One problem occurred on Monday.  When we called at 2:30 in the afternoon to check on status, we were told that "the tech is on the phone with the parts supplier now".  It seems more likely that they had forgotten about us and our call woke them up.  But even if true, why the heck did they wait until 2:30 to order the part?  Maybe if they had ordered it in the morning they could have had it the same day.  So I'm taking off one star for that.
My point is that the brand of equipment you choose is going to affect your HVAC installation cost greatly. People often call us for an air conditioning installation job and say, “I would like to install Carrier equipment.” Now, if you are a future client of ours, I’ll have to warn you – I can be a bit of a smart-ass. Why can’t work be fun? Besides…I was in the Navy for 11 years, what do you expect. 
There are many interesting comments from several informed individuals. The question that has not been answered is how do duct systems get dusty and dirty? As a RESNET Home Energy Rater, I perform pressure tests on homes and duct systems, and the one common thread is . . . most air delivery sytems have large amounts of air leakage. The solution is to seal the duct system, and pay particular attention to the return duct system and ductwork near the air handler (the 'blower'). As others have said, a captive (sealed) duct system with proper filter maintenance should be more then adequate for most occupants. For those who have allergy, asthma, or other breathing problems, a filter with a higher MERV rating (number should be listed on the package) or a HEPA filter are good choices. These filters will capture smaller particulates and should improve the indoor air quality. Again, make certain that the entire duct system is sealed, preferably with mastic, second choice UL-181 foil tape - never use cloth duct (also known as duck) tape.
PickHVAC Tips: First, see the PickHVAC tip above about sizing a central air conditioner. It applies to heat pumps just as much. Secondly, Even if the line set for the new heat pump is the correct size, we recommend replacing the set or at least the fittings. Old lines and fittings are a major source of leaks. When refrigerant leaks out, the heat pump efficiency suffers. Eventually, the unit stops providing heating and air conditioning, and it might break down.

Some research suggests that cleaning heating and cooling system components (e.g., cooling coils, fans and heat exchangers) may improve the efficiency of your system, resulting in a longer operating life, as well as some energy and maintenance cost savings. However, little evidence exists that cleaning only the ducts will improve the efficiency of the system.


Had our ducts cleaned late April, 2016. Sodium Chlorite was sprayed into ducts after cleaning. Ever since, we have been bothered with eye and nasal passage irritation because of a “chemical” and “musty” odor. This odor is present whether or not a/c is on.) We are told the sodium chlorite (“EnviroCon, manufactured by Bio-Cide International) is used in hospital and nursing home settings and is not hazardous to health. The air duct company’s suggestion is that they come out and spray even more sodium chlorite…we absolutely don’t want this done! Have had various other recommendations about what we need to have done to remedy our problem. We will be unable to stay in our home if a resolution cannot be found. We’d be willing to replace the ductwork if necessary. (One professional suggested that the cleaning may have “knocked something loose” inside the ductwork and that is the source of the irritant.) This home was built in 1920…no idea when the present ductwork was installed. Any suggestions would be appreciated.
All modern air conditioning systems, even small window package units, are equipped with internal air filters. These are generally of a lightweight gauze-like material, and must be replaced or washed as conditions warrant. For example, a building in a high dust environment, or a home with furry pets, will need to have the filters changed more often than buildings without these dirt loads. Failure to replace these filters as needed will contribute to a lower heat exchange rate, resulting in wasted energy, shortened equipment life, and higher energy bills; low air flow can result in iced-over evaporator coils, which can completely stop air flow. Additionally, very dirty or plugged filters can cause overheating during a heating cycle, and can result in damage to the system or even fire.

There are multiple reasons to replace your HVAC system. If you have built additions onto your house, you may find your old system no longer meets the requirements for the new dimensions. Perhaps a new technological breakthrough has provided features that will improve your comfort and air quality. Most often, however, you need to replace your system because it no longer works properly.
Our heater went out last Saturday, which was a cold day.  Called a few different places and they were the only ones that called back.  The technician Tony came out and after a little testing said the main control board needed to be replaced.  He quoted us a total of $489 which seemed on the high side but it was cold and we were somewhat desperate, so we agreed and paid a parts deposit.
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.

I was able to get a next day appointment with them last week after multiple other providers did not have availability. The tech was on time and did a good job to diagnose and eventually replace the circuit board and get it up running again. The service itself would be 5 stars, although it did take a week to complete the job due to ordering the part.
Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]
With the split system, the evaporator coil is connected to a remote condenser unit using refrigerant piping between an indoor and outdoor unit instead of ducting air directly from the outdoor unit. Indoor units with directional vents mount onto walls, suspended from ceilings, or fit into the ceiling. Other indoor units mount inside the ceiling cavity, so that short lengths of duct handle air from the indoor unit to vents or diffusers around the rooms.
Contact/Relay -- Relays are electronically controlled switches that activate the various components of your HVAC system. They manage everything from the power going to the motor to automatic dampers, humidifiers, etc. Most of them are controlled by the thermostat. The most common failure for a relay is being stuck in the "open" position. Separated from its assigned contact point, it fails to complete the connection and send the message to whatever it was supposed to operate. This failure usually occurs from use over time. Each time a relay connects and sends its signal, the electrical arcing from point to point eventually causes wear and tear.

