I recently did some remodeling and figured I’d get the air ducts cleaned in our 12 year old home. After obtaining 4 estimates between $572 and a whopping $3,075 for 25 vents and 2 air handlers, I knew I was in for a ride. I read through this blog and decided to use a $79 inspection camera I just found online (Home Depot) to take a look at all my ducts by removing the ceiling grilles first and then try to get into the ducts from the other end. From what I have just learned here, I believe that will take care of my “concerns”.
Capacitors -- Capacitors help your HVAC motor start from a standstill. Over time they can weaken. As they weaken, they cause the motor to run hotter. This can shorten the life expectancy of your motor. Once a capacitor fails, the whole motor will stop working. You usually won't notice that a capacitor has weakened until your motor stops turning on.
I'm very glad that I found another guy to come replace the circuit board and put it away from the water, fix the water leak, and also find and fix another impending failure.  All of that was for much less than HVAC Service wanted to charge for repair or replacement. The other guy did a great repair, so I'm confident it will not break down again, but if it does, I will not call HVAC Service. Don't get suckered by their Yelp Deal.
#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
You can adjust for seasons: During the summer, you can have the air conditioner stay off during the cooler morning hours and start cooling the house as everyone gets up and starts moving around. During the winter, you can have your heater stay off while you are away at work and turn on about a half hour or so before you get home so that you are coming home to a nice, warm house.

An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]
Did not realize cost had gone up so much for this service. Two years ago I had furnace and ducts cleaned at my old house and it was under $400. Now the cost is $700 for this house. I will keep looking for someone to offer a lower price, check them out, and have it done. Or will find the paperwork to see who did it before. I liked this article and did learn some things. Thanks.
I thought the price advertised at 129.95 for duct cleaning was great and called to clean our ducts. When they came in to do the the job I could not be home and my wife dealt with them. My wife ended up paying 954.00. They convinced my wife that there was 1.5 inches of mold built up on the Evaporators and coils. It is not the money, my wife could not go to the basement to witness the mold build up or the coil fouling. We have not cleaned our ducts for at least 10 years. The last price we paid for our duct cleaning was 150.00. My concern is that they told my wife not to turn on the heat for 2 hours due the strong chemicals they used to kill the mold. Are these chemicals approved as safe?
As a homeowner and an owner of rental property I can tell you that the air ducts sometimes need to be cleaned. If you have had pets or anyone smoking in your home (even a visitor) for any length of time, having the ducts cleaned is really good idea. I had a tenant who did not smoke, but got married to a smoker more than year after moving in. When I realized someone was smoking I had them move out, but the smell was awful. I had the ducts cleaned and sanitized (it was a bit extra). The ducts were shiny like new afterwards. I left the windows open for a few days and we cleaned the place super clean and then replaced the carpets. The duct cleaning was worth every penny because the house looked, smelled, and felt new afterward. I plan to have my own house ducts cleaned again this year as we have two cats. We had them cleaned about 12 years ago and they found building materials in the ducts! If you move into a house that has never had them cleaned, it is good to do it. If you have allergies, clean the ducts to see if it helps. You never know what is in your ducts if you have never had them cleaned.
20 yrs ago I bought the house I am in and a Central H/A was installed at that time. At the beginning of ea season I have the unit serviced. Every yr since I have owned the house I have had to have freon added and been told that I must have a freon leak. Fast forward to this yr when I hired a new company to do the service. They went up into the attic as part of their overall servicing. Nobody else has ever done that. He came down showing me pics on his camera phone of ducts that were not even connected to anything and in my estimation have probably been laying there for 20 yrs. Of course he fixed this. I have not needed freon this year either. I have been complaining to friends about the huge amount of dust and how I can't keep up with the cleaning away of it for a long time. Now it makes so much sense.To me it is like that duct work was just up there laying around and every time my unit was blowing, all the insulation, debris, dust and whatever else over the years was just randomly filling up those ducts. What now that they are re-connected? Will it be better? Or am I someone that needs to have my ducts cleaned? I am so confused after reading all these comments. Can one of you experts tell me what you would do before I spend a bunch of money that I don't really have? Thank you for any input you can provide. Also, feel free to respond to email address denise@digitalflak.com
If you’re purchasing from a big-box store, you can expect to pay approximately $120-$1,000 for a window unit. Window units are appealing for their quick setup and relatively low cost, but they can use more energy over time than central air and only cool the room in which they’re installed. The price will vary depending on the type of air conditioner you buy and its cooling capacity. Window units, which require minimal installation, are one of the most affordable options on the market. Portable air conditioners don’t have the cooling power of a window unit, but they do have the perk of being transportable from room to room. Expect to pay between $225 and $800 for a portable air conditioner, on average. The cost of an air conditioning system with coils, condenser and line (not including installation or ductwork) can range from approximately $2,000 to $4,000 or more. If you don’t have (and don’t want to put in) ducts, a ductless mini-split air conditioner is a good option, although pricey up front. Pricing can range from $650 to $4,250 per unit on average; you’ll need one unit for each room in which you want temperature control.
Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  
Had duct cleaners here coupon for 40.00 for complete home I was not here but my husband was. I told my husband that they will prolly ask for more money and I was right. 85 extra to do duct cleaning which I pled because my dryer vent was full of animal hair extensions then for 600 to clean a/c coils I said no. Just do what the coupon said. Do your homework be 100 steps ahead of these con men rember they con people all day long and know the ans to your objections
I agree, if you replace (or wash depending on type) your air filters regularly AND vaccum, then you probably don't need the ducts or air coils cleaned. However, if you purchase a pre-owned home, and the previous owners did not regularly change the air filter or vaccum the home, then duct cleaning is worth the expense especially if you are sensitive to allergens. Especially if the previous owners had pets.
We have provided Arkansas families and businesses with quality HVAC products and services for 42 years. Offering reasonable rates and personalized service, we are a dedicated team of experts equipped to handle any service requirement. Your source for modern heating, cooling, and ventilation equipment and servicing, Wilson's Heating & Air Conditioning is the HVAC specialist in Van Buren.
On average, we (Indians in Ontario) receive 3-5 calls per day for duct cleaning services from India. I did get ducts cleaned twice in 25 years. For a newly built house, it should be done as material goes into the ducts. Every year, before turning the heat on, I clean the ducts, using the vacuum pipe or with wet towel. Most of the dust, pet hair, small items get to the ducts from the top floors, not where system is installed. Even in winter months, I open 2-3 windows for air circulation for 15 minutes, specially right after cooking, almost daily. We breath in the same stale air, develop health issues. Also, I have an added air cleaning and fileration system installed. At a low rate, this system constantly cleans the inside air and also that it pulls from the outside. Duct cleaning is a scam, there are other efficient and cost effective methods we can use to purify the inside air.
Although most new homes have ducts and vents already in place, many older homes have old convection heating systems or baseboard heaters without ductwork. In such cases, you will need to install ducts and vents to provide the air conditioning with a flow system. This would be the time to explore upgrading the existing heating system as well, as it will be much cheaper to do together.

