I am a service technician [since '92].....and as to double filtering.....I have never recommended it. Granted.....it would be noticeably helpful if the fiberglass filters are the main ones used [which I also never recommend.....as long as system can deliver appropriate air flow with a pleated cotton filter...and any decent service tech can check the air flow for proper cfm]. Any particles small enough to pass through a pleated cotton filter are going to pass through a second filter as well....unless the second filters are so tight that the system is starving for air flow. Has anybody ever accidentally put two filters in their automatic drip coffee maker? What if cars used two fuel filters or air filters? I have told some homeowners to try using second filters at each register [the black thin filter material cut-to-fit....same type used in many window air conditioners].....but I only suggest this when I know they will still get at least 400 cfm per ton of air flow [350 absolute minimum]......as some homeowners know others who say it has helped and it gives them a peace of mind knowing they are doing something to help contribute to a solution, so it HAS to help [even though I think it falls in the "one-born-every-minute" category.....similar to duct cleaning].

I just had my blower module replaced because my AC coil was frozen over. The underside of my coils had a thick mat of dust because I had never had it cleaned. I cleaned it myself by using a soft brush attachement on a shop vac. The inside of the blower appears to have a white/green growth, and I am sure the ductwork of my 30 year old house can’t be in good condition.

I'm very glad that I found another guy to come replace the circuit board and put it away from the water, fix the water leak, and also find and fix another impending failure.  All of that was for much less than HVAC Service wanted to charge for repair or replacement. The other guy did a great repair, so I'm confident it will not break down again, but if it does, I will not call HVAC Service. Don't get suckered by their Yelp Deal.


I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.

