These factors are included in a "Manual J" calculation. Contractors who make these calculations before recommending a size can take a couple of hours collecting the information and making the calculation. If your contractor doesn't do it, there are services that will do it for around $99. If you're feeling particularly on the ball, there are also free online calculators.
An air conditioning system's SEER is especially important if you live in a climate that changes temperature dramatically. The SEER is determined by the cooling output during the winter divided by its electric input during the winter. The higher the rating, the more efficient it will be. In January of 2006, the U.S. put standards in place for cooling units which are still in effect today. They must have a minimum SEER of 13. So, if you live in a home with a system installed before the new standards went into effect, consider having it replaced. SEER 13 units increase home efficiency by 30 percent.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.
As I type this, I am having my ducts cleaned. About 30 including returns and the furnace. $543.00. I am watching the team do it and can see the clear vacuuming tubing and how dirty it has become. I like the gentleman’s comment on “stick your head in your vacuum and breath”….I get it. The team showed me the machine and it’s filtration system…and they will show me it again after the cleaning. However, like I said before, I am actively seeing the tubing that is clear before they start and how dirty it is once they begin and continue cleaning. Reputable company and not a “fly by night” coupon service. People don’t be so cheap, that is your problem.
Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  
The number of years an HVAC system lasts depend on the type and brand of components that make up your system. The lifespan of an air conditioner averages between 15 and 20 years. The life expectancy of a tankless water heater is approximately 20 years, while a storage water heater is closer to 10-15 years. Ducts may need replacing within 10-15 years. Your equipment will have a longer life if you have regular tuneups and maintenance to keep everything in good working order. If you’re having repair problems and your HVAC system is over 10 years old, it’s a good time to consider the costs and benefits of repairing vs. replacing. Energystar.gov provides the following tips to help you decide whether to repair or replace:
I was told that 15 out vents would be cleaned and one main vent. the guy came over and gave me an estimate of $500. I had acquired a groupon for $49. the guy said just doing the out vents and one main vent would accomplish nothing. Now I am in dispute with the groupon people for a refund which they won’t give and have to go ahead and waste the money and let them do it. Is their doing the 15 outvents and one main one going to accomplish anything?
I just bought a home, and the sellers clearly never had the air ducts cleaned. This is, unfortunately, typical of their neglect of the home, so I am not surprised. I was cleaning around the wooden floor registers, and I took the registers off. I found nests of some sort...all kinds of really gross stuff!! I am calling now to schedule duct cleaning for my new home. Anyway, it is very easy to check to see if you really need duct cleaning. Remove the floor registers and use a flashlight if necessary to see if there is dust or debris in the ducting. If these look bad, I'd definitely have the system cleaned. I would also do it after a construction project, after installing a new furnace, etc. I have found that once I had my previous system cleaned, it seemed to remain spotless for 3 years. So it seems that if you just change your filters on time (I have an iPhone alert set for every 3 months), the system will stay clean for years. Hope this helps!
Heating, ventilation, and air conditioning (HVAC) systems have been shown to act as a collection source for a variety of contaminants that have the potential to affect health, such as mold, fungi, bacteria, and very small particles of dust. The removal of such contaminants from the HVAC system and home should be considered as one component in an overall plan to improve indoor air quality.
The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.
With today’s consistently rising energy costs, improperly sealed windows, ductwork, and poor insulation can pose serious problems for many home and business owners in Arkansas. Wilson's Heating & Air Conditioning provides complete HVAC system servicing including sales, installation, maintenance and repair, and offers numerous practical solutions that will reduce your energy costs.
If you think duct cleaning might be a good idea for your home, but you are not sure, talk to a professional. The company that services your heating and cooling system may be a good source of advice. You may also want to contact professional duct cleaning service providers and ask them about the services they provide. Remember, they are trying to sell you a service, so ask questions and insist on complete and knowledgeable answers.
No one has addressed mfg homes and doesn't seem any of the comments are from people in So CA which of course does make a difference as my dust comes from the outside not from the vents. My windows are open pretty much 365 days a year. Secondly mfg homes don't have basements or attics I keep mine clean with my vacuum as they are only about 2 ft deep. I purchased my home 10 yrs ago and it is a high end home but have never had a problem. I clean my furnace filter about twice a month as I have cats and most everything in there is cat fur. I am not saying they don't ever need to be cleaned but I am questioning mfg homes, I also clean my own filters in my AC unit outside as the HVAC guy told me too he QUATITY they would sell. I use this same company every year now for my tune up and inspection which takes them about 10 minutes. Not a bad return for them and I don't mind the $79 fee. If anyone has more info than this on mfg homes please let me know!
My vent covers have lots of mildew. They look bad! I live in a very humid climate in a condo. The handyman here has offered to take those down, wash them, sand, & then spray paint them with a mildew resistant paint. He said that he will leave them off overnight to dry. I am wondering if this is safe to breath the AC blowing out into the open all night??. ! Guess it is better than the mildew!?

