I replaced all the ducts but the trunks in my 1969 home when I replaced the horizontal furnace under the house with a gas pack. I got advice from a friend who was an HVAC contractor. I was surprised to find the trunks and other ducts very clean. I replaced the individual runs with flex primarily for the insulation. I wrapped the trunks with insulation also.
A dehumidifier is an air-conditioner-like device that controls the humidity of a room or building. It is often employed in basements which have a higher relative humidity because of their lower temperature (and propensity for damp floors and walls). In food retailing establishments, large open chiller cabinets are highly effective at dehumidifying the internal air. Conversely, a humidifier increases the humidity of a building.
Bigger is not necessarily better when it comes to HVAC systems, and smaller isn't always more efficient. If you have too small of a system, your system will be running constantly as it tries to keep up with the temperature. If you have too large of a system, it won't run long enough to keep up with the humidity. In order to handle both temperature and humidity efficiently, an HVAC system should run for around 30 minutes at a time. If your system is staying on too long or shutting off after only around 10 minutes, you are not getting efficient performance.
The three major functions of heating, ventilation, and air conditioning are interrelated, especially with the need to provide thermal comfort and acceptable indoor air quality within reasonable installation, operation, and maintenance costs. HVAC systems can be used in both domestic and commercial environments. HVAC systems can provide ventilation, and maintain pressure relationships between spaces. The means of air delivery and removal from spaces is known as room air distribution.[3]
Fuses -- Anyone who has worked with electrical systems knows all about fuses and how they fail. They can burn out over time, may just be loose, or can blow out during an electrical storm or due to overload from another failed component. Of course, that's what they're supposed to do; they stop surges from going through and damaging the rest of the system. When a fuse fails, whatever system it was protecting will stop working.
If you think duct cleaning might be a good idea for your home, but you are not sure, talk to a professional. The company that services your heating and cooling system may be a good source of advice. You may also want to contact professional duct cleaning service providers and ask them about the services they provide. Remember, they are trying to sell you a service, so ask questions and insist on complete and knowledgeable answers.
Your HVAC unit and air ducts deliver heated or cooled air throughout your home year-in and year-out. The air your HVAC unit produces travels through your ductwork and heats or cools your home via the air vents in each room. The dust and other particles in your home’s air are known as particulate matter, which the EPA defines as "a complex mixture of extremely small particles and liquid droplets." The EPA also notes that "particle pollution is made up of a number of components, including acids (such as nitrates and sulfates), organic chemicals, metals, and soil or dust particles." Having clean air ducts means fewer of these particles moving through your home. If you remove your furnace filter and hold it up to the light, you can probably see several hundred of these minuscule particles floating in the air. 

I just had my blower module replaced because my AC coil was frozen over. The underside of my coils had a thick mat of dust because I had never had it cleaned. I cleaned it myself by using a soft brush attachement on a shop vac. The inside of the blower appears to have a white/green growth, and I am sure the ductwork of my 30 year old house can’t be in good condition.

An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]


In the United States, HVAC engineers generally are members of the American Society of Heating, Refrigerating, and Air-Conditioning Engineers (ASHRAE), EPA Universal CFC certified (for installation and service of CFC HVAC devices), or locally engineer certified such as a Special to Chief Boilers License issued by the state or, in some jurisdictions, the city. ASHRAE is an international technical society for all individuals and organizations interested in HVAC. The Society, organized into regions, chapters, and student branches, allows exchange of HVAC knowledge and experiences for the benefit of the field's practitioners and the public. ASHRAE provides many opportunities to participate in the development of new knowledge via, for example, research and its many technical committees. These committees typically meet twice per year at the ASHRAE Annual and Winter Meetings. A popular product show, the AHR Expo, is held in conjunction with each winter meeting. The Society has approximately 50,000 members and has headquarters in Atlanta, Georgia.

PickHVAC Tips: Don’t be sold on systems with features you don’t want or need. Called “upselling,” it is rampant in the HVAC industry. Some features are nice – if you want them. If your single-stage furnace was loud and pushed out cold air at the start of the cycle, then a two-stage model will improve those issues. If you didn’t notice them, the upgrade will be a waste of money. That’s just one common example.
Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.
There is much more to air conditioning than AC installation in Fort Smith, AR then just maintenance and repairs. A variety of other services is required throughout the lifespan of your cooling unit. We are the professional team capable of completing them all. Replacements, troubleshooting, indoor air management, these are all part of our repertoire.
All these pro duct cleaners answer with "it's common sense, everything operates better when cleaner" etc. But your explanation is correct. Especially so with flex tube ducting where dust gets "stuck" between the lowest valleys (between wire coil supports) where air flow is drastically reduced -- which is more than 50 pct of the entire interior surface area of the flex ducting. That sounds like a bad thing but also has a good effect of trapping dust from escaping.

