My vent covers have lots of mildew. They look bad! I live in a very humid climate in a condo. The handyman here has offered to take those down, wash them, sand, & then spray paint them with a mildew resistant paint. He said that he will leave them off overnight to dry. I am wondering if this is safe to breath the AC blowing out into the open all night??. ! Guess it is better than the mildew!?
In reading through all this about duct cleaning, THE ONE preventative measure people need to realize is that a poorly installed HVAC system that is not sealed and air tight to ensure that ALL indoor air passes through a GOOD air filtration system IS THE best means of ensuring your ducts remain clean. Duct cleaning does not now and will NEVER improve an HVAC systems efficiency. Proper maintenance and installation are the key just as improper installation practices allow for dust infiltration into the duct system. I am a state licensed contractor in Texas, and unless people have their hvac system sealed and/or properly installed, duct cleaning is an absolute waste of money. My duct system is 12 years old as is as clean today as the day I installed the system with ductwork. SO before ANYONE jumps on the bandwagon of duct cleaning, get with your hvac professional FIRST.
I am NADCA Certified Air Systems Cleaning Specialist. Over the years I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
You should be aware that although a substance may look like mold, a positive determination of whether it is mold or not can be made only by an expert and may require laboratory analysis for final confirmation. For about $50, some microbiology laboratories can tell you whether a sample sent to them on a clear strip of sticky household tape is mold or simply a substance that resembles it.
Some systems include an "economizer mode", which is sometimes called a "free-cooling mode". When economizing, the control system will open (fully or partially) the outside air damper and close (fully or partially) the return air damper. This will cause fresh, outside air to be supplied to the system. When the outside air is cooler than the demanded cool air, this will allow the demand to be met without using the mechanical supply of cooling (typically chilled water or a direct expansion "DX" unit), thus saving energy. The control system can compare the temperature of the outside air vs. return air, or it can compare the enthalpy of the air, as is frequently done in climates where humidity is more of an issue. In both cases, the outside air must be less energetic than the return air for the system to enter the economizer mode.

Did you know that cleaning your ducts and vents can help airflow and increase energy efficiency? According to the Environmental Protection Agency (EPA), keeping your air ducts and vents clear can increase energy efficiency and indoor air quality. While the cost to clean ducts and vents might sound high, the benefits to homeowners–especially those sensitive to allergens–is worth considering.


The HVAC installation costs below are based on residential installations only, and are priced for a single unit. Two units should be about twice the price. “Tim, shouldn’t there be a discount?” If people start giving you discounts, they are probably charging you too much to begin with.  That’s our philosophy anyway. Twice the parts and time should be twice the price from a fair contractor. The prices listed include component parts (with warranty), labor, and all materials for a complete HVAC installation.

Furnace Circuit Board -- The furnace circuit board controls a variety of functions. It not only handles the regular operation of the furnace, it also monitors the furnace's various safety circuits. Over time, vibrations from the furnace can weaken solder point and cause them to separate. Dirt and debris can cause short-circuits that damage the board. Failure of the circuit board can cause a variety of effects ranging from the fan not turning on to the complete shutdown of the furnace.
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.

What you might not know is that the brand you choose is one of the most important factors in determining a fair HVAC installation cost. So, before delving in-depth, let’s take a quick look at the average prices of a new air conditioner and matching coil by brand…keep in mind, these are the average prices (by brand) that contractors pay for your AC equipment, and it is meant to give you a rough guideline until you are closer to buying:

How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .
Greetings from Mama Duck from Ductz of Greater Atlanta. These are some awesome comments and a few are from high quality duct cleaners that I personally know. After 19 years in this industry I agree that a government agency is not always up to date with their knowledge but won't admit it. If they were out in the field with our technicians every day they would upgrade their info. I get calls all the time where customers have been taken advantage of by "go and blow" companies. The customers don't know what they don't know but many are too lazy to do the research and are just looking for cheap. The industry has gotten a bad rap due to these con artists but the customer has to take some responsibility. I ask them why they would want to do business with a company who lies to them in print? Are they stupid or just cheap? Thankfully there are those of us in the industry who are working diligently to raise the bar on quality, protect the consumer and perform high quality work. At Ductz all our technicians are NADCA certified, trained by the best in the industry and know how to clean the entire system.