To qualify for a tax credit from the federal government, you must save the manufacturer's certificate from your system. The IRS won't require the certificate at the time you file your federal tax forms, but they recommend keeping it with your records in case of an audit. It proves that you purchased a qualifying product. The government offers tax credits for:

While a lot of people understand the consequences of AC problems throughout the summer, the summer comes with its own set of unique issues that require a call to the plumber, too. Whether it’s a malfunctioning sprinkler system or a sewer line backup, Service Experts can help. We’ve encountered it all, and you won’t have to worry about any of it with our 24/7/365 Emergency Plumbing Service. When you need a plumber, we are here for you. And, just like all of our other services and products, any plumbing repair or work completed by Service Experts is backed by the same 100% Satisfaction Guarantee*.


Interesting. Giuliano Cuete and Carlo Olcese have the exact same post about pretenders and being NADCA certified, word for word. So how do you become NADCA certified? And does that mean you are not a scam artist or a "blow and do" ripoff? hmmm, interesting. The EPA says that under normal conditions, a properly maintained system should NEVER need it's ducts cleaned.
Before we get to HVAC installation prices, we will first need to briefly discuss some terms, definitions, and factors that will affect how an honest HVAC installation company determines their prices. Notice that I said honest. Unfortunately, there are dishonest people out there. There always have been, there always will be, and there is a good chance that you had an experience with such a contractor, which is what drove you to read this article. I can’t teach you how to tell if someone is honest, but I can give you the knowledge to help you decide. Take a look at How to Choose an HVAC Contractor for tips on what to look for.
Fresh-Aire UV is an innovation leader in the field of indoor air quality. Our award-winning UV light and carbon products fight mold, bacteria, viruses and odors in commercial and residential HVACR systems. Our products include Blue-Tube UV®, the worlds most popular germicidal UV light, the revolutionary APCO® PCO/carbon whole-house air purifier, and Mini UV the first UV light system designed specifically for mini-split AC systems.
Duct cleaning is a band aid, like washing you hands is. Under your description, why wash your hands more than once? If it gets cleaned once, it shouldn't get dirty again. Well that is, unless they touch something dirty. Keeping your hands completely clean is virtually impossible. Same as keeping dust out of your home. You clean your ducts and over a 3-5 year span they get dirty again. Also, duct cleaners are not licensed but should be certified by NADCA(National Air Duct Cleaning Association).
Roof-mounted systems have the heating and cooling systems in one cabinet. Sometimes called "gas packs" (if the heater uses natural gas), they typically cost less than a comparable split system. In dry regions, most homes originally had "swamp-coolers" installed. When replacing them with HVAC systems, it's often cheaper to use existing mounts and ducting.
CIBSE publishes several guides to HVAC design relevant to the UK market, and also the Republic of Ireland, Australia, New Zealand and Hong Kong. These guides include various recommended design criteria and standards, some of which are cited within the UK building regulations, and therefore form a legislative requirement for major building services works. The main guides are:

