You can install the greatest HVAC system ever built, but if your house is not insulated well, it's only going to end up costing you more money. Older homes may have fiberglass insulation that has broken down due to pests, moisture, or improper installation. Spray foam insulation can be damaged by careless repair or modification work or can be improperly installed. If your insulation in compromised, your attempts to save money and be comfortable will be in vain.

The fact is if they are dirty why not clean them. As for the Dr’s comment about if it is not disrupted it is fine. As a pet owner sometimes un disrupted pet hair will sit in the corner of a room or under a counter un disrupted but I still clean it when I notice it. Just because you cant see it doesn’t mean you should leave it there to collect more and more. The people that don’t want there air ducts clean either simply cant afford it but would like it done. OR! the crowd that are to cheap.. You should Clean all portions of your house.


PickHVAC Tips: Installing the right size central air conditioner is extremely important. Have a load calculation done to ensure proper sizing. ACs that are too big aren’t as energy-efficient as they should be, and they cycle on and off too much. This creates over-cooling and temperature imbalance. Units that are too small run constantly in very hot weather and can’t keep your home cool. When an air conditioner is properly sized, it runs at optimal efficiency and indoor comfort.

Before we get to HVAC installation prices, we will first need to briefly discuss some terms, definitions, and factors that will affect how an honest HVAC installation company determines their prices. Notice that I said honest. Unfortunately, there are dishonest people out there. There always have been, there always will be, and there is a good chance that you had an experience with such a contractor, which is what drove you to read this article. I can’t teach you how to tell if someone is honest, but I can give you the knowledge to help you decide. Take a look at How to Choose an HVAC Contractor for tips on what to look for.
If the one noticeable spot is where the wall [or ceiling or floor] is white.......first.....take a pair of needle nose pliers and bend each louver of the register to a straight outward position [as they all come brand new with a slant to each side]....so the register is shooting all supply air straight outward. If its a round register [in ceiling].....no help there. You also should always burn soy or beeswax candles.
Here in Frisco, TX…just had a tech come out to clean vents. I used a 30 bucks groupon for “complete vent cleaning”. He told me I have 3 AC units and groupon covers only 1. I told him to do the unit upstairs where the kids sleep. He decided on his own to do the downstairs unit. I yelled at him why he is not doing the unit I told him to do! He said they are all connected. I will clean two for you for the price of one… Oh really?

DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.


Roof-mounted systems have the heating and cooling systems in one cabinet. Sometimes called "gas packs" (if the heater uses natural gas), they typically cost less than a comparable split system. In dry regions, most homes originally had "swamp-coolers" installed. When replacing them with HVAC systems, it's often cheaper to use existing mounts and ducting.
An alternative to packaged systems is the use of separate indoor and outdoor coils in split systems. Split systems are preferred and widely used worldwide except in North America. In North America, split systems are most often seen in residential applications, but they are gaining popularity in small commercial buildings. The split systems are a great choice for small buildings where ductwork is not feasible or where the space conditioning efficiency is of prime concern [20]. The benefits of ductless air conditioning systems include easy installation, no ductwork, greater zonal control, flexibility of control and quiet operation [21]. In space conditioning, the duct losses can account for 30% of energy consumption [22]. The use of minisplit can result in energy savings in space conditioning as there are no losses associated with ducting.
Free cooling systems can have very high efficiencies, and are sometimes combined with seasonal thermal energy storage so that the cold of winter can be used for summer air conditioning. Common storage mediums are deep aquifers or a natural underground rock mass accessed via a cluster of small-diameter, heat-exchanger-equipped boreholes. Some systems with small storages are hybrids, using free cooling early in the cooling season, and later employing a heat pump to chill the circulation coming from the storage. The heat pump is added-in because the storage acts as a heat sink when the system is in cooling (as opposed to charging) mode, causing the temperature to gradually increase during the cooling season.
Heaters are appliances whose purpose is to generate heat (i.e. warmth) for the building. This can be done via central heating. Such a system contains a boiler, furnace, or heat pump to heat water, steam, or air in a central location such as a furnace room in a home, or a mechanical room in a large building. The heat can be transferred by convection, conduction, or radiation.
PickHVAC Tips: Oil burns dirty, so it is important to have your plenum and ducts checked to see if they should be cleaned when replacing an oil furnace. If you don’t clean the plenum and ducts when replacing the furnace, the new furnace might not run as efficiently and comfortably as possible due to restricted airflow. This can also reduce the oily smell sometimes associated with oil furnaces.
The sky is the limit. I am a big fan of adding zoning systems, but realize that this will typically add $2,300 to $3,500 (or more) to the price. “Why a price range, isn’t it just a part?” No, the part then has to be installed, and the customized ductwork required will vary based on the difficulty of the job and layout of your attic. It is very labor intensive, and most people don’t do it right. It should also include a bypass damper and ductwork! Simply put, the more you add, the more it will affect your HVAC installation cost.

