An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.
Ok what you said is true but in most cases ducts are in a duct flex format, and knowing that the dust in people's flex duct is just surface dust, any real debris that are in the duct itself will result in very little to no air flow which will keep your unit from performing properly, but if it is true allergy reasons then replacing your duct system is better for overall better air quality, plus if you do pay attention to the warranty on flexible duct is that it only has a 10 year warranty and typically only lasts for 20 years so do your research before having a duct cleaning, and to add one more thing if your duct work is completely metal and you can't see visible insulation then your duct on the inside has insulation inside of it, if you replace that with duct work that is clean metal on the inside and wrapped with insulation on the outside then it will further reduce the air bourne fiberglass and dust.
Your cleaning service should involve all aspects of your duct work to maximize energy efficiency and air quality. This includes attending to the heat exchanger, blower, drain pan, plenum and coils as well. In the process, your service provider may find that you're facing larger issues than debris and build-up. The professional may recommend having your furnace repaired if they notice, for example, damage to your heat exchanger or blower motor. Generally, a furnace repair costs between $130 and $500. They may also find that an A/C coil needs to be replaced rather than cleaned and would then recommend A/C repair.
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.
I noticed a lot of negative feedback, though unfortunately there are many dishonest companies out there. I currently work with a company that cleans duct work and we DO NOT use any scare tactics or up sell services or equipment. Once every 10years of course there are exceptions. We clean supply, returns, air handler, housing, motor, and fan. Though be discerning when qualifying anyone to work in your home. I would ask for REAL REFERENCES to contact.
A year and a half ago (fall of 2015) we replaced the furnace and air conditioner. From what we could determine this was the third forced air furnace and second air conditioner unit for the house. As part of the installation, we changed out the two 6″ ducts feeding the second floor with 8″ ducts. The idea was to get more cold air to the second floor in the summer. It worked and for the first time the second floor and first floor temperatures were the same when the air conditioner was running. Of course, to make the system work I close down upstairs duct damper doors in the winter and open them up in the summer.

Filtration systems -- A second-stage filter is sometimes inserted & used to remove particulates such as pets, smoking or cooking, as well as other odors, gases, and VOCs (volatile organic compounds). A HEPA filter is also available to remove spores, pollens, bacteria and lung-damaging particles. There are also systems that use ultraviolet (UV) light to protect against bacteria and germs.


Cost Factors: The size of the unit, its efficiency and it’s single-stage, two-stage or variable-capacity are the top cost factors. Features like communicating technology and improved dehumidification performance also affect the price. Learn more about communicating technology here including the pros and cons, before being agreeing to a communicating system.
So, whether you need an AC repair or you’re in search of a new heating and air conditioning system—or you need a new water heater now–you can count on our team in North America. We’re experts in AC and plumbing repair, and offering top-notch AC and plumbing service is what we do best. Call Service Experts 24/7/365 at 866-397-3787 or request an appointment online today, and don’t forget to check out our coupons page for savings on your AC or plumbing repair service.

We bought 2 top of the line Lennox HAC for $29,000 less about $3,500 rebates, thinking they would at least last 10 years. Well, after 6 years, the system leaked. We are paying $1,700 to fix that leak. We thought at least it is still under warranty - yes BUT - the warranty covered $15 & the rest we were up for ,even though they advertise 10 year warranty. We are trying to sell & move out of high cost southern Calif & have looked at 20+ places in Arizona. Most of the houses we looked at were built from 1998 to 2005. We asked if the HAC was original & in most case it was - even though the highs were 115 to 120 & the lows 90F - versus where we live the highs run 85 to 95 & the lows are in the 60s. I asked the repairman WHY ours went out at 6 years. He replied that they just do not build them the same anymore. In Arizona, I did not see any Lennox - mostly Trane or Carrier. We had Fujistu in Australia which were fantastic - nothing went wrong in the 9 years we had them. Also, they had full induction motors not like the energy consuming 2 stage motors in Lennox. Maybe the Japanese built Fujusita still builds quality & the warranty is meaningful?

