So HVAC sent Tony Diaz to my house. I was at work so he was subjected to the most excruciatingly exacting woman on the planet (my wife). Tony impressed her with his friendliness, professionalism and the obvious jouneyman-level knowledge of his craft. He found literally --burnt-out-- parts in our system and replaced them. It cost us a bit but I know enough about the parts to see there was no gouging on the parts and a fair rate for the labor. It wasn't cheap but it was fair and worth every dime.
Refrigerant Metering Device -- Every HVAC system has one of these, and heat pumps have two. They regulate the amount of refrigerant going through your air-conditioner. If it fails, either too much or too little refrigerant will course along the lines and either not perform well or will overwhelm the compressor and cause it to fail. A total failure of this component will result in a complete loss of operation.
I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.
Dehumidification (air drying) in an air conditioning system is provided by the evaporator. Since the evaporator operates at a temperature below the dew point, moisture in the air condenses on the evaporator coil tubes. This moisture is collected at the bottom of the evaporator in a pan and removed by piping to a central drain or onto the ground outside.
If you are using existing ducting, it will have to be inspected. Proper ducting loses around 2% to 5% of your energy. Old, leaking ducts can lose 50% or more. A contractor will need to have the ducts inspected and replace any parts ahead of time. If you are changing the size of your HVAC system because of significant changes to your home, you might need to replace the ductwork regardless.
I have worked cleaning HVAC in my area for almost 5 years. I always do a thorough inspection and cleaning, providing before and after photos. I have completed some jobs where I felt that it was not entirely necessary, but ultimately what the customer wanted. With that being said, I have endless photos of unspeakable horrors. Hotels are usually nasty, post construction mess is certain, pets and kids create lots off debris, bugs congregate and die, then spiders set up and die, I have even had one supply that was nearly plugged with sand!
Your HVAC unit and air ducts deliver heated or cooled air throughout your home year-in and year-out. The air your HVAC unit produces travels through your ductwork and heats or cools your home via the air vents in each room. The dust and other particles in your home’s air are known as particulate matter, which the EPA defines as "a complex mixture of extremely small particles and liquid droplets." The EPA also notes that "particle pollution is made up of a number of components, including acids (such as nitrates and sulfates), organic chemicals, metals, and soil or dust particles." Having clean air ducts means fewer of these particles moving through your home. If you remove your furnace filter and hold it up to the light, you can probably see several hundred of these minuscule particles floating in the air. 
PickHVAC Tips: Electricity resistance heat is the most expensive heating type. You don’t want one of these unless you’re heating less than 30 days per year. The upfront cost of an electric furnace is much lower than the cost of a gas furnace. However, operating costs are two to three times higher. If winters are cold where you live, you’ll waste your upfront cost savings in just a few years of high electric bills.

I read your article with interest and think it is a good start. One service that is always talked about is fogging ductwork for sanitizing. Many companies offer this service for disinfecting or adding a clean smell to the ductwork. Before any chemical or disinfectant is used, please read the MSDS (Material Safety Data Sheet). You might be surprise on what you are putting into the air stream. This is a high profit service and should be explored thoroughly before purchasing,


We hope you found this article on a fair HVAC installation cost helpful. In the end, you’ll be alright so don’t worry too much. Do your research on reputable air conditioning contractors in your area, and spend time making sure that you have a company that you can trust – it will cost you less in the long-run, trust me. Take your time, follow the tips above, and you will end up with an HVAC installation cost that is more than reasonable, keeping your family comfortable for years to come. For more on topics like this, see: ASM’s Air Conditioning Blog.
The amount of time it takes to clean a residential HVAC system depends on many variables such as the size of the home, the number of systems, the extent of the contamination and the number of HVAC cleaners performing the job. Ask at least two contractors to inspect your system and give you a time estimate for your particular system. This will give you a general idea of how long the job should take as well as an idea of how thoroughly the contractor plans to do the job.
I even asked if this is something they don't do, as in services on a Saturday night.  I was told by the receptionist that they do and I would just be ok calling another company if they is not  part of their services. They again assured me someone WILL call me in 10 mins.  Well, unless their definition of 10 mins is never, then they got it wrong as I am still waiting to be called 5 days later.
Unfortunately, manufacturers and contractors don’t publish this information…it’s a secret. Why? Who knows…but we have access to a full contractor pricing database of 1,000’s of different units in our online HVAC installation cost calculator, so let’s choose one for our example calculation. We’ll go with Carrier equipment, since our readers always bother us about them (despite us telling them that they are overpriced):
Indoor Fan Motor -- Indoor fans circulate the air from your house and through the system. Age and dust buildup are the two biggest contributing factors to their failure. When they are starting to fail they will often make noise. Failure of the fan will result in no heating or cooling, and if it is not repaired soon, it can cause other components to fail.
I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.
Humidifiers/Dehumidifiers: Humidifiers add needed moisture to the air in winter and very dry climates. Dehumidifiers remove dampness any time of the year. Central air conditioners dehumidify too, but in very humid climates, you might want to remove humidity without also cooling the air. You have a good range of options for both of these HVAC accessories. Whole-house humidifiers cost $350 to $800 installed, while dehumidifiers are $1,250 to $2,000 or slightly more.
Capacitors -- Capacitors help your HVAC motor start from a standstill. Over time they can weaken. As they weaken, they cause the motor to run hotter. This can shorten the life expectancy of your motor. Once a capacitor fails, the whole motor will stop working. You usually won't notice that a capacitor has weakened until your motor stops turning on.