Outdoor Fan Motor -- The outdoor fan, also called the condenser fan, is exposed to external conditions. As such it is most prone to dust and debris and the extreme weather. In desert climates, the outdoor fan motor is subject to heat not only from normal operation but from the outside temperature as well. As it starts to fail, the fan may work fine in the cooler morning hours but stop by afternoon. This can shut down the entire system for hours. When they stop running completely, your air conditioner will no longer work. Running a faulty fan will lead to compressor failure, which is a very costly repair.
I am in need of HVAC ADVICE!! I need a new furnace badly, mine is cracked. I have bought both a 95 % AFUE furnace and a 5 Ton evap coil, I figured it should all be replaced at once for both cost and efficency. My question is with all the negaitive things I have heard about companies ripping you off, what type of price should I pay someone for putting in those two items and bringing everything in my attic up to code? I have been quoted $550 - $ 3300. Wide margin here!! Then of course comes the licencing part!! I know in my heart that I should use a licenced contractor but I have had such bad luck and prices from them that honestly one that was licened in Ga. and just not here in TN and is a tech. which charges 1100 - 2200 less sounds good as so long as I pay some type of Profenial HVAC person say $100 to inspect the work after its done and before I pay them.
Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]
Is there a such thing as a PQ-15 valve? No…but how do we know? And oh, by the way, there are only two types of line-sets: 3/4 inch, and 7/8 inch. All modern equipment runs on a 7/8 inch line-set, so the only time they’ll have to change something is if you have antiquated 3/4 inch line-set from the 60’s or 70’s. I’m digressing though…the point is that they can easily prey on uninformed consumers…like you, baby bird! Don’t worry though…you’ll be flying by the end of this article.
I am very interested by your post. We recently had a lead inspection on our property and one thing the lead inspector suggested was to get the air ducts cleaned out. We had our ducts cleaned last year after we under went a large renovation project (since we have a toddler in the house). This year we decided to go for lead compliance and had all our lead removed (we moved out for the work). Recently, my son had a false positive lead test, which prompted us to get a lead dust inspection around the house (including having the vents dust-wiped on the inside). The levels inside the ducts weren't crazy high (but more than would be acceptable for a floor). As it turned out my son's lead levels are very low (but not zero). Is it possible however that lead dust from the inside of a vent can come out? Would this be a scenario where you think air duct cleaning would be beneficial?
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. My mom is located in Arizona and they trust J&M Restoration air duct cleaning company, they have an A+ BBB rating, they used EPA approved sanitizing agents, their technicians are NADCA certified, and the company is certified by the Institute of Inspection, cleaning and Restoration. Make sure to shop around and get written estimates first.