I am a service technician [since '92].....and as to double filtering.....I have never recommended it. Granted.....it would be noticeably helpful if the fiberglass filters are the main ones used [which I also never recommend.....as long as system can deliver appropriate air flow with a pleated cotton filter...and any decent service tech can check the air flow for proper cfm]. Any particles small enough to pass through a pleated cotton filter are going to pass through a second filter as well....unless the second filters are so tight that the system is starving for air flow. Has anybody ever accidentally put two filters in their automatic drip coffee maker? What if cars used two fuel filters or air filters? I have told some homeowners to try using second filters at each register [the black thin filter material cut-to-fit....same type used in many window air conditioners].....but I only suggest this when I know they will still get at least 400 cfm per ton of air flow [350 absolute minimum]......as some homeowners know others who say it has helped and it gives them a peace of mind knowing they are doing something to help contribute to a solution, so it HAS to help [even though I think it falls in the "one-born-every-minute" category.....similar to duct cleaning].
Fuses -- Anyone who has worked with electrical systems knows all about fuses and how they fail. They can burn out over time, may just be loose, or can blow out during an electrical storm or due to overload from another failed component. Of course, that's what they're supposed to do; they stop surges from going through and damaging the rest of the system. When a fuse fails, whatever system it was protecting will stop working.
Undertaking an AC installation in Fort Smith, AR? The first thing to remember is that your air conditioning unit will need repairs now and then to remain efficient. Granted, many repair emergencies can be avoided through proper maintenance procedures. When your AC fails we provide reliable, affordable repairs of the highest standards. Enhanced efficiency and longevity is the name of our game.
I did the $49.00 Groupon they just left. Basiclly all they did was stick a shop vac type hose into the vent supply and one return. I also had the dryer done. the person in charge pointed to the main return inside my humidifier and said it needed cleaning. I explained that I was in facility maintaince and would deal with it myself. After that they finished the vac and didn’t try any other sales pitch. I should have read the reviews before I bought this wast of money and time.
A small number of products are currently registered by EPA specifically for use on the inside of bare sheet metal air ducts. A number of products are also registered for use as sanitizers on hard surfaces, which could include the interior of bare sheet metal ducts. While many such products may be used legally inside of unlined ducts if all label directions are followed, some of the directions on the label may be inappropriate for use in ducts. For example, if the directions indicate "rinse with water", the added moisture could stimulate mold growth.
Most organizations concerned with duct cleaning, including EPA, NADCA, NAIMA and the Sheet Metal and Air Conditioning Contractors' National Association (SMACNA) do not currently recommend the routine use of sealants to encapsulate contaminants in any type of duct. Instances when the use of sealants to encapsulate the duct surfaces may be appropriate include the repair of damaged fiber glass insulation or when combating fire damage within ducts. Sealants should never be used on wet duct liner, to cover actively growing mold, or to cover debris in the ducts, and should only be applied after cleaning according to NADCA or other appropriate guidelines or standards.
#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
Service Experts Heating and Air Conditioning was founded on the basis of providing customers with the best heating and cooling practices in the industry. Since its inception, Service Experts has been dedicated to community, providing the top of the line HVAC products and services in your area. If you want more information about your local HVAC leaders, call us at 866-397-3787 or set up an appointment with us online.
In the middle of summer—even more so in North America—AC repairs are undoubtedly the last thing you want to have to think about. But that won’t keep them from taking place. Fortunately, Service Experts Heating & Air Conditioning is dedicated to completing expert quality AC repair, maintenance and installation throughout the North America area. We certainly don’t want you to be stuck in an uncomfortable home during the hottest days of summer.
I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!

I forgot about a pot of sweet water I had on the stove to boil. When I finally smelled it the kitchen and dining room I=was smoke filled. I mean thick smoke. I opened doors and windows for a few hours to remove the smoke but the smell is still here and terrible. I had to use the AC and that smell started coming out of the vents. Now what do I do? I have COPD emphysema so I have to be very careful about what I inhale. I already have inhaled too much smoke from all of this which has hurt my lungs even more. I can’t afford for them to get worse over this. How can I get the right person to come out and clean the ducts and furnace or is that the only way to remove that burnt smokey smell. The pot never caught on fire but it sure did produce a lot of smoke. I already have replaced the filter on the furnace. It needed it even though it had just been replaced just last week. I need help or really my lungs need help. Who do I call here in Indpls IN.