I forgot about a pot of sweet water I had on the stove to boil. When I finally smelled it the kitchen and dining room I=was smoke filled. I mean thick smoke. I opened doors and windows for a few hours to remove the smoke but the smell is still here and terrible. I had to use the AC and that smell started coming out of the vents. Now what do I do? I have COPD emphysema so I have to be very careful about what I inhale. I already have inhaled too much smoke from all of this which has hurt my lungs even more. I can’t afford for them to get worse over this. How can I get the right person to come out and clean the ducts and furnace or is that the only way to remove that burnt smokey smell. The pot never caught on fire but it sure did produce a lot of smoke. I already have replaced the filter on the furnace. It needed it even though it had just been replaced just last week. I need help or really my lungs need help. Who do I call here in Indpls IN.
Humidifiers/Dehumidifiers: Humidifiers add needed moisture to the air in winter and very dry climates. Dehumidifiers remove dampness any time of the year. Central air conditioners dehumidify too, but in very humid climates, you might want to remove humidity without also cooling the air. You have a good range of options for both of these HVAC accessories. Whole-house humidifiers cost $350 to $800 installed, while dehumidifiers are $1,250 to $2,000 or slightly more.
Though this installation is not always complicated, it's best to work with an air conditioning contractor to ensure it's done correctly. Permits are usually required for this type of work and can be obtained by a state-licensed contractor. You should not attempt to install central air conditioning on your own since you need a license to handle the refrigerant chemicals (Freon) involved.
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
My heat pump/hvac system is not blowing cold air anymore, got checked out was told compressor broken. was told it cost  almost the same to repair/replace they recommend whole system. It's the same company that installed it 18 years ago, telling me that system is old and it will cost $9-10k for new system, because furnace has to be replaced with new hvac. what to do, need answers thanks????
We moved to a house built in 1965 from a 1915 house with a dirt basement. Against what I anticipated, the 1965 house was much dustier. It was like felt on top of everything. I cleaned and cleaned and it did become less dusty over time. We then found out a cat lady with over 2 dozen cats lived in the house in the past. We then had to get our furnace replaced and I was able to look down some of the duct work, the dirt and debris was 3-5 inches deep. Additionally, the basement ducts were entirely plugged with debris including dirt, seeds, ants, toys, etc. I had already removed what I could from those. We had our ducts cleaned last year, and the dust in the house is greatly reduced. Also have lost the runny nose I got after moving here. There are duct cleaning con artists out there, but ours did a good job.
My Carrier furnace occasionally (one-two times a day) does not start. It shows error code 15 ("BLOWER MOTOR LOCKOUT -This status code indicates the blower failed to reach 250 RPM or the blower failed to communicate to the variable speed furnace control within 30 seconds after being turned ON in two successive heating cycles."). However, when I turn off and on the furnace power switch it starts and runs fine for a while. Sometimes it runs fine all day, but does not start only once in the evening or in the night. It is 13 years old I was thinking to replace whole thing if repair cost is too high. But I am not ready to pay $10,000. 

Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]
Furnace cleaners are mostly young men, I know this, I have been one for 15 years or so……so heres the truth, if there are any allergies, children, older people with health issues, we are GOING to make money. do not tell the company you have hired about any health complication. they are salesmen. and they don’t care about you. or your money. make sure they do a good job, then kick them out. you don’t need all the bells and whistles they wanna sell you. any idiot can clean duct work, like I said, I am one of them. I am very good at it, but I don’t have the back bone to sell a widowed old lady a humidifier that she doesn’t need for 500 bucks, overall, if you think you need this service done, which you probably don’t, get it done, do not spend anything over 300$ and do not do it again for at least ten years.
HVAC System Quality Installation Contractor Checklist -- This checklist identifies all of the steps the contractor has taken for the Energy Star Certification and identifies what work the contractor has done. If the system is later modified, this checklist can help identify what was done to proper Energy Star specifications and what was added later that may not meet the requirements.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.

An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.

While a lot of people understand the consequences of AC problems throughout the summer, the summer comes with its own set of unique issues that require a call to the plumber, too. Whether it’s a malfunctioning sprinkler system or a sewer line backup, Service Experts can help. We’ve encountered it all, and you won’t have to worry about any of it with our 24/7/365 Emergency Plumbing Service. When you need a plumber, we are here for you. And, just like all of our other services and products, any plumbing repair or work completed by Service Experts is backed by the same 100% Satisfaction Guarantee*.
Had duct cleaned (apartment) however, dust is still settling throughout the apartment. Contractor said no other cleaning necessary until two (2) years. Is there a time period before dust no longer settles prior to that time? Should the vendor had worn a mask? He did not cover his face the vents and dust was blown throughout the apartment (had family help with the cleanup). I had to leave when they left because I have asthma and I couldn’t breathe without coughing. Please help!