Outdoor Fan Motor -- The outdoor fan, also called the condenser fan, is exposed to external conditions. As such it is most prone to dust and debris and the extreme weather. In desert climates, the outdoor fan motor is subject to heat not only from normal operation but from the outside temperature as well. As it starts to fail, the fan may work fine in the cooler morning hours but stop by afternoon. This can shut down the entire system for hours. When they stop running completely, your air conditioner will no longer work. Running a faulty fan will lead to compressor failure, which is a very costly repair.
Although i love to burn candles, depending on the type your asking for problems big ones! At work one day i had been talking with co workers about these black shadows that were appearing on my ceilings and higher wall areas. They seemed to in the corners and along the stud supports , i could even see what i thought to be where all had been nailed. There would be dark shadows perfectly straight across my ceiling and then real dark circels every few inches within the lines. I thought it was the propane heat but learned quickly that oil heat will do that but not normally propane. A co worker brought me a magazine with a huge article about candles and what actually burns off them when lit, an ashy soot that is attracted to the areas on walls and ceilings that omit the most heat or warmth, of course where the drywall and studs meet and corners of the room. Its been about 8 years since i painted the entire house. I started bending to my love for candles again in the last 3 years, surprise i will be spending part of my summer re painting again!! No more candles ,well maybe at the holidays LOL
I guess, I will start with saying that air duct cleaning is almost never needed. It is not a scam, but it is certainly something that uneducated homeowners get suckered into. In regards to air flow, a well balanced HVAC system should be able to deliver more than enough air flow. If you are not getting good air flow, it's because your system may be out of balance. Additionally, regular cleaning/changing of the air filters will solve about 95% of your problem. Though you would be surprised how many people either a. don't have a filter or b. don't know about it and leave it there for 10+years. a washable one should be cleaned every 6 months(spring and fall) and a disposable one should be replaced every 3-4 months.
We have provided Arkansas families and businesses with quality HVAC products and services for 42 years. Offering reasonable rates and personalized service, we are a dedicated team of experts equipped to handle any service requirement. Your source for modern heating, cooling, and ventilation equipment and servicing, Wilson's Heating & Air Conditioning is the HVAC specialist in Van Buren.

Monday the following week, no phone calls, or follow up.  I call to get an update and am told that they cannot install my system because they don't have time.  I ask what does that mean, one year? One week? Until the end of summer they say.  What does that mean I ask?  They say at the end of September.  I say thank you for wasting 1 month of my time.
Air conditioning units are prone to the pitfalls of wear and tear. You can prolong this, however, with proper maintenance procedures. Without regular maintenance even an immaculate AC installation in Fort Smith, Arkansas cannot guarantee performance. Our maintenance service is thorough, leaving no area unattended. If there’s a problem, we’ll catch it early and prevent avoidable breakdowns and costly repairs.
I purchased a Groupon for cleaning of unlimited air ducts and one return vent for $39. I should have checked into their hours first because they only offer services during normal business hours. So, with no evenings or weekends available you have to take time off work. I asked Groupon for a refund when I realized this and they refused because it wasn’t within the three day window. Then they didn’t even show up or call for the appointment. I called them after they were an hour late and they were going to call the local dispatch office and have them call me back within 15 minutes. I did not receive that call. I called again and was told I would get a call back from a manager. That didn’t happen either. So I asked Groupon for a refund again and they gave me Groupon bucks. When the survey came asking if I was satisfied with the Groupon customer service I said no, I want real money. I got my real refund the next day. Seems to me Groupon should stop dealing with these companies.