The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.


They were quick to come out and diagnose the problem with my furnace, but I thought the estimate of $549 a bit high to replace the circuit board.  So called around and found Leo's Appliance in Concord that sells appliance parts and the circuit board was only $90.49 - that is the retail cost to me, so I imagine the wholesale cost is a lot less.  So BEWARE of this company since they wanted $500!!! to replace the circuit board which is located right in the front of the furnace - extremely easy to access.  I hate it that you cannot trust repair companies.
You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 
Tip – Be careful with change-outs. Ductwork deteriorates and sometimes has to be replaced.  It is only if the ductwork is in fantastic condition that you should get a change-out without ductwork (Remember – the ductwork has already been there for 15-20 years, and now it will be there another 15-20…it has to be in good shape). However, many HVAC installation companies like to push change-outs because the ductwork is the most time consuming part of the job, and a change-out is quick, easy money. Realize that it’s only about 15-20% of the jobs that qualify for a change-out, so be careful.
The jury is out on whether or not cleaning your air ducts and vents has a significant enough impact to be necessary. A proven connection between immaculate duct systems and air quality in the home has not been made. However, if your vents display any of the signs listed above, cleaning would certainly be in your best interest. Allowing mold, debris and bacteria to fester could create bigger problems down the line. If having your system disinfected is within your budget, you may prefer to take care of these issues rather than ignore them.
I always get a laugh at anyone claiming to be in the business for any length of time that doesnt understand the importance of cleaning out a ventilation system. Not only for better indoor air quality but for maintaining your heating equipment. I guess it makes more sense to some people that the furnace will just run better with a ton of dust and debris and maybe this wont be a big cause of sytem breakdown and malfunction. I mean really? Maybe this guy got a bad company and or cleaning and is a little jaded but to advise cleaning your grills , which does nothing, and replacing a filter....come on guy.
I am very interested by your post. We recently had a lead inspection on our property and one thing the lead inspector suggested was to get the air ducts cleaned out. We had our ducts cleaned last year after we under went a large renovation project (since we have a toddler in the house). This year we decided to go for lead compliance and had all our lead removed (we moved out for the work). Recently, my son had a false positive lead test, which prompted us to get a lead dust inspection around the house (including having the vents dust-wiped on the inside). The levels inside the ducts weren't crazy high (but more than would be acceptable for a floor). As it turned out my son's lead levels are very low (but not zero). Is it possible however that lead dust from the inside of a vent can come out? Would this be a scenario where you think air duct cleaning would be beneficial?

The heat pump gained popularity in the 1950s in Japan and the United States.[13] Heat pumps can extract heat from various sources, such as environmental air, exhaust air from a building, or from the ground. Heat pumps transfer heat from outside the structure into the air inside. Initially, heat pump HVAC systems were only used in moderate climates, but with improvements in low temperature operation and reduced loads due to more efficient homes, they are increasing in popularity in cooler climates.
Although i love to burn candles, depending on the type your asking for problems big ones! At work one day i had been talking with co workers about these black shadows that were appearing on my ceilings and higher wall areas. They seemed to in the corners and along the stud supports , i could even see what i thought to be where all had been nailed. There would be dark shadows perfectly straight across my ceiling and then real dark circels every few inches within the lines. I thought it was the propane heat but learned quickly that oil heat will do that but not normally propane. A co worker brought me a magazine with a huge article about candles and what actually burns off them when lit, an ashy soot that is attracted to the areas on walls and ceilings that omit the most heat or warmth, of course where the drywall and studs meet and corners of the room. Its been about 8 years since i painted the entire house. I started bending to my love for candles again in the last 3 years, surprise i will be spending part of my summer re painting again!! No more candles ,well maybe at the holidays LOL

Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.

I am 79 years old, bought a condo & spent a lot of money on it. this winter my first bill was 450.00. had my furnace checked out, which is on the roof. it was old rusted out & leeking oil. i talked to owner & had new unit installed. they came out to clean ducks & they were split & worn out. there is no crawl space because theres a unit above me. my real estate lady or this company will not help me fix this problem.
Alberto said they were busy but could either install on the upcoming Saturday.  We were going to be out of town and said unfortunately that day did not work.  He then proposed the upcoming Tuesday as a possible solution, but just had to confirm with another appointment.  I said great.  I will review the estimate and call your office to confirm I want to move forward with the install.
If you think duct cleaning might be a good idea for your home, but you are not sure, talk to a professional. The company that services your heating and cooling system may be a good source of advice. You may also want to contact professional duct cleaning service providers and ask them about the services they provide. Remember, they are trying to sell you a service, so ask questions and insist on complete and knowledgeable answers.
×