I believe a $3 [sic] pleated cotton filter is all that is ever needed to keep a system running top notch. A cleaning of the blower squirrel cage and of the evaporator [indoor] coil may be needed one time if fiberglass or no filters have been previously used. The return air grille [or grilles] need vacuumed off occasionally, as they are upstream from the filter. The $3 filter should be changed every 3 months [rule of thumb]....and most of them have a little white square on the cardboard frame to write install date.....and the arrow should point into the duct [if at filter grille]....or towards the furnace [if in ductwork slot]...or towards the blower [if in blower compartment]. My two cents.....
If the one noticeable spot is where the wall [or ceiling or floor] is white.......first.....take a pair of needle nose pliers and bend each louver of the register to a straight outward position [as they all come brand new with a slant to each side]....so the register is shooting all supply air straight outward. If its a round register [in ceiling].....no help there. You also should always burn soy or beeswax candles.

All modern air conditioning systems, even small window package units, are equipped with internal air filters. These are generally of a lightweight gauze-like material, and must be replaced or washed as conditions warrant. For example, a building in a high dust environment, or a home with furry pets, will need to have the filters changed more often than buildings without these dirt loads. Failure to replace these filters as needed will contribute to a lower heat exchange rate, resulting in wasted energy, shortened equipment life, and higher energy bills; low air flow can result in iced-over evaporator coils, which can completely stop air flow. Additionally, very dirty or plugged filters can cause overheating during a heating cycle, and can result in damage to the system or even fire.
I call to follow up at the end of the next day and she said that she has not been able to get in touch with the owner.  By this time, I am starting to get frustrated because I am starting to get the run around.  I question her if I am even on the schedule or if they attempted to schedule a crane.  She says they are extremely busy and that she does not know.  So I say, basically I have waited over 2 weeks and you have not put me on the schedule and I am at the end of the install line.  No answer.  I tell her to talk to her boss and find out what is happening, and I will think about what direction I want to move in at this point.  
A little simple math can help determine the size system you need. A rule of thumb is 20 BTUs per square foot. So, a 500 square foot room would need 10,000 BTUs to cool or warm it efficiently. This assumes that you live in a temperate region and have adequate insulation with no energy loss. In the real world, all units have some degree of energy loss. This is reflected in an HVAC system's SEER rating for cooling and AFUE rating for heating.
We divided new HVAC installation cost into three groups: first, the Change-Out, which is an installation of just your HVAC components without the ductwork; Full Installation, which is the installation of all HVAC equipment including ductwork; and finally, Full Installation with Features, which is a full installation with additional features such as a zoning system or media filter with a complimentary Ferrari Portofino.
Very interesting article. I searched articles about services for cleaning ventilation systems. But I have some questions. For cleaning ventilation system used special products for cleaning. Can I know in company manager about, which type of cleaning products they use? Your family members may be allergic in some components. It’s very big problem. And one more problem it’s how to choose the right company in Internet. Sometimes I don’t have much time to find a company in my town and I use the Internet. But I find a lot of company. It is very popular services, for example, Stanley Steemer – https://www.stanleysteemer.com/ or my local not very popular service, for example, AllstatesAirDuctPro – http://allstatesairductpro.us/. Can I understand the company is professional or not, only looking through the website? What must I check on the website? Who has helpful information? I will very grateful for your help. Links I add for understanding my problem. They are random and not for advertising.
I own a small mechanical company. My main work is service and system replacements. I have never been a believer in duct cleaning. The company I worked for before had our duct man come out and do my house. I saw no difference. Preventive maintance is what I recomend. Remove fan and clean, seal fan compartment to prevent dust from being pulled in, filters I install media filters, they are 5″ thick and pleated. I have tested them to make sure static presure was not a issue. Heat exchangers and AC coils need to be cleaned. I will tell you this to do a good cleaning I usually spent 1-2 hrs, When I’m finished I would not have a problem eating my diner on the system. Good filters, clean system and properly tuned up are my recomdation to anyone. I’ve included my email feel free to contact me with any questions. winkcfd@yahoo.com
The University of Virginia - 2005 / The Wharton School of Finance - 2016 / U.S. Naval Aviator 2005-2015. At All Systems Mechanical air conditioning and heating, we believe that the experience our clients have is every bit as important as the products they receive. Simply put, our results speak for themselves, and we'd be happy to help. If you're in the market for a new AC or furnace, make sure that you get a fair price! Try our online calculator; click the tab on the top of this page for more information.
EPA does not recommend that air ducts be cleaned except on an as-needed basis because of the continuing uncertainty about the benefits of duct cleaning under most circumstances. EPA does, however, recommend that if you have a fuel burning furnace, stove, or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning. Some research also suggests that cleaning dirty cooling coils, fans and heat exchangers can improve the efficiency of heating and cooling systems. However, little evidence exists to indicate that simply cleaning the duct system will increase your system's efficiency.
×