Undertaking an AC installation in Fort Smith, AR? The first thing to remember is that your air conditioning unit will need repairs now and then to remain efficient. Granted, many repair emergencies can be avoided through proper maintenance procedures. When your AC fails we provide reliable, affordable repairs of the highest standards. Enhanced efficiency and longevity is the name of our game.
I have lived in Calgary for quite some time now. When I first moved here I couldn’t stand the humidity levels. Its like a desert come winter. When I first moved into my new home, the house inspector insisted I have my furnace and ducts cleaned. I was very sceptical about duct cleaning to begin with. The company I hired came on time and were very respectable from the start. Before mentioning anything they asked me what my concerns were and what issues I was having. They were more concerned about addressing my issues then bringing anything non related up. I ended up going with this company and getting a humidifier installed a couple days later after the cleaning. Its been almost 4 years now that I have been here. The humidifier is working great and the difference is incredible. They took me around explained step by step what they were doing and the reasons they were doing it. With all those other companies out there, I am glad I found them at this site.
As you can see, if we know what the contractor is actually paying for specific equipment, we know what their labor rates are, and we know what they bid the project for, then we can also use some basic algebra (or just let the program do it for us because we’re lazy) to figure out how much of a profit they are making off of us (you) at different bid prices:
We have provided Arkansas families and businesses with quality HVAC products and services for 42 years. Offering reasonable rates and personalized service, we are a dedicated team of experts equipped to handle any service requirement. Your source for modern heating, cooling, and ventilation equipment and servicing, Wilson's Heating & Air Conditioning is the HVAC specialist in Van Buren.
Before you choose any duct cleaning service provider, interview as many service providers as you can. Ensure that the service provider is certified by the National Air Duct Cleaners Association or NADCA. Make sure that they hold a good standing in the Better Business Bureau and have all the necessary certifications and license. Be clear about their terms of service. Make sure they have the right equipment to do the job. It is best to go for a company that has been tried and tested successfully by any of your acquaintances or opt for a service provider that has been in the business for quite some time.

What if you move into a 20 year old house and find that the people who owned it previously NEVER replaced the filter? It was so dirty that the HVAC system did not work at all. For most people - duct cleaning is NOT a waste of time or money. You must not have allergies. I have very bad ones plus asthma. It makes it very hard for me if I don't get it done every few years. By the way - the ducts get dusty just sitting there - especially without air going through them. Dust settles on them just like it does the furniture.


The answer to your question is most likely "Yes," but not defiitely. It depends on where the dust is coming from. Now, if your house is more than say, 12 years old then you likely do have leaks in your ducts that can let in insulation particles and dust from your attic. If this is the case then cleaning of the ducts-PROPER CLEANING, which like the article sas doess include EVERYTHING that the conditioned air passes through, such as your indoor evaporator coil and blower housing assembly-is definitely a good first step to getting that dust under control! Of course I highly recommend that you also have your ducts SEALED as well, or else you will have to repeat the cleaning some time down the line. As a 3rd step, consider an electronic air filter. I always thought they were a scam, personally, so I never bothered selling them to my clients. Then one day my manager sent me to install one for a senior couple in a mobile home. The wife had bad allergies, and her eyes were constantly watering and puffy and red. Well, I did a quality check 60 days later and she could not stop praising that air filter! Keep in mind that in a mobile home, duct seals are not as complete as those in other homes due to access issues.
I believe a $3 [sic] pleated cotton filter is all that is ever needed to keep a system running top notch. A cleaning of the blower squirrel cage and of the evaporator [indoor] coil may be needed one time if fiberglass or no filters have been previously used. The return air grille [or grilles] need vacuumed off occasionally, as they are upstream from the filter. The $3 filter should be changed every 3 months [rule of thumb]....and most of them have a little white square on the cardboard frame to write install date.....and the arrow should point into the duct [if at filter grille]....or towards the furnace [if in ductwork slot]...or towards the blower [if in blower compartment]. My two cents.....

HRV/ERV Ventilators: These whole-house ventilators exchange air. They are ideal for homes with what is called a “tight envelope,” homes where house wrap has been applied and airgaps in the attic, around windows, doors and outlets have been sealed. Air in these homes becomes stale and polluted, so exchanging the air is important to IAQ. Heat recovery ventilators (HRV) are designed for cold climates. Energy recovery ventilators (ERV) are best for warm climates.  Your cost for an installed HRV or ERV will range from about $2,000 to more than $5,000 based on its capacity and features.
If you are replacing your air conditioning system, make sure that the unit is the proper size for your needs and that all ducts are sealed at the joints. A unit that is too big will cycle on and off frequently, resulting in poor moisture removal, particularly in areas with high humidity. Also make sure that your new system is designed to manage condensation effectively.
×