I to had an odd layer of white'ish dust building up especially during seasonal periods when the HVAC ran a a lot. I carefully swept up the fine dust into a small pile and had it analyzed. Turns out it was very fine fiberglass powder dust. It turns out it is the insulation form the attic! (My attic has blown in insulation). Turns out if you (I) had small gaps around my HVAC registers in the ceiling whee the airs blows into the room. What occurred in my case was that the exiting air at that seam creates a vacuum effect at the grate vent cover and draws and then blows fine insulation dust from the attic into the house. Removing each register grate and sealing each tin outlet gap with calking between the dry wall ceiling and tin fixed the issue. A couple were so bad with bowed gaps I had to screw down the bowed tin to the attaching stud better. Checking the very same glass top desk that catches and shows any dust accumulation now shows only very small amounts of normal house dust build up over several weeks. A big, big improvement. You might have a look by simply removing a couple vent covers yourself.


I hired duct cleaning company out of "Service Magic" website. I did not realize the name of his company was Duck cleaning of Central Florida...that should have given me a hint.. The guy did a very poor, incomplete job, and ruined a closet full of clothes when he sprayed up to clean a vent instead of taking it down and cleaning it outside. He left me with more than 1/2 dirty vents and ducts, did not do the air handler in the garage and failed to fog the system. He spent 6 useless hours at my residence and now his insurance is denying coverage..very disappointed in Service Magic....
You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 

in response to this reply " should your ducts be cleaned", i have to politely correct the person who answered this. you are not using common sense. first, most of the country uses metal duct work, so for you to say what you did, is wrong. second, the duct system in a house is a circulatory system. that means it draws air into the furnace, it gets filtered, and then it is blown out into the house to heat or cool. So, obviously that air is being brought into the house from somewhere right? Yes, its coming from the outside where there are many allergens and dust particles . For you to says that about whether a duct system is sealed or not, makes no difference. The air is coming from somewhere right? It has to originate from somewhere right? Just look on top of your cieling fan. If there is a bunch of dust up there, then there is obviously a bunch in your ducts. And the duct air is being circulated every day, and every hour through your house. Its simple, dust collects everywhere in your house. Imagine if you never dusted your shelves, or tv? There would be a ton of dust after a while. Well, now think about the air in the duct system. Of course theres gonna be a ton of dust in there. For you to say that it is not benififcial to clean the ducts, is plain ignorant. 90% of the air we breathe is in our household. Wouldnt you want that air to be as dust and allergen free? I could go on for hours about the benifits of duct cleaning, but i just wanted to make a quick point that the person whose says it is not benificial to clean them, is not using common sense. Not to mention, giving the people who clean ducts for a living, a bad name. Use your head .
I even asked if this is something they don't do, as in services on a Saturday night.  I was told by the receptionist that they do and I would just be ok calling another company if they is not  part of their services. They again assured me someone WILL call me in 10 mins.  Well, unless their definition of 10 mins is never, then they got it wrong as I am still waiting to be called 5 days later.
Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.
Monday the following week, no phone calls, or follow up.  I call to get an update and am told that they cannot install my system because they don't have time.  I ask what does that mean, one year? One week? Until the end of summer they say.  What does that mean I ask?  They say at the end of September.  I say thank you for wasting 1 month of my time.
Although i love to burn candles, depending on the type your asking for problems big ones! At work one day i had been talking with co workers about these black shadows that were appearing on my ceilings and higher wall areas. They seemed to in the corners and along the stud supports , i could even see what i thought to be where all had been nailed. There would be dark shadows perfectly straight across my ceiling and then real dark circels every few inches within the lines. I thought it was the propane heat but learned quickly that oil heat will do that but not normally propane. A co worker brought me a magazine with a huge article about candles and what actually burns off them when lit, an ashy soot that is attracted to the areas on walls and ceilings that omit the most heat or warmth, of course where the drywall and studs meet and corners of the room. Its been about 8 years since i painted the entire house. I started bending to my love for candles again in the last 3 years, surprise i will be spending part of my summer re painting again!! No more candles ,well maybe at the holidays LOL
Appliance Repair in Fayetteville Appliance Repair Santa Barbara Lansing, MI Appliance Repair Augusta, GA Appliance Repair Appliance Store Raleigh York Appliance Repair Appliance Repair Austin Appliance Repair Topeka Appliance Repair Louisville Appliance Repair Salem, NH Paducah, KY Appliance Repair Evansville Appliance Repair Toms River, NJ Appliance Repair Appliance Repair in Easton, PA
×