In reading through all this about duct cleaning, THE ONE preventative measure people need to realize is that a poorly installed HVAC system that is not sealed and air tight to ensure that ALL indoor air passes through a GOOD air filtration system IS THE best means of ensuring your ducts remain clean. Duct cleaning does not now and will NEVER improve an HVAC systems efficiency. Proper maintenance and installation are the key just as improper installation practices allow for dust infiltration into the duct system. I am a state licensed contractor in Texas, and unless people have their hvac system sealed and/or properly installed, duct cleaning is an absolute waste of money. My duct system is 12 years old as is as clean today as the day I installed the system with ductwork. SO before ANYONE jumps on the bandwagon of duct cleaning, get with your hvac professional FIRST.
Hello, I read your comment and I know it was two years ago but I hope you see my message. I am trying to figure out what to do as I was told that there is some cat odor in the finished basement. I think with the air conditioning running that it may carry odor. The litter boxes are always kept clean. I wonder if odor can be trapped in the ducts, if Air Duct Cleaning could help, but it is quite expensive plus I'm concerned that it may not help. Please elaborate as to why you think it doesn't work that well. Do you have any other advise? Did you work in the field of Air Duct Cleaning? Thanks so much!
We installed a TRANE XL18 HVAC with a TRANE HV80 furnace 16 years ago and it still works great in Tucson, AZ.  We inquired into a replacement for the future since the R-22 refrigerant will be off market at the end of this year.  Our maintenance folks want to sell me a new system anyway (even though the TRANE works great).  We are considering the BOSCH Inverter heat pump as a lower cost option down the road.  Watch out for the tricky salesmen trying to sell beer at champagne prices though. Get estimates on whether you need to replace your current system and how much it could cost.  And if they are factory certified.
I have worked cleaning HVAC in my area for almost 5 years. I always do a thorough inspection and cleaning, providing before and after photos. I have completed some jobs where I felt that it was not entirely necessary, but ultimately what the customer wanted. With that being said, I have endless photos of unspeakable horrors. Hotels are usually nasty, post construction mess is certain, pets and kids create lots off debris, bugs congregate and die, then spiders set up and die, I have even had one supply that was nearly plugged with sand!
Pro Tips: Before you buy one of the learning thermostats available, you should beware of their shortcomings. First, many require a c-wire to work properly. A common problem is that the old thermostat might not use a c-wire, and this makes it confusing when swapping wires to the new thermostat. Secondly, if you change your thermostat setting often, you might become frustrated with a nest thermostat or other learning thermostat. It will be constantly trying to learn patterns in your random setting changes, and will therefore change your home’s temperature when you don’t want it to. If you have a fairly consistent schedule or don’t mind overriding the unit either manually or via the app on your way home or when leaving, then you won’t experience this issue.
Alberto said they were busy but could either install on the upcoming Saturday.  We were going to be out of town and said unfortunately that day did not work.  He then proposed the upcoming Tuesday as a possible solution, but just had to confirm with another appointment.  I said great.  I will review the estimate and call your office to confirm I want to move forward with the install.
yes get a good company and pay the price, I found so much dust and dirt and wood and paint chips and bugs and even bottle caps in my ductwork. I hired a major plumbing company who cleaned ductwork and i will say they did an excellent job cleaning my vent. they did miss one point in my ductwork because i still started to see dust all over my furniture and i realized that my retunduct work that was connected with a piece of sheet metal beam which was 16" across , the contractor that built my condo used a 16" wide sheet of sheet metal to connect the vent system to my return for the air to return back into my condo. The contractor should have built a 8" x16" square duct by 6 feet long to connect my intake to my return instead of using a sheet of sheet metal 16" wide by using two 3' sections by 16 inches wide. That was a shor cut which caused a major problem fir me.
Equipment used to clean ducts varies widely. The cheaper the equipment used the more you are just wasting money. This is why it's typically not worth doing. In some situations it may be beneficial, but only after determining and investigating the duct system. This should be done by a licensed HVAC contractor and not a duct cleaner that typically do not hold and HVAC license. (Duct cleaners aren't required to be licensed in HVAC in many areas.)
1. Ducts need cleaning mostly because they were not installed properly. There should be regulatory inpection and approval of clean and proper duct works on new houses. I was extremely unpset when I looked and found significant amounts of construction dust in parts of the ducts in my new house. There is apparently no way to hold the bullder to be responsible for clean ducts.
in response to this reply " should your ducts be cleaned", i have to politely correct the person who answered this. you are not using common sense. first, most of the country uses metal duct work, so for you to say what you did, is wrong. second, the duct system in a house is a circulatory system. that means it draws air into the furnace, it gets filtered, and then it is blown out into the house to heat or cool. So, obviously that air is being brought into the house from somewhere right? Yes, its coming from the outside where there are many allergens and dust particles . For you to says that about whether a duct system is sealed or not, makes no difference. The air is coming from somewhere right? It has to originate from somewhere right? Just look on top of your cieling fan. If there is a bunch of dust up there, then there is obviously a bunch in your ducts. And the duct air is being circulated every day, and every hour through your house. Its simple, dust collects everywhere in your house. Imagine if you never dusted your shelves, or tv? There would be a ton of dust after a while. Well, now think about the air in the duct system. Of course theres gonna be a ton of dust in there. For you to say that it is not benififcial to clean the ducts, is plain ignorant. 90% of the air we breathe is in our household. Wouldnt you want that air to be as dust and allergen free? I could go on for hours about the benifits of duct cleaning, but i just wanted to make a quick point that the person whose says it is not benificial to clean them, is not using common sense. Not to mention, giving the people who clean ducts for a living, a bad name. Use your head .
The original furnace was a coal fired “octopus” design which had no blower to circulate the air but relied upon warm air rising to distribute the heat. That also means that the system breathed air in from the basement and most of this type did not have a cold air return system. At some point (probably in the 1940’s) the system was upgraded to a forced air gas furnace. The upgrade included replacing the 12″ diameter air ducts exposed in the basement with 6″ ducts and a cold air return system of ducts from the two (only two) air returns on the first floor.
I own and live in a mobile home and was told to install a mobile home air condition well I did not want one because the ones for moblie homes are to small,so I install a home air-condidtion and its good for heating and cooling the only thing I do is change is the filter every month or two,What I want to know is how does dirt and dust comes from????
The use of furnaces, space heaters, and boilers as a method of indoor heating could result in incomplete combustion and the emission of carbon monoxide, nitrogen oxides, formaldehyde, volatile organic compounds, and other combustion byproducts. Incomplete combustion occurs when there is insufficient oxygen; the inputs are fuels containing various contaminants and the outputs are harmful byproducts, most dangerously carbon monoxide, which is a tasteless and odorless gas with serious adverse health effects.[14]
Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]
Multiple inventions within this time frame preceded the beginnings of first comfort air conditioning system, which was designed in 1902 by Alfred Wolff (Cooper, 2003) for the New York Stock Exchange, while Willis Carrier equipped the Sacketts-Wilhems Printing Company with the process AC unit the same year. Coyne College was the first school to offer HVAC training in 1899.[12]
Asking how much an HVAC installation costs is kind of like asking, “how much does a new car cost?”  Well, are you buying a Porsche or a Honda? Is it a 911 or just a Boxster, and are you going to get the leather seats? Likewise, are you going to get a Carrier or a Goodman air conditioner? Does the ductwork need to be replaced? These are all questions that will affect your HVAC installation cost, so let’s take a closer look.