Well, I had the cleaning done. The handler is definitely much quieter. It was explained to me that with the coils clean, the condensation will be able to sweat off instead of sticking to the dust and dirt, therefore the humidity (lots of humidity in florida) will be removed better. I feel as if it was worth it, but, I will definitely change that filter every 3 weeks or so from now on. I don’t want to pay that cost again.
I to had an odd layer of white'ish dust building up especially during seasonal periods when the HVAC ran a a lot. I carefully swept up the fine dust into a small pile and had it analyzed. Turns out it was very fine fiberglass powder dust. It turns out it is the insulation form the attic! (My attic has blown in insulation). Turns out if you (I) had small gaps around my HVAC registers in the ceiling whee the airs blows into the room. What occurred in my case was that the exiting air at that seam creates a vacuum effect at the grate vent cover and draws and then blows fine insulation dust from the attic into the house. Removing each register grate and sealing each tin outlet gap with calking between the dry wall ceiling and tin fixed the issue. A couple were so bad with bowed gaps I had to screw down the bowed tin to the attaching stud better. Checking the very same glass top desk that catches and shows any dust accumulation now shows only very small amounts of normal house dust build up over several weeks. A big, big improvement. You might have a look by simply removing a couple vent covers yourself.
Whether you’re starting your air conditioner for the first time this year, or a unit isn’t running properly and you need to service an air conditioner, following a few simple steps can save you time and money. While some service jobs should be left to a professional, there are several do-it-yourself fixes you can do to keep your air conditioner cooling all summer long.
Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.
No matter what time it is, our experts will have you lounging in the cool air of your home quickly. We stand by our workmanship so much so that we guarantee it in writing for one full year. Our 100% Satisfaction Guarantee* firmly backs our dedication to providing the highest level of air conditioning service in the industry. In fact, Service Experts repairs, sells and installs more air conditioners than any other HVAC company through North America. More people count on us for their home comfort, so you can be certain your home will be back to being cool and comfortable in no time.
Indoor Coil -- The indoor coil is a heat transfer device. It absorbs the heat from the inside of the house and passes it on to the refrigerant and is pumped outside. Dust that builds up on the coil can hamper its ability to absorb heat. High heat transference coils use very thin metal. Airborne chemicals can cause corrosion which leads to leaks. The constant vibration of the compressor can also cause solder joints to weaken and leak. An indoor coil may operate for weeks with a tiny leak, and you may not notice the loss in performance right away. As soon as a leak is made known, it should be replaced or repaired immediately.

A year and a half ago (fall of 2015) we replaced the furnace and air conditioner. From what we could determine this was the third forced air furnace and second air conditioner unit for the house. As part of the installation, we changed out the two 6″ ducts feeding the second floor with 8″ ducts. The idea was to get more cold air to the second floor in the summer. It worked and for the first time the second floor and first floor temperatures were the same when the air conditioner was running. Of course, to make the system work I close down upstairs duct damper doors in the winter and open them up in the summer.
Those of you who read our posts regularly know that we built our reputation as a U.S. Veteran-Owned business that prides ourselves on giving people straight, honest answers to their questions...and there’s no question that makes people cringe more than asking, what does a new HVAC installation cost? Oddly enough, most contractors keep their air conditioning installation cost a closely guarded secret, as if the knowledge of how much it should cost will somehow change your decision when you have to buy a new AC. What I will tell you, is that the fair price of an HVAC installation will vary greatly based on the type of heating and air conditioning system installed, as well as the options needed or desired (Ductwork included? Zoning system?). In this article, we’ll discuss the five system features that affect HVAC installation cost, fair price ranges you can expect to pay for your new system, we will then perform an example calculation of how you can calculate a fair price, and finally, what you can do to keep from getting ripped off on your new HVAC installation price.

