Natural ventilation is a key factor in reducing the spread of airborne illnesses such as tuberculosis, the common cold, influenza and meningitis. Opening doors, windows, and using ceiling fans are all ways to maximize natural ventilation and reduce the risk of airborne contagion. Natural ventilation requires little maintenance and is inexpensive.[19]
Air conditioning units are prone to the pitfalls of wear and tear. You can prolong this, however, with proper maintenance procedures. Without regular maintenance even an immaculate AC installation in Fort Smith, Arkansas cannot guarantee performance. Our maintenance service is thorough, leaving no area unattended. If there’s a problem, we’ll catch it early and prevent avoidable breakdowns and costly repairs.
I believe a $3 [sic] pleated cotton filter is all that is ever needed to keep a system running top notch. A cleaning of the blower squirrel cage and of the evaporator [indoor] coil may be needed one time if fiberglass or no filters have been previously used. The return air grille [or grilles] need vacuumed off occasionally, as they are upstream from the filter. The $3 filter should be changed every 3 months [rule of thumb]....and most of them have a little white square on the cardboard frame to write install date.....and the arrow should point into the duct [if at filter grille]....or towards the furnace [if in ductwork slot]...or towards the blower [if in blower compartment]. My two cents.....
Some systems include an "economizer mode", which is sometimes called a "free-cooling mode". When economizing, the control system will open (fully or partially) the outside air damper and close (fully or partially) the return air damper. This will cause fresh, outside air to be supplied to the system. When the outside air is cooler than the demanded cool air, this will allow the demand to be met without using the mechanical supply of cooling (typically chilled water or a direct expansion "DX" unit), thus saving energy. The control system can compare the temperature of the outside air vs. return air, or it can compare the enthalpy of the air, as is frequently done in climates where humidity is more of an issue. In both cases, the outside air must be less energetic than the return air for the system to enter the economizer mode.
Interesting. Giuliano Cuete and Carlo Olcese have the exact same post about pretenders and being NADCA certified, word for word. So how do you become NADCA certified? And does that mean you are not a scam artist or a "blow and do" ripoff? hmmm, interesting. The EPA says that under normal conditions, a properly maintained system should NEVER need it's ducts cleaned.
And if you have flex duct and/or fiberglass ductboard in your home- the last thing you want is a big brush or anything abrasive running through it. Even high-pressure air can erode ductboard so I wouldn’t clean it with anything. If it becomes contaminated, get rid of it and install real ductwork. If your ductwork is accessible in the basement – the best thing to do is take it down and manually clean it if it’s full of junk. It’s not going to cost a nickel more to do that than to pay $500-1000 for a ‘duct cleaning machine” AKA big blower and vacuum – to do the job.
Whether you’re starting your air conditioner for the first time this year, or a unit isn’t running properly and you need to service an air conditioner, following a few simple steps can save you time and money. While some service jobs should be left to a professional, there are several do-it-yourself fixes you can do to keep your air conditioner cooling all summer long.

An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.

Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
Your contractor will do a load calculation to determine the proper central air conditioning unit for your home. This calculation accounts for the climate, size, shape and orientation of your home, as well as its square footage. A professional will also look at the insulation, windows, walls, floors and other materials that compose your home. He/she will then examine any leaks, seals and existing ducts or vents.
HELP is am drowing in LENT . It has been noticed in the master bedroom there is lent all over the furniture and the floors. I have dark brown/black furniture and same for the wooden floors. There are wods of lent every day. My furniture covered in lent. The rest of the house is fine just the tipical dust. I am sure my lungs are also full of lent. I looks like if my dryer vent was in my bedroom. Please help
My Carrier furnace occasionally (one-two times a day) does not start. It shows error code 15 ("BLOWER MOTOR LOCKOUT -This status code indicates the blower failed to reach 250 RPM or the blower failed to communicate to the variable speed furnace control within 30 seconds after being turned ON in two successive heating cycles."). However, when I turn off and on the furnace power switch it starts and runs fine for a while. Sometimes it runs fine all day, but does not start only once in the evening or in the night. It is 13 years old I was thinking to replace whole thing if repair cost is too high. But I am not ready to pay $10,000. 
I noticed a lot of negative feedback, though unfortunately there are many dishonest companies out there. I currently work with a company that cleans duct work and we DO NOT use any scare tactics or up sell services or equipment. Once every 10years of course there are exceptions. We clean supply, returns, air handler, housing, motor, and fan. Though be discerning when qualifying anyone to work in your home. I would ask for REAL REFERENCES to contact.
Those of you who read our posts regularly know that we built our reputation as a U.S. Veteran-Owned business that prides ourselves on giving people straight, honest answers to their questions...and there’s no question that makes people cringe more than asking, what does a new HVAC installation cost? Oddly enough, most contractors keep their air conditioning installation cost a closely guarded secret, as if the knowledge of how much it should cost will somehow change your decision when you have to buy a new AC. What I will tell you, is that the fair price of an HVAC installation will vary greatly based on the type of heating and air conditioning system installed, as well as the options needed or desired (Ductwork included? Zoning system?). In this article, we’ll discuss the five system features that affect HVAC installation cost, fair price ranges you can expect to pay for your new system, we will then perform an example calculation of how you can calculate a fair price, and finally, what you can do to keep from getting ripped off on your new HVAC installation price.
The number of years an HVAC system lasts depend on the type and brand of components that make up your system. The lifespan of an air conditioner averages between 15 and 20 years. The life expectancy of a tankless water heater is approximately 20 years, while a storage water heater is closer to 10-15 years. Ducts may need replacing within 10-15 years. Your equipment will have a longer life if you have regular tuneups and maintenance to keep everything in good working order. If you’re having repair problems and your HVAC system is over 10 years old, it’s a good time to consider the costs and benefits of repairing vs. replacing. Energystar.gov provides the following tips to help you decide whether to repair or replace:
And if you have flex duct and/or fiberglass ductboard in your home- the last thing you want is a big brush or anything abrasive running through it. Even high-pressure air can erode ductboard so I wouldn’t clean it with anything. If it becomes contaminated, get rid of it and install real ductwork. If your ductwork is accessible in the basement – the best thing to do is take it down and manually clean it if it’s full of junk. It’s not going to cost a nickel more to do that than to pay $500-1000 for a ‘duct cleaning machine” AKA big blower and vacuum – to do the job.
The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.
Capacitors -- Capacitors help your HVAC motor start from a standstill. Over time they can weaken. As they weaken, they cause the motor to run hotter. This can shorten the life expectancy of your motor. Once a capacitor fails, the whole motor will stop working. You usually won't notice that a capacitor has weakened until your motor stops turning on.
I am very interested by your post. We recently had a lead inspection on our property and one thing the lead inspector suggested was to get the air ducts cleaned out. We had our ducts cleaned last year after we under went a large renovation project (since we have a toddler in the house). This year we decided to go for lead compliance and had all our lead removed (we moved out for the work). Recently, my son had a false positive lead test, which prompted us to get a lead dust inspection around the house (including having the vents dust-wiped on the inside). The levels inside the ducts weren't crazy high (but more than would be acceptable for a floor). As it turned out my son's lead levels are very low (but not zero). Is it possible however that lead dust from the inside of a vent can come out? Would this be a scenario where you think air duct cleaning would be beneficial?
American design standards are legislated in the Uniform Mechanical Code or International Mechanical Code. In certain states, counties, or cities, either of these codes may be adopted and amended via various legislative processes. These codes are updated and published by the International Association of Plumbing and Mechanical Officials (IAPMO) or the International Code Council (ICC) respectively, on a 3-year code development cycle. Typically, local building permit departments are charged with enforcement of these standards on private and certain public properties.
PickHVAC Tips: First, see the PickHVAC tip above about sizing a central air conditioner. It applies to heat pumps just as much. Secondly, Even if the line set for the new heat pump is the correct size, we recommend replacing the set or at least the fittings. Old lines and fittings are a major source of leaks. When refrigerant leaks out, the heat pump efficiency suffers. Eventually, the unit stops providing heating and air conditioning, and it might break down.

For more than 60 years Stanley Steemer has been perfecting our hot water extraction method to clean carpet with unparalleled results. Take control of the environment in your home and enjoy a cleaner, healthier living space for your family. Every carpet cleaning is Certified to remove an average of 94% of common household allergens. We remove the dirt you can see and the allergens you can't. 
Some research suggests that cleaning heating and cooling system components (e.g., cooling coils, fans and heat exchangers) may improve the efficiency of your system, resulting in a longer operating life, as well as some energy and maintenance cost savings. However, little evidence exists that cleaning only the ducts will improve the efficiency of the system.
×