If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.
The EPA is so far behind on useful knowledge because of the lack of funding so don't be mislead. The Hvac old timers were left at the dock so to speak and missed out on the IAQ movement. The ones that are savvy and up to date on the information do Air Duct Cleaning, even tho that will lead to a few less service calls its the right thing to do for their customer. Please take a look into a return duct that has never been cleaned, I dare anyone to say it does not need to be cleaned.
When these aren't properly maintained and sanitized, they can build up dust, pollen, and even mold. This means when the air conditioner or heater turns on, the spores are released into the air for you to inhale. While some are less harmful, people who have allergies or sensitivity to certain spores will react negatively. Plus, mold is dangerous for anyone to ingest and should be avoided by regular maintenance.
Lennox, on the other hand, is probably the most expensive unit out there and I can’t stand them.  In our (humble?) experience, they have a horrible logistics chain, making repair parts difficult to come by (sometimes taking weeks), poor customer service, and the parts cost three times as much. That’s not what this article is about, so read more in: Carrier vs. Lennox Furnace Review.
I recently replaced my 44 year old furnace. Over the years we have had several construction projects inside the home. For many years breathing the heated air from the duct work caused excessive sneezing, sinus issues, and lung irritation. . The heat smelled like dust. To maximize air quality I added a humidifier, MERV-11 filter, and UV light onto the new furnace. To further improve air quality, I had the ducts cleaned and sanitized. I took before and after pictures of the inside of each return and output duct. They were filthy before, and sparkling clean and fresh after the procedure. Now when running the system, clean sanitized air flows through my whole house. A huge difference. It will make sleeping and being indoors during the winter months far more tolerable. I use window air conditioners, and run the system in the summer to keep the house air clean and fresh on hot summer days too. It works! Great decision!
Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]
If the one noticeable spot is where the wall [or ceiling or floor] is white.......first.....take a pair of needle nose pliers and bend each louver of the register to a straight outward position [as they all come brand new with a slant to each side]....so the register is shooting all supply air straight outward. If its a round register [in ceiling].....no help there. You also should always burn soy or beeswax candles.
The heat pump gained popularity in the 1950s in Japan and the United States.[13] Heat pumps can extract heat from various sources, such as environmental air, exhaust air from a building, or from the ground. Heat pumps transfer heat from outside the structure into the air inside. Initially, heat pump HVAC systems were only used in moderate climates, but with improvements in low temperature operation and reduced loads due to more efficient homes, they are increasing in popularity in cooler climates.
Though this installation is not always complicated, it's best to work with an air conditioning contractor to ensure it's done correctly. Permits are usually required for this type of work and can be obtained by a state-licensed contractor. You should not attempt to install central air conditioning on your own since you need a license to handle the refrigerant chemicals (Freon) involved.
As I type this, I am having my ducts cleaned. About 30 including returns and the furnace. $543.00. I am watching the team do it and can see the clear vacuuming tubing and how dirty it has become. I like the gentleman’s comment on “stick your head in your vacuum and breath”….I get it. The team showed me the machine and it’s filtration system…and they will show me it again after the cleaning. However, like I said before, I am actively seeing the tubing that is clear before they start and how dirty it is once they begin and continue cleaning. Reputable company and not a “fly by night” coupon service. People don’t be so cheap, that is your problem.

Although most new homes have ducts and vents already in place, many older homes have old convection heating systems or baseboard heaters without ductwork. In such cases, you will need to install ducts and vents to provide the air conditioning with a flow system. This would be the time to explore upgrading the existing heating system as well, as it will be much cheaper to do together.

This is to Blueberry who.wrote.about home rental dust problems on 12/ 06/2016. If you’ve been there 13 years.your landlord has made enough money to have those problems repaired.I would call your city property standards dept. And let them know what.conditions you are having to live.There is no excuse for living in those conditions when most problems like that are easy fixes.Especially if your kids are getting sick. Tell your landlord your.calling City Health Inspector if he doesn’t fix.the problems.
AC installation in Fort Smith, AR is vital to comfort, safety, and quality of life. The region is infamous for the unbearable heat that can often become debilitating. This is why investing into an AC to improve the overall lifestyle of your family is well worth the cost. Avoid the constant frustration by seeking the assistance of a professional team.

Interesting. Giuliano Cuete and Carlo Olcese have the exact same post about pretenders and being NADCA certified, word for word. So how do you become NADCA certified? And does that mean you are not a scam artist or a "blow and do" ripoff? hmmm, interesting. The EPA says that under normal conditions, a properly maintained system should NEVER need it's ducts cleaned.
You've probably noticed many appliances boasting an Energy Star Certification. What this means is that manufacturer voluntarily built the product to help reduce greenhouse gases and meet non-regulatory guidelines offered by the Environmental Protection Agency. To earn an Energy Star rating, a product or system must be tested by a third party that has been recognized by the EPA for meeting their testing qualifications.
PickHVAC Tips: Oil burns dirty, so it is important to have your plenum and ducts checked to see if they should be cleaned when replacing an oil furnace. If you don’t clean the plenum and ducts when replacing the furnace, the new furnace might not run as efficiently and comfortably as possible due to restricted airflow. This can also reduce the oily smell sometimes associated with oil furnaces.
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.
If there is stuff in the ducts, the fact that it’s laying there and not being blown into the rooms is proof positive that it is hurting no-one. The 5-6 exceptions you cite in this article I’ll buy, but only with the caveat that at least some of those could have been avoided by proper protection (during remodeling for example) – and if asbestos/lead/whatever winds up in your ducts- the remodeling contractor should be the one paying to remove it.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!

If you are replacing your air conditioning system, make sure that the unit is the proper size for your needs and that all ducts are sealed at the joints. A unit that is too big will cycle on and off frequently, resulting in poor moisture removal, particularly in areas with high humidity. Also make sure that your new system is designed to manage condensation effectively.
×