Deciding if central air is worth the cost depends on your needs and local housing market. If you live in a hotter climate, it can definitely be worth the price. Not only can it keep your home at a comfortable temperature, but air conditioning can even save lives during extreme heat waves. But in a milder zone without severe temperatures, window units, fans or the breeze from an open window could be adequate.
You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 
Venice warns homeowners to beware of air duct cleaning scams, especially the sort where unscrupulous cleaners offer a $49 special deal but start piling on extra fees. “It’s a bait and switch scam where they say they’ll offer unlimited cleaning, but then they throw around terms you might not understand, such as extra fees for a ‘main duct line,’” he says. “And many times, these cleaners end up walking out the door with twice the amount of money a reputable duct cleaner would charge. They’ve gotten very sophisticated at upselling.”
Although most new homes have ducts and vents already in place, many older homes have old convection heating systems or baseboard heaters without ductwork. In such cases, you will need to install ducts and vents to provide the air conditioning with a flow system. This would be the time to explore upgrading the existing heating system as well, as it will be much cheaper to do together.
The answer to your question is most likely "Yes," but not defiitely. It depends on where the dust is coming from. Now, if your house is more than say, 12 years old then you likely do have leaks in your ducts that can let in insulation particles and dust from your attic. If this is the case then cleaning of the ducts-PROPER CLEANING, which like the article sas doess include EVERYTHING that the conditioned air passes through, such as your indoor evaporator coil and blower housing assembly-is definitely a good first step to getting that dust under control! Of course I highly recommend that you also have your ducts SEALED as well, or else you will have to repeat the cleaning some time down the line. As a 3rd step, consider an electronic air filter. I always thought they were a scam, personally, so I never bothered selling them to my clients. Then one day my manager sent me to install one for a senior couple in a mobile home. The wife had bad allergies, and her eyes were constantly watering and puffy and red. Well, I did a quality check 60 days later and she could not stop praising that air filter! Keep in mind that in a mobile home, duct seals are not as complete as those in other homes due to access issues.
What you might not know is that the brand you choose is one of the most important factors in determining a fair HVAC installation cost. So, before delving in-depth, let’s take a quick look at the average prices of a new air conditioner and matching coil by brand…keep in mind, these are the average prices (by brand) that contractors pay for your AC equipment, and it is meant to give you a rough guideline until you are closer to buying:
My best advice has always been that a proper duct cleaning is a valuable investment when moving into a home (new or old), after major renovations and if the ducts have never been cleaned before. It is unlikely that there will be increased air flow, as finding major blockage is unusual, but this will eliminate this as a possible concern if there are air flow concerns. It is also true that the "dust" that is cleared out will most likely never have been distributed through the house unless there has been some work done on the ducts. What is cleared out will be pet hair, toys, clothes, construction material, and biological material (small carcasses and/or feces). Once a proper cleaning is done a follow-up is rarely necessary, but up to the home owners discression.

Since most states and municipalities don’t license air duct cleaners, you need to check their professional credentials instead, such as NADCA membership. EPA recommends all duct cleaners follow NADCA standards. Member companies must keep at least one technician on staff who has passed a NADCA test. “They have to pass rigorous testing to earn the certificate, and our code of ethics is very important,” Vinick says.
My best advice has always been that a proper duct cleaning is a valuable investment when moving into a home (new or old), after major renovations and if the ducts have never been cleaned before. It is unlikely that there will be increased air flow, as finding major blockage is unusual, but this will eliminate this as a possible concern if there are air flow concerns. It is also true that the "dust" that is cleared out will most likely never have been distributed through the house unless there has been some work done on the ducts. What is cleared out will be pet hair, toys, clothes, construction material, and biological material (small carcasses and/or feces). Once a proper cleaning is done a follow-up is rarely necessary, but up to the home owners discression.
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.
Cost Factors: The size of the unit, its efficiency and it’s single-stage, two-stage or variable-capacity are the top cost factors. Features like communicating technology and improved dehumidification performance also affect the price. Learn more about communicating technology here including the pros and cons, before being agreeing to a communicating system.
Whether or not central air adds value to your home depends on your location. You probably won't recoup the entire cost for the installation, as it is an expensive project that isn't as flashy as something like a new deck. But this invisible upgrade can help you sell your home if you live in a hot climate. And many buyers are willing to pay a bit more for a working AC.
The use of furnaces, space heaters, and boilers as a method of indoor heating could result in incomplete combustion and the emission of carbon monoxide, nitrogen oxides, formaldehyde, volatile organic compounds, and other combustion byproducts. Incomplete combustion occurs when there is insufficient oxygen; the inputs are fuels containing various contaminants and the outputs are harmful byproducts, most dangerously carbon monoxide, which is a tasteless and odorless gas with serious adverse health effects.[14]
Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]
The answer to your question is most likely "Yes," but not defiitely. It depends on where the dust is coming from. Now, if your house is more than say, 12 years old then you likely do have leaks in your ducts that can let in insulation particles and dust from your attic. If this is the case then cleaning of the ducts-PROPER CLEANING, which like the article sas doess include EVERYTHING that the conditioned air passes through, such as your indoor evaporator coil and blower housing assembly-is definitely a good first step to getting that dust under control! Of course I highly recommend that you also have your ducts SEALED as well, or else you will have to repeat the cleaning some time down the line. As a 3rd step, consider an electronic air filter. I always thought they were a scam, personally, so I never bothered selling them to my clients. Then one day my manager sent me to install one for a senior couple in a mobile home. The wife had bad allergies, and her eyes were constantly watering and puffy and red. Well, I did a quality check 60 days later and she could not stop praising that air filter! Keep in mind that in a mobile home, duct seals are not as complete as those in other homes due to access issues.
The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
I forgot about a pot of sweet water I had on the stove to boil. When I finally smelled it the kitchen and dining room I=was smoke filled. I mean thick smoke. I opened doors and windows for a few hours to remove the smoke but the smell is still here and terrible. I had to use the AC and that smell started coming out of the vents. Now what do I do? I have COPD emphysema so I have to be very careful about what I inhale. I already have inhaled too much smoke from all of this which has hurt my lungs even more. I can’t afford for them to get worse over this. How can I get the right person to come out and clean the ducts and furnace or is that the only way to remove that burnt smokey smell. The pot never caught on fire but it sure did produce a lot of smoke. I already have replaced the filter on the furnace. It needed it even though it had just been replaced just last week. I need help or really my lungs need help. Who do I call here in Indpls IN.
Lennox, on the other hand, is probably the most expensive unit out there and I can’t stand them.  In our (humble?) experience, they have a horrible logistics chain, making repair parts difficult to come by (sometimes taking weeks), poor customer service, and the parts cost three times as much. That’s not what this article is about, so read more in: Carrier vs. Lennox Furnace Review.
Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]

