I just had my blower module replaced because my AC coil was frozen over. The underside of my coils had a thick mat of dust because I had never had it cleaned. I cleaned it myself by using a soft brush attachement on a shop vac. The inside of the blower appears to have a white/green growth, and I am sure the ductwork of my 30 year old house can’t be in good condition.

Outdoor Fan Motor -- The outdoor fan, also called the condenser fan, is exposed to external conditions. As such it is most prone to dust and debris and the extreme weather. In desert climates, the outdoor fan motor is subject to heat not only from normal operation but from the outside temperature as well. As it starts to fail, the fan may work fine in the cooler morning hours but stop by afternoon. This can shut down the entire system for hours. When they stop running completely, your air conditioner will no longer work. Running a faulty fan will lead to compressor failure, which is a very costly repair.
Clean the condenser fan blades before the start of the cooling season. Brush any dust or debris off gently and then uncover the condenser coils, gently cleaning the dirty side. Then wrap the motor and other electrical components in plastic bags and gently spray from the inside with a hose. Now check the base pan under the unit and clear it out of any debris that has gathered.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
Pay particular attention to cooling coils, which are designed to remove water from the air and can be a major source of moisture contamination of the system that can lead to mold growth. Make sure the condensate pan drains properly. The presence of substantial standing water and/or debris indicates a problem requiring immediate attention. Check any insulation near cooling coils for wet spots.
Asbestos removal tip.  Don’t trust any HVAC installation company that says that they will remove asbestos for you. They will do either one of two things: remove it and do a horrible job because they don’t know how (an illegal act in California, finable by up to $250,000), or they will say they did and never actually do it, which is dangerous to your health. Any HVAC contractor worth their weight will know not to touch it. Call an asbestos abatement company – it should cost around $500-$1,000, and your HVAC installation company will come in right after them and do the installation to decrease cost and inconvenience.
PickHVAC Tips: Oil burns dirty, so it is important to have your plenum and ducts checked to see if they should be cleaned when replacing an oil furnace. If you don’t clean the plenum and ducts when replacing the furnace, the new furnace might not run as efficiently and comfortably as possible due to restricted airflow. This can also reduce the oily smell sometimes associated with oil furnaces.
But Tim, doesn’t this mean that a less-than-honest air conditioning company can just charge what he wants and say that it’s a difficult job? No. You see, dishonest contractors, typically, aren’t the brightest people (I figure if you’re still reading this, you’re warming up to me so I’m taking off the training-wheels). They aren’t smart enough to take difficulty into account, and will probably get confused if you ask them about it. They will tell you things like, “that’s how much the unit costs,” or “California has a new law that magically adds $5,000 to the price.”  Trust me, follow your gut, and you’ll be able to tell who the honest contractors are...or just use one of our ASM-approved contractors.
Many homes have a forced-air HVAC system. Both the heating and the central air conditioning units share a ductwork system where they either push in or pull out warm or cooled air. There are also heating and cooling systems that don’t require ductwork — such as ductless mini-splits — but work on the same principles of heat exchange. The national average to hire an HVAC specialist is $2,920-$3,670, with costs varying depending on the work you need done and the equipment you are installing.
My point is that the brand of equipment you choose is going to affect your HVAC installation cost greatly. People often call us for an air conditioning installation job and say, “I would like to install Carrier equipment.” Now, if you are a future client of ours, I’ll have to warn you – I can be a bit of a smart-ass. Why can’t work be fun? Besides…I was in the Navy for 11 years, what do you expect. 
Indoor Fan Motor -- Indoor fans circulate the air from your house and through the system. Age and dust buildup are the two biggest contributing factors to their failure. When they are starting to fail they will often make noise. Failure of the fan will result in no heating or cooling, and if it is not repaired soon, it can cause other components to fail.
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.
Duct cleaning has never been shown to actually prevent health problems. Neither do studies conclusively demonstrate that particle (e.g., dust) levels in homes increase because of dirty air ducts or go down after cleaning. This is because much of the dirt that may accumulate inside air ducts adheres to duct surfaces and does not necessarily enter the living space. It is important to keep in mind that dirty air ducts are only one of many possible sources of particles that are present in homes. Pollutants that enter the home both from outdoors and indoor activities such as cooking, cleaning, smoking, or just moving around can cause greater exposure to contaminants than dirty air ducts. Moreover, there is no evidence that a light amount of household dust or other particulate matter in air ducts poses any risk to health.