Heating, ventilation, and air conditioning (HVAC[1]) is the technology of indoor and vehicular environmental comfort. Its goal is to provide thermal comfort and acceptable indoor air quality. HVAC system design is a subdiscipline of mechanical engineering, based on the principles of thermodynamics, fluid mechanics and heat transfer. "Refrigeration" is sometimes added to the field's abbreviation, as HVAC&R or HVACR or "ventilation" is dropped, as in HACR (as in the designation of HACR-rated circuit breakers).
Whether you’re starting your air conditioner for the first time this year, or a unit isn’t running properly and you need to service an air conditioner, following a few simple steps can save you time and money. While some service jobs should be left to a professional, there are several do-it-yourself fixes you can do to keep your air conditioner cooling all summer long.
The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
So, whether you need an AC repair or you’re in search of a new heating and air conditioning system—or you need a new water heater now–you can count on our team in North America. We’re experts in AC and plumbing repair, and offering top-notch AC and plumbing service is what we do best. Call Service Experts 24/7/365 at 866-397-3787 or request an appointment online today, and don’t forget to check out our coupons page for savings on your AC or plumbing repair service.
Had our ducts cleaned late April, 2016. Sodium Chlorite was sprayed into ducts after cleaning. Ever since, we have been bothered with eye and nasal passage irritation because of a “chemical” and “musty” odor. This odor is present whether or not a/c is on.) We are told the sodium chlorite (“EnviroCon, manufactured by Bio-Cide International) is used in hospital and nursing home settings and is not hazardous to health. The air duct company’s suggestion is that they come out and spray even more sodium chlorite…we absolutely don’t want this done! Have had various other recommendations about what we need to have done to remedy our problem. We will be unable to stay in our home if a resolution cannot be found. We’d be willing to replace the ductwork if necessary. (One professional suggested that the cleaning may have “knocked something loose” inside the ductwork and that is the source of the irritant.) This home was built in 1920…no idea when the present ductwork was installed. Any suggestions would be appreciated.
I am in need of HVAC ADVICE!! I need a new furnace badly, mine is cracked. I have bought both a 95 % AFUE furnace and a 5 Ton evap coil, I figured it should all be replaced at once for both cost and efficency. My question is with all the negaitive things I have heard about companies ripping you off, what type of price should I pay someone for putting in those two items and bringing everything in my attic up to code? I have been quoted $550 - $ 3300. Wide margin here!! Then of course comes the licencing part!! I know in my heart that I should use a licenced contractor but I have had such bad luck and prices from them that honestly one that was licened in Ga. and just not here in TN and is a tech. which charges 1100 - 2200 less sounds good as so long as I pay some type of Profenial HVAC person say $100 to inspect the work after its done and before I pay them.
The fact is if they are dirty why not clean them. As for the Dr’s comment about if it is not disrupted it is fine. As a pet owner sometimes un disrupted pet hair will sit in the corner of a room or under a counter un disrupted but I still clean it when I notice it. Just because you cant see it doesn’t mean you should leave it there to collect more and more. The people that don’t want there air ducts clean either simply cant afford it but would like it done. OR! the crowd that are to cheap.. You should Clean all portions of your house.
Is duct cleaning worth it? There is not a yes or no answer that suits everyone. On an Air Force base, the system was not air tight and there was leakage around the filters. The system got dirty. A professional company was called out. The Duct was big enough that a technician could go inside the metal duct and clean it. There was a new Air Handler installed and things were sealed up better. in this case it was worth it.
I called a company name “GREEN RHVAC” with their $29.00 one system air duck cleaning. When the guy came with a truck I asked him to tell me how much he will charge and he said that if he gave me price and I didn’t want the service then he would charge me $89 or he would tell me how much he charge me after he finished the work. I immoderately sense that I made mistake to call him to my house. To cut my lost I asked him to give me the price and it was $1600 for two systems house. I paid $100 to him for my lesson to learn and search online to find this site is very helpfully and I should do it before to call anyone for air duck cleaning.
HRV/ERV Ventilators: These whole-house ventilators exchange air. They are ideal for homes with what is called a “tight envelope,” homes where house wrap has been applied and airgaps in the attic, around windows, doors and outlets have been sealed. Air in these homes becomes stale and polluted, so exchanging the air is important to IAQ. Heat recovery ventilators (HRV) are designed for cold climates. Energy recovery ventilators (ERV) are best for warm climates.  Your cost for an installed HRV or ERV will range from about $2,000 to more than $5,000 based on its capacity and features.
Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.

The use of furnaces, space heaters, and boilers as a method of indoor heating could result in incomplete combustion and the emission of carbon monoxide, nitrogen oxides, formaldehyde, volatile organic compounds, and other combustion byproducts. Incomplete combustion occurs when there is insufficient oxygen; the inputs are fuels containing various contaminants and the outputs are harmful byproducts, most dangerously carbon monoxide, which is a tasteless and odorless gas with serious adverse health effects.[14]
I am a service technician [since '92].....and as to double filtering.....I have never recommended it. Granted.....it would be noticeably helpful if the fiberglass filters are the main ones used [which I also never recommend.....as long as system can deliver appropriate air flow with a pleated cotton filter...and any decent service tech can check the air flow for proper cfm]. Any particles small enough to pass through a pleated cotton filter are going to pass through a second filter as well....unless the second filters are so tight that the system is starving for air flow. Has anybody ever accidentally put two filters in their automatic drip coffee maker? What if cars used two fuel filters or air filters? I have told some homeowners to try using second filters at each register [the black thin filter material cut-to-fit....same type used in many window air conditioners].....but I only suggest this when I know they will still get at least 400 cfm per ton of air flow [350 absolute minimum]......as some homeowners know others who say it has helped and it gives them a peace of mind knowing they are doing something to help contribute to a solution, so it HAS to help [even though I think it falls in the "one-born-every-minute" category.....similar to duct cleaning].
Concrete Blocks -- Concrete blocks are used in foundations and are often found in full basements. Insulating the spaces in the blocks is not the way to insulate them as the heat energy will travel along the concrete itself. The best way to insulate with concrete blocks is to use insulated concrete blocks, which have polystyrene incorporated into them.
You might also want to check your home for thermal insulation if you live in extreme heat or freezing temperatures. Insulation keeps the heat and cool air in your home, which can lead to a lower electric bill. If the heated or cool air leaks out, your system turns on more often. There are various types of insulation that you can install in your home and a home energy auditor can point out the best places for it in your house.

If you are replacing your air conditioning system, make sure that the unit is the proper size for your needs and that all ducts are sealed at the joints. A unit that is too big will cycle on and off frequently, resulting in poor moisture removal, particularly in areas with high humidity. Also make sure that your new system is designed to manage condensation effectively.
×