Energy efficiency can be improved even more in central heating systems by introducing zoned heating. This allows a more granular application of heat, similar to non-central heating systems. Zones are controlled by multiple thermostats. In water heating systems the thermostats control zone valves, and in forced air systems they control zone dampers inside the vents which selectively block the flow of air. In this case, the control system is very critical to maintaining a proper temperature.


Multiple inventions within this time frame preceded the beginnings of first comfort air conditioning system, which was designed in 1902 by Alfred Wolff (Cooper, 2003) for the New York Stock Exchange, while Willis Carrier equipped the Sacketts-Wilhems Printing Company with the process AC unit the same year. Coyne College was the first school to offer HVAC training in 1899.[12]

Indoor Coil -- The indoor coil is a heat transfer device. It absorbs the heat from the inside of the house and passes it on to the refrigerant and is pumped outside. Dust that builds up on the coil can hamper its ability to absorb heat. High heat transference coils use very thin metal. Airborne chemicals can cause corrosion which leads to leaks. The constant vibration of the compressor can also cause solder joints to weaken and leak. An indoor coil may operate for weeks with a tiny leak, and you may not notice the loss in performance right away. As soon as a leak is made known, it should be replaced or repaired immediately.
One problem occurred on Monday.  When we called at 2:30 in the afternoon to check on status, we were told that "the tech is on the phone with the parts supplier now".  It seems more likely that they had forgotten about us and our call woke them up.  But even if true, why the heck did they wait until 2:30 to order the part?  Maybe if they had ordered it in the morning they could have had it the same day.  So I'm taking off one star for that.
Stick with a maximum of 16 SEER units in most cases.  Like I said above, contractors push higher SEER units because they make more money, but these units can be expensive at this stage of development, and can drive up your HVAC installation cost.  21 SEER units run about twice the price of a 14 SEER unit, so unless you live in a desert and plan on being there for 30 more years... Likewise, a 16 SEER unit typically costs only about $600-$1,000 more than a 14 SEER, and will usually pay for itself over the lifetime of the unit.
Typically speaking, the lower SEER, more basic models are also more reliable.  Reliability is big with us, so we steer clear of features with reliability issues, and it’s as simple as that. When you factor in the price of repairs and the extra expense of the 21-SEER, you may actually lose money! 16 SEER is the sweet-spot, and it is key to reducing your HVAC installation cost.

