum]......as some homeowners know others who say it has helped and it gives them a peace of mind knowing they are doing something to help contribute to a solution, so it HAS to help [even though I think it falls in the "one-born-every-minute" category.....similar to duct cleaning].
The original furnace was a coal fired “octopus” design which had no blower to circulate the air but relied upon warm air rising to distribute the heat. That also means that the system breathed air in from the basement and most of this type did not have a cold air return system. At some point (probably in the 1940’s) the system was upgraded to a forced air gas furnace. The upgrade included replacing the 12″ diameter air ducts exposed in the basement with 6″ ducts and a cold air return system of ducts from the two (only two) air returns on the first floor.
Whether you’re starting your air conditioner for the first time this year, or a unit isn’t running properly and you need to service an air conditioner, following a few simple steps can save you time and money. While some service jobs should be left to a professional, there are several do-it-yourself fixes you can do to keep your air conditioner cooling all summer long.

Asbestos removal tip.  Don’t trust any HVAC installation company that says that they will remove asbestos for you. They will do either one of two things: remove it and do a horrible job because they don’t know how (an illegal act in California, finable by up to $250,000), or they will say they did and never actually do it, which is dangerous to your health. Any HVAC contractor worth their weight will know not to touch it. Call an asbestos abatement company – it should cost around $500-$1,000, and your HVAC installation company will come in right after them and do the installation to decrease cost and inconvenience.
Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]
I live in a 1950's ranch house in the South. The prior owners were smokers. Based on recommendations from one of the local conservation organizations, I decided to have a home energy audit done. As part of their findings, they recommended additional insulation in the attic and duct cleaning and sealing. This turned out to be a very problematic process. In terms of the ducts, it was necessary to remove the metal grates. However, these grates had been painted over many times and shoe molding covered the bottom of the grates. The vendor was not able to remove the grates without damaging them in the process. Because these grates dated back to the 1950's, it was difficult to find appropriate replacements. The ones I finally discovered were correct except they were 1/4" wider. This meant that the shoe molding had to be carved out. The duct cleaner could not provide any assistance with this problem. It took me a month of long evenings replacing the vent covers myself, carefully chiseling out the shoe molding and repainting. In terms of the extra installation in the attic, the same vendor used blow in insulation. Unfortunately, they did not recognize that the 13 floodlights whose mounting extended into the attic were not designed to be buried under insulation. The problem manifested itself in terms of expensive flood light bulbs failing continually. So, I had to have all of the light housings replaced. Yet another unexpected expense. Despite the expense, pain and suffering, I cannot report any improvement in my heating costs or the "quality" of the air. To be fair, I do not have any allergies and did not undertake this for air quality improvements but rather heating efficiency improvements.

We moved to a house built in 1965 from a 1915 house with a dirt basement. Against what I anticipated, the 1965 house was much dustier. It was like felt on top of everything. I cleaned and cleaned and it did become less dusty over time. We then found out a cat lady with over 2 dozen cats lived in the house in the past. We then had to get our furnace replaced and I was able to look down some of the duct work, the dirt and debris was 3-5 inches deep. Additionally, the basement ducts were entirely plugged with debris including dirt, seeds, ants, toys, etc. I had already removed what I could from those. We had our ducts cleaned last year, and the dust in the house is greatly reduced. Also have lost the runny nose I got after moving here. There are duct cleaning con artists out there, but ours did a good job.

Asbestos removal tip.  Don’t trust any HVAC installation company that says that they will remove asbestos for you. They will do either one of two things: remove it and do a horrible job because they don’t know how (an illegal act in California, finable by up to $250,000), or they will say they did and never actually do it, which is dangerous to your health. Any HVAC contractor worth their weight will know not to touch it. Call an asbestos abatement company – it should cost around $500-$1,000, and your HVAC installation company will come in right after them and do the installation to decrease cost and inconvenience.

The liquid refrigerant is returned to another heat exchanger where it is allowed to evaporate, hence the heat exchanger is often called an evaporating coil or evaporator. As the liquid refrigerant evaporates it absorbs energy (heat) from the inside air, returns to the compressor, and repeats the cycle. In the process, heat is absorbed from indoors and transferred outdoors, resulting in cooling of the building.


How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .
Very interesting article. I searched articles about services for cleaning ventilation systems. But I have some questions. For cleaning ventilation system used special products for cleaning. Can I know in company manager about, which type of cleaning products they use? Your family members may be allergic in some components. It’s very big problem. And one more problem it’s how to choose the right company in Internet. Sometimes I don’t have much time to find a company in my town and I use the Internet. But I find a lot of company. It is very popular services, for example, Stanley Steemer – https://www.stanleysteemer.com/ or my local not very popular service, for example, AllstatesAirDuctPro – http://allstatesairductpro.us/. Can I understand the company is professional or not, only looking through the website? What must I check on the website? Who has helpful information? I will very grateful for your help. Links I add for understanding my problem. They are random and not for advertising.

My 48 yr old house (mine for the last 4 yrs) has considerable dust in the return plenum (fiber duct). I’m remodeling and recently re-sealed the return plenum AND the site-fabbed transition built when the new unit was installed, 2013. The return was leaky no doubt drawing musty, dusty air from the crawl space due to the Red-Neck fab & seal job! Pitiful craftsmanship! It took me 7 hours to fix the new transition piece. Anyway, the dust in the house is the same “color” as whats in the return duct and I’m getting way too much & too often in the house. I’ve also cleaned my coils, which were not that dirty.
×