I just had my Air ducts “cleaned”. The person who came to my house works for an air duct cleaning company who uses a professional vacuum. He said the company would charge me about $900 but he can do it aside on his own and charge me half of that. However, when he came over the house, he brought the rotary brush along with his domestic vacuum cleaner that it’s hose was about 5 feet long, I ask him that the wasnt strong enough to pull dust out, and he said, it’s similar to what companies use. I was in doubt and he didnt cover the vents so im thinking all dust must have come out from every air vents. Could this vacuum have taking the debris out of the air ducts? Or how can I myself find out if the inside of the air ducts have been cleaned and no debris is sitting there? I have dust all over my house.
These factors are included in a "Manual J" calculation. Contractors who make these calculations before recommending a size can take a couple of hours collecting the information and making the calculation. If your contractor doesn't do it, there are services that will do it for around $99. If you're feeling particularly on the ball, there are also free online calculators.
Whether you’re starting your air conditioner for the first time this year, or a unit isn’t running properly and you need to service an air conditioner, following a few simple steps can save you time and money. While some service jobs should be left to a professional, there are several do-it-yourself fixes you can do to keep your air conditioner cooling all summer long.
We moved to a house built in 1965 from a 1915 house with a dirt basement. Against what I anticipated, the 1965 house was much dustier. It was like felt on top of everything. I cleaned and cleaned and it did become less dusty over time. We then found out a cat lady with over 2 dozen cats lived in the house in the past. We then had to get our furnace replaced and I was able to look down some of the duct work, the dirt and debris was 3-5 inches deep. Additionally, the basement ducts were entirely plugged with debris including dirt, seeds, ants, toys, etc. I had already removed what I could from those. We had our ducts cleaned last year, and the dust in the house is greatly reduced. Also have lost the runny nose I got after moving here. There are duct cleaning con artists out there, but ours did a good job.
We moved to a house built in 1965 from a 1915 house with a dirt basement. Against what I anticipated, the 1965 house was much dustier. It was like felt on top of everything. I cleaned and cleaned and it did become less dusty over time. We then found out a cat lady with over 2 dozen cats lived in the house in the past. We then had to get our furnace replaced and I was able to look down some of the duct work, the dirt and debris was 3-5 inches deep. Additionally, the basement ducts were entirely plugged with debris including dirt, seeds, ants, toys, etc. I had already removed what I could from those. We had our ducts cleaned last year, and the dust in the house is greatly reduced. Also have lost the runny nose I got after moving here. There are duct cleaning con artists out there, but ours did a good job.
Chemical biocides are regulated by EPA under Federal pesticide law. A product must be registered by EPA for a specific use before it can be legally used for that purpose. The specific use(s) must appear on the pesticide (e.g., biocide) label, along with other important information. It is a violation of federal law to use a pesticide product in any manner inconsistent with the label directions.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.
I to had an odd layer of white'ish dust building up especially during seasonal periods when the HVAC ran a a lot. I carefully swept up the fine dust into a small pile and had it analyzed. Turns out it was very fine fiberglass powder dust. It turns out it is the insulation form the attic! (My attic has blown in insulation). Turns out if you (I) had small gaps around my HVAC registers in the ceiling whee the airs blows into the room. What occurred in my case was that the exiting air at that seam creates a vacuum effect at the grate vent cover and draws and then blows fine insulation dust from the attic into the house. Removing each register grate and sealing each tin outlet gap with calking between the dry wall ceiling and tin fixed the issue. A couple were so bad with bowed gaps I had to screw down the bowed tin to the attaching stud better. Checking the very same glass top desk that catches and shows any dust accumulation now shows only very small amounts of normal house dust build up over several weeks. A big, big improvement. You might have a look by simply removing a couple vent covers yourself.
Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]
We installed a TRANE XL18 HVAC with a TRANE HV80 furnace 16 years ago and it still works great in Tucson, AZ.  We inquired into a replacement for the future since the R-22 refrigerant will be off market at the end of this year.  Our maintenance folks want to sell me a new system anyway (even though the TRANE works great).  We are considering the BOSCH Inverter heat pump as a lower cost option down the road.  Watch out for the tricky salesmen trying to sell beer at champagne prices though. Get estimates on whether you need to replace your current system and how much it could cost.  And if they are factory certified.

Typically speaking, the lower SEER, more basic models are also more reliable.  Reliability is big with us, so we steer clear of features with reliability issues, and it’s as simple as that. When you factor in the price of repairs and the extra expense of the 21-SEER, you may actually lose money! 16 SEER is the sweet-spot, and it is key to reducing your HVAC installation cost.
On the other hand, if a service provider fails to follow proper duct cleaning procedures, duct cleaning can cause indoor air problems. For example, an inadequate vacuum collection system can release more dust, dirt and other contaminants than if you had left the ducts alone. A careless or inadequately trained service provider can damage your ducts or heating and cooling system, possibly increasing your heating and air conditioning costs or forcing you to undertake difficult and costly repairs or replacements.
×