There is much more to air conditioning than AC installation in Fort Smith, AR then just maintenance and repairs. A variety of other services is required throughout the lifespan of your cooling unit. We are the professional team capable of completing them all. Replacements, troubleshooting, indoor air management, these are all part of our repertoire.
The HVAC industry is a worldwide enterprise, with roles including operation and maintenance, system design and construction, equipment manufacturing and sales, and in education and research. The HVAC industry was historically regulated by the manufacturers of HVAC equipment, but regulating and standards organizations such as HARDI, ASHRAE, SMACNA, ACCA, Uniform Mechanical Code, International Mechanical Code, and AMCA have been established to support the industry and encourage high standards and achievement.
I call to follow up at the end of the next day and she said that she has not been able to get in touch with the owner.  By this time, I am starting to get frustrated because I am starting to get the run around.  I question her if I am even on the schedule or if they attempted to schedule a crane.  She says they are extremely busy and that she does not know.  So I say, basically I have waited over 2 weeks and you have not put me on the schedule and I am at the end of the install line.  No answer.  I tell her to talk to her boss and find out what is happening, and I will think about what direction I want to move in at this point.  
I always get a laugh at anyone claiming to be in the business for any length of time that doesnt understand the importance of cleaning out a ventilation system. Not only for better indoor air quality but for maintaining your heating equipment. I guess it makes more sense to some people that the furnace will just run better with a ton of dust and debris and maybe this wont be a big cause of sytem breakdown and malfunction. I mean really? Maybe this guy got a bad company and or cleaning and is a little jaded but to advise cleaning your grills , which does nothing, and replacing a filter....come on guy.

Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.
I was with you until you said avoid steaming cleaning or moisture, there is no way you can remove mold or any other type of biological without moisture. The best way to do this is in fact with a steamer using a commercial disinfectant and a non reactive odor remover so your home smells refreshed and not like a hospital . This is directly contradictory to your article.

Humidifiers/Dehumidifiers: Humidifiers add needed moisture to the air in winter and very dry climates. Dehumidifiers remove dampness any time of the year. Central air conditioners dehumidify too, but in very humid climates, you might want to remove humidity without also cooling the air. You have a good range of options for both of these HVAC accessories. Whole-house humidifiers cost $350 to $800 installed, while dehumidifiers are $1,250 to $2,000 or slightly more.
Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]
Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.
Fuses -- Anyone who has worked with electrical systems knows all about fuses and how they fail. They can burn out over time, may just be loose, or can blow out during an electrical storm or due to overload from another failed component. Of course, that's what they're supposed to do; they stop surges from going through and damaging the rest of the system. When a fuse fails, whatever system it was protecting will stop working.
Your cleaning service should involve all aspects of your duct work to maximize energy efficiency and air quality. This includes attending to the heat exchanger, blower, drain pan, plenum and coils as well. In the process, your service provider may find that you're facing larger issues than debris and build-up. The professional may recommend having your furnace repaired if they notice, for example, damage to your heat exchanger or blower motor. Generally, a furnace repair costs between $130 and $500. They may also find that an A/C coil needs to be replaced rather than cleaned and would then recommend A/C repair.

The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.


I have a white gritty dust throughout my whole house. Dust and it comes right back. We have central air. In 2013 had all the air conditioning tubing in the attic replaced. Old ones were completely clean. Why?? Thought dust would be in there. Put everything in plastic containers. Furniture everything is always covered with this. Problem is always there year round. Furnace people said it is not coming from furnace. We built house in 1971. Only started with this @ 19 years ago. Thinking when air conditioning went in. We cough all the time and sneeze. I do not have friends come here because I hate how dirty my house looks.
He proceeded to clean each heat register by removing the grille and blasting it with an air pressure hose toward the duct opening thinking that the dust would magically be sucked inside. In one room this caused a ceiling smoke detector to go off because the excess dust fooled it into thinking there was smoke. I put my hand in front of a register he wasn’t working on and could hardly feel a suction. Although we discussed how I open and close damper doors, I realized later that he never checked, opened or adjusted them during the cleaning. He could have closed all but the one he was working on in order to increase suction results. His next step was to blast air into the duct and then attach a “squid-like” device that slapped around inside the duct as far as he could reach. This is important! In a newer house, ducts have long straight runs from the furnace. In older houses like mine they can turn and twist. In fact, the duct we have a problem with runs straight up from the basement inside a wall and turns 90 degrees into a soffit for three feet then into two 90 degree turns to get into the floor joist area for another two feet and finally a 90 degree turn up to the second floor register. When he cleaned this one he could only get three feet into the register with the hose or squid because of the turns. That was the case with most. Hardly what could be described as a decent cleaning.
If not properly installed, maintained and operated, these components may become contaminated with particles of dust, pollen or other debris. If moisture is present, the potential for microbiological growth (e.g., mold) is increased and spores from such growth may be released into the home's living space. Some of these contaminants may cause allergic reactions or other symptoms in people if they are exposed to them. If you decide to have your heating and cooling system cleaned, it is important to make sure the service provider agrees to clean all components of the system and is qualified to do so. Failure to clean a component of a contaminated system can result in re-contamination of the entire system, thus negating any potential benefits. Methods of duct cleaning vary, although standards have been established by industry associations concerned with air duct cleaning. Typically, a service provider will use specialized tools to dislodge dirt and other debris in ducts, then vacuum them out with a high-powered vacuum cleaner.
×