How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .
The sky is the limit. I am a big fan of adding zoning systems, but realize that this will typically add $2,300 to $3,500 (or more) to the price. “Why a price range, isn’t it just a part?” No, the part then has to be installed, and the customized ductwork required will vary based on the difficulty of the job and layout of your attic. It is very labor intensive, and most people don’t do it right. It should also include a bypass damper and ductwork! Simply put, the more you add, the more it will affect your HVAC installation cost.
HVAC professionals in the US can receive training through formal training institutions, where most earn associate degrees. Training for HVAC technicians includes classroom lectures and hands-on tasks, and can be followed by an apprenticeship wherein the recent graduate works alongside a professional HVAC technician for a temporary period.[33] HVAC techs who have been trained can also be certified in areas such as air conditioning, heat pumps, gas heating, and commercial refrigeration.[34]
I own an HVAC company. Dirt in your ducts stays there and hurts no one. It is like dirt on the ground outside. This industry was infiltrated by a bunch of money grubbing low lifes years ago. As a credible company, we do not clean air ducts. Some who were credible probably signed on not knowing what else to do or to try to make a buck another way. These companies, because they also do HVAC work not only rip off private homeowners, they are ripping off legitimate HVAC company's customers and the integrity of what can and should as a rule be a great service industry. Some probably have gotten into this to simply offer what competitors who were ripping off their customers were offering. Anyone cleaning ducts is in my opinion raising a big red flag that they cannot and should not be trusted. Political pressure from NADCA, advertising dollars, manufacturers and marketers of duct cleaning equipment, and intense competition for the customers is the only reason the government and adverstising companies have not run them out of business and that this cancer perpetuates itself.
Did you know that cleaning your ducts and vents can help airflow and increase energy efficiency? According to the Environmental Protection Agency (EPA), keeping your air ducts and vents clear can increase energy efficiency and indoor air quality. While the cost to clean ducts and vents might sound high, the benefits to homeowners–especially those sensitive to allergens–is worth considering.

I've been in business in Florida for 25 years and purchased a $12,000 duct cleaning system 4 years ago. In the last four years I've cleaned 5 duct systems charging around $400 each. Not a very good return on investment. What I have been doing most the time is I get a call by someone panicked because they called some low priced company to inspect their system and were told they have dangerous black mold. Then they call me to have a look. Most the time they don't have mold, ducts look very clean. However the coils are dirty and the inside of the air handler cabinet needs cleaning. Keep in mind not every system can handle supper high efficiency filters! These filters can block air flow quite a bit right out of the package. Many older systems can't handle pleated filters due to increased static pressure. "Back rooms with low air flow". I have taken many hours of classroom study on indoor air quality. Never got any certification because I don't want to pay another organization dues yearly. I think the problem with duct / system cleaning is most people are suckers for low priced scams that are rip- offs . People call me all the time and ask how much? When I tell them average $400 they hang up. I know I do the job correctly and honestly, and they are going to get racked over the coals by the scam artists by calling $79 whole house duct cleaning guys. People need to check internet, angies list and BBB reviews. But keep in mind even reviews need to be sifted through your rational person filter.


While your HVAC filter is designed to trap particulate matter and prevent it from entering your air ducts, particles often still get through. The number of particles your HVAC filter traps is directly connected to the quality of air in your home: the lower the quality of air, the more particles will be present, and the more particles are likely to get through the filter. If these particles are allowed to build up, your HVAC system can become less efficient, operating longer to heat or cool your home. An inefficient HVAC system can result in inconsistent heating or cooling, higher utility costs, and expensive HVAC unit repairs, such as an A-coil or blower motor replacement if the problem is left unchecked. Air duct cleaning from Sears, which focuses on the dirt in your air ducts, can boost the efficiency of a dirty HVAC system, cleaning out the particulate matter that can hinder HVAC effectiveness and affect your health.

Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]
PickHVAC Tips: Don’t be sold on systems with features you don’t want or need. Called “upselling,” it is rampant in the HVAC industry. Some features are nice – if you want them. If your single-stage furnace was loud and pushed out cold air at the start of the cycle, then a two-stage model will improve those issues. If you didn’t notice them, the upgrade will be a waste of money. That’s just one common example.
A year and a half ago (fall of 2015) we replaced the furnace and air conditioner. From what we could determine this was the third forced air furnace and second air conditioner unit for the house. As part of the installation, we changed out the two 6″ ducts feeding the second floor with 8″ ducts. The idea was to get more cold air to the second floor in the summer. It worked and for the first time the second floor and first floor temperatures were the same when the air conditioner was running. Of course, to make the system work I close down upstairs duct damper doors in the winter and open them up in the summer.

Brands like American Standard, Trane and Lennox cost the most. Goodman is the cheapest. The rest populate the middle of the spectrum. Here’s something to know: The quality among brands isn’t as great as price differences. The difference in prices reflect that some customers want “bargain” equipment to save cost and others want “premium” equipment they believe will run longer with less trouble. Therefore, each manufacturer has priced to meet consumer perception.


With today’s consistently rising energy costs, improperly sealed windows, ductwork, and poor insulation can pose serious problems for many home and business owners in Arkansas. Wilson's Heating & Air Conditioning provides complete HVAC system servicing including sales, installation, maintenance and repair, and offers numerous practical solutions that will reduce your energy costs.
When these aren't properly maintained and sanitized, they can build up dust, pollen, and even mold. This means when the air conditioner or heater turns on, the spores are released into the air for you to inhale. While some are less harmful, people who have allergies or sensitivity to certain spores will react negatively. Plus, mold is dangerous for anyone to ingest and should be avoided by regular maintenance.
Venice warns homeowners to beware of air duct cleaning scams, especially the sort where unscrupulous cleaners offer a $49 special deal but start piling on extra fees. “It’s a bait and switch scam where they say they’ll offer unlimited cleaning, but then they throw around terms you might not understand, such as extra fees for a ‘main duct line,’” he says. “And many times, these cleaners end up walking out the door with twice the amount of money a reputable duct cleaner would charge. They’ve gotten very sophisticated at upselling.”

Compressor -- Compressors are outdoor components in your system. The compressor is the pump that circulates the refrigerants through the air-conditioner. You can hear it when it's running so you'll know if it's working just by listening. If it starts getting louder, your compressor is about to fail. If it makes no sound when it should be on, it has already failed. Compressors fail for a number of reasons. Most often they fail due to strain from another failed part such as the fan motor. Electrical storms can also damage compressors. If the sound from the compressor gets louder or if you see a decrease in performance, you should have your compressor checked. A failed compressor will not heat or cool your house.
Dehumidification (air drying) in an air conditioning system is provided by the evaporator. Since the evaporator operates at a temperature below the dew point, moisture in the air condenses on the evaporator coil tubes. This moisture is collected at the bottom of the evaporator in a pan and removed by piping to a central drain or onto the ground outside.
I have worked cleaning HVAC in my area for almost 5 years. I always do a thorough inspection and cleaning, providing before and after photos. I have completed some jobs where I felt that it was not entirely necessary, but ultimately what the customer wanted. With that being said, I have endless photos of unspeakable horrors. Hotels are usually nasty, post construction mess is certain, pets and kids create lots off debris, bugs congregate and die, then spiders set up and die, I have even had one supply that was nearly plugged with sand!
I noticed a lot of negative feedback, though unfortunately there are many dishonest companies out there. I currently work with a company that cleans duct work and we DO NOT use any scare tactics or up sell services or equipment. Once every 10years of course there are exceptions. We clean supply, returns, air handler, housing, motor, and fan. Though be discerning when qualifying anyone to work in your home. I would ask for REAL REFERENCES to contact.

Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
And if you have flex duct and/or fiberglass ductboard in your home- the last thing you want is a big brush or anything abrasive running through it. Even high-pressure air can erode ductboard so I wouldn’t clean it with anything. If it becomes contaminated, get rid of it and install real ductwork. If your ductwork is accessible in the basement – the best thing to do is take it down and manually clean it if it’s full of junk. It’s not going to cost a nickel more to do that than to pay $500-1000 for a ‘duct cleaning machine” AKA big blower and vacuum – to do the job.
Excalibur Water Systems helps solve the water challenges around the globe with water solutions for any possible water concerns in: water hardness, filtration of any contaminant, bacteria removal and high purity water needs and also comes with a warranty of up to 20 years at no extra cost. The best warranty for the water treatment equipment industry.

Just had my HVAC System restored and working again on a Sunday and before the 104 weather tomorrow!!!! Called Big Mountain Heating and Air and spoke to very helpful woman named Martina. She connected me to a Technician named Josh. He was at my home within a few minutes and tackled my Honey Well system's issues. He is both skilled, personable and better yet, he got my system up and going and safe. He installed a surge suppressor on the system to prevent power surges that can kick off any system, when the electric company has to reduce power, etc.  I will be using Big Mountain in the future. Truly grateful for such good service and people. Thank you!  I recommend this firm to everyone!


I called a company name “GREEN RHVAC” with their $29.00 one system air duck cleaning. When the guy came with a truck I asked him to tell me how much he will charge and he said that if he gave me price and I didn’t want the service then he would charge me $89 or he would tell me how much he charge me after he finished the work. I immoderately sense that I made mistake to call him to my house. To cut my lost I asked him to give me the price and it was $1600 for two systems house. I paid $100 to him for my lesson to learn and search online to find this site is very helpfully and I should do it before to call anyone for air duck cleaning.

Bigger is not necessarily better when it comes to HVAC systems, and smaller isn't always more efficient. If you have too small of a system, your system will be running constantly as it tries to keep up with the temperature. If you have too large of a system, it won't run long enough to keep up with the humidity. In order to handle both temperature and humidity efficiently, an HVAC system should run for around 30 minutes at a time. If your system is staying on too long or shutting off after only around 10 minutes, you are not getting efficient performance.


As I type this, I am having my ducts cleaned. About 30 including returns and the furnace. $543.00. I am watching the team do it and can see the clear vacuuming tubing and how dirty it has become. I like the gentleman’s comment on “stick your head in your vacuum and breath”….I get it. The team showed me the machine and it’s filtration system…and they will show me it again after the cleaning. However, like I said before, I am actively seeing the tubing that is clear before they start and how dirty it is once they begin and continue cleaning. Reputable company and not a “fly by night” coupon service. People don’t be so cheap, that is your problem.

Sounds like your first hvac company was ripping you off. Ask your new company to go to your coil and see if there is a leak. If there isn't the last company was just lining their pockets. If you have had ducts unhooked for a long time I would recommend duct cleaning, trust me I'm not a fan of duct cleaning myself. I have done hvac for 20 yrs. in GA. When I just bought a home built in 1996, we had all the ducts replaced immediately.


DIY: Most DIY installations go smoothly. The major brands have compatibility checkers to see which of their models will work with the wiring your old thermostat is using. Potential problems involve the need for a C-wire, or common wire, when the existing bundle doesn’t include one. There are solutions discussed in our Thermostat Buying Guide, linked to below.
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.
If no one in your household suffers from allergies or unexplained symptoms or illnesses and if, after a visual inspection of the inside of the ducts, you see no indication that your air ducts are contaminated with large deposits of dust or mold (no musty odor or visible mold growth), having your air ducts cleaned is probably unnecessary. It is normal for the return registers to get dusty as dust-laden air is pulled through the grate. This does not indicate that your air ducts are contaminated with heavy deposits of dust or debris; the registers can be easily vacuumed or removed and cleaned.
×