There is a lot of good, general information in the article. As with anything, the homeowner should do their due diligence in getting enough information to make an educated decision. Should duct-work be cleaned? YES! Does it need to be cleaned annually or even every second or third year? Not necessarily. It all depends on a bunch of variables. You're right that a well designed and balanced system will deliver the right amount of air flow, but sometimes conditions outside the home/business, make it a necessity to get the ducts cleaned. As for mold? NO filter is going to address a mold issue. If you have mold, you have a moisture issue that needs to be addressed. Also, in my 38 years of experience in the HVAC and sheet metal industries, washable filters are one of the reasons ducts need to be cleaned. They are no where near efficient in cleaning/filtering the air to the level that they should.
Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  
Simply living in your home creates dust and dirt. Have you ever seen dust floating in the air in your home when the sun shines in?  Dust, dirt, pet dander, mold spores, and allergens get pulled into the air handling system in your home. They build up in the ductwork; some of it gets recirculated back into your home, and some of it can be captured by a good quality air filter. Eventually, enough debris builds up to the point where most of it blows back into your home. Your furnace or air conditioner must run longer to cool or heat your home, which costs you more in utility bills. With a service call from Sears Air Duct Cleaning, you can feel comfortable knowing that the accumulation of dust, dirt, dander, mold, and allergens has been cleaned from your HVAC duct system.

I call to follow up at the end of the next day and she said that she has not been able to get in touch with the owner.  By this time, I am starting to get frustrated because I am starting to get the run around.  I question her if I am even on the schedule or if they attempted to schedule a crane.  She says they are extremely busy and that she does not know.  So I say, basically I have waited over 2 weeks and you have not put me on the schedule and I am at the end of the install line.  No answer.  I tell her to talk to her boss and find out what is happening, and I will think about what direction I want to move in at this point.  


Despite Bergendahl's experience, Vinick says NADCA's certification standards have improved the situation. "A lot of [service companies] weren't going about it the correct way," he says. “We have an anti-fraud task force, and we’ve gone after some fraudulent duct cleaners with the help of state attorneys general.” He suggests that in addition to NADCA membership, homeowners make sure their cleaners are an established business, have appropriate insurance and are registered to do business in their state and locality.

What about ringworm? If the fungus is as contagious as doctors warn, and the spores can live several months, doesn’t it make sense to spray some sort of fungus killer into the HVAC system to kill the spores that it has sucked in from the air? Duct cleaning would not be helpful at all here; these spores are microscopic and it could actually spread them further. But given how severely contagious ringworm is, body and especially scalp, does anyone make an aerosol product that will clean the system and kill the fungus? One the resident can use, not call an HVAC company; you can’t do that when you are in an apartment. I hear it’s not the same as mold, it is much more difficult. Truth?


Your HVAC unit and air ducts deliver heated or cooled air throughout your home year-in and year-out. The air your HVAC unit produces travels through your ductwork and heats or cools your home via the air vents in each room. The dust and other particles in your home’s air are known as particulate matter, which the EPA defines as "a complex mixture of extremely small particles and liquid droplets." The EPA also notes that "particle pollution is made up of a number of components, including acids (such as nitrates and sulfates), organic chemicals, metals, and soil or dust particles." Having clean air ducts means fewer of these particles moving through your home. If you remove your furnace filter and hold it up to the light, you can probably see several hundred of these minuscule particles floating in the air. 
Had duct cleaners here coupon for 40.00 for complete home I was not here but my husband was. I told my husband that they will prolly ask for more money and I was right. 85 extra to do duct cleaning which I pled because my dryer vent was full of animal hair extensions then for 600 to clean a/c coils I said no. Just do what the coupon said. Do your homework be 100 steps ahead of these con men rember they con people all day long and know the ans to your objections
I’m a heating and air conditioning contractor. I’ve been in the trade for over 15 years. I’ve witnessed numerous duct cleaning projects and talked with many duct cleaners. Duct cleaning as it’s usually promoted is a fraud. Most duct cleaners claim to deliver cleaner air. They deliver exactly the opposite. The studies on duct cleaning prove it, including a May 1998 study sponsored by NADCA and the EPA! The stories are compelling, but they can come up with stories that “prove” anything they want. Internet searches are dominated by results from those who are paid to tell you that duct cleaning is worthwhile. Search a little more and you’ll find the truth.
If you don't agree with duct cleaning, fine. If there are some things that HVAC people can do to make the system need cleaning less often fine, but to suggest that I need to GO TO JAIL????? If you need to knock others to make yourself look better....... If duct cleaning is such a scam, why are their governing bodies like NADCA (which I do NOT belong to),several manufacturers of equipment, and national restoration franchises (I'm not a franchise either) who provide this service? I guess the whole world is stupid and only HVAC people are smart. I suppose I am scamming them when I clean puff backs, water damage, fire damage, and clean their carpets too? Or did I wake up one morning and say "ya know, it is great to be a hard working, honest owner operator, but I would love to provide a service that unlike everything else I do is a con and rips off the 90% referral business I busted my butt to earn"
Demonstrate visible evidence of microbial growth in your duct work. Some service providers may attempt to convince you that your air ducts are contaminated by demonstrating that the microorganisms found in your home grow on a settling plate (i.e., petri dish). This is inappropriate. Some microorganisms are always present in the air, and some growth on a settling plate is normal. As noted earlier, only an expert can positively identify a substance as biological growth and lab analysis may be required for final confirmation. Other testing methods are not reliable.
×