No matter what time it is, our experts will have you lounging in the cool air of your home quickly. We stand by our workmanship so much so that we guarantee it in writing for one full year. Our 100% Satisfaction Guarantee* firmly backs our dedication to providing the highest level of air conditioning service in the industry. In fact, Service Experts repairs, sells and installs more air conditioners than any other HVAC company through North America. More people count on us for their home comfort, so you can be certain your home will be back to being cool and comfortable in no time.
At Airco Heating and Air Conditioning, we’re proud of our years of service to the Van Buren area and look forward to helping you with your air conditioning and heating needs. We’re pleased to serve both residential and commercial customers; our team is prepared to help you with the sales, service, and installation of the comfort system that is ideal for your home or business. And be sure to ask Airco Heating and Air Conditioning for a free estimate. Whether it’s a new installation or routine service, our factory-trained technicians provide the expertise your comfort depends on. And at Airco Heating and Air Conditioning, we repair all makes and models.
There are many interesting comments from several informed individuals. The question that has not been answered is how do duct systems get dusty and dirty? As a RESNET Home Energy Rater, I perform pressure tests on homes and duct systems, and the one common thread is . . . most air delivery sytems have large amounts of air leakage. The solution is to seal the duct system, and pay particular attention to the return duct system and ductwork near the air handler (the 'blower'). As others have said, a captive (sealed) duct system with proper filter maintenance should be more then adequate for most occupants. For those who have allergy, asthma, or other breathing problems, a filter with a higher MERV rating (number should be listed on the package) or a HEPA filter are good choices. These filters will capture smaller particulates and should improve the indoor air quality. Again, make certain that the entire duct system is sealed, preferably with mastic, second choice UL-181 foil tape - never use cloth duct (also known as duck) tape.
I'm very glad that I found another guy to come replace the circuit board and put it away from the water, fix the water leak, and also find and fix another impending failure.  All of that was for much less than HVAC Service wanted to charge for repair or replacement. The other guy did a great repair, so I'm confident it will not break down again, but if it does, I will not call HVAC Service. Don't get suckered by their Yelp Deal.
Do you live in a historic home and want to tie your new system in to work with existing features? The price will go up to do the job right. All of these things add up to slow down the HVAC company, which takes more time, which costs more money for labor and parts. This is especially true if they are a legitimate company which is licensed, bonded and insured. Simply put, this is the “X-Factor” in your HVAC installation cost. Again, you could get people to do it for cheaper…but you won’t be happy with the results, I promise.
They were quick to come out and diagnose the problem with my furnace, but I thought the estimate of $549 a bit high to replace the circuit board.  So called around and found Leo's Appliance in Concord that sells appliance parts and the circuit board was only $90.49 - that is the retail cost to me, so I imagine the wholesale cost is a lot less.  So BEWARE of this company since they wanted $500!!! to replace the circuit board which is located right in the front of the furnace - extremely easy to access.  I hate it that you cannot trust repair companies.
WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.
Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.
Just had my HVAC System restored and working again on a Sunday and before the 104 weather tomorrow!!!! Called Big Mountain Heating and Air and spoke to very helpful woman named Martina. She connected me to a Technician named Josh. He was at my home within a few minutes and tackled my Honey Well system's issues. He is both skilled, personable and better yet, he got my system up and going and safe. He installed a surge suppressor on the system to prevent power surges that can kick off any system, when the electric company has to reduce power, etc.  I will be using Big Mountain in the future. Truly grateful for such good service and people. Thank you!  I recommend this firm to everyone!
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.
Since most states and municipalities don’t license air duct cleaners, you need to check their professional credentials instead, such as NADCA membership. EPA recommends all duct cleaners follow NADCA standards. Member companies must keep at least one technician on staff who has passed a NADCA test. “They have to pass rigorous testing to earn the certificate, and our code of ethics is very important,” Vinick says.
Consider what kind of heating and cooling system you want installed for the square footage of your home. Do you want a full system with a thermostat or a specific machine for the summer like a swamp cooler? Do you need a new furnace just for the winter? For any of these projects, the cost will vary depending on the quality, style and machine size you choose. If you have a tight budget, think of going smaller and upgrading over time. For example, if you can't afford to convert your entire home to solar power, you may want to consider only utilizing it to heat your water. Some other types of heating systems are:
From furnace installation and heating system installation to air conditioning installation and central air installation, Lowe’s has all your HVAC installation needs covered. Lowe’s will coordinate with independent air conditioner installation professionals to make installing central air a breeze. So stop worrying about how to install an air conditioner and contact Lowe’s to help with your air conditioning install.
Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.
Concealed behind your walls and mostly ignored, your air ducts serve as vital pathways that deliver warm and cool air throughout your home. While they may be unseen, your air ducts are working whenever you have your air conditioner or furnace running–nearly year round. Attached to your HVAC, air ducts transfer the air from these systems throughout your home. What many homeowners don't realize is that your air ducts, in nearly constant use, continually accumulate dust, grime, debris, pet dander, and allergens throughout the year. A professional air duct cleaning is necessary for better indoor air quality and the health of your family.
Very interesting article. I searched articles about services for cleaning ventilation systems. But I have some questions. For cleaning ventilation system used special products for cleaning. Can I know in company manager about, which type of cleaning products they use? Your family members may be allergic in some components. It’s very big problem. And one more problem it’s how to choose the right company in Internet. Sometimes I don’t have much time to find a company in my town and I use the Internet. But I find a lot of company. It is very popular services, for example, Stanley Steemer – https://www.stanleysteemer.com/ or my local not very popular service, for example, AllstatesAirDuctPro – http://allstatesairductpro.us/. Can I understand the company is professional or not, only looking through the website? What must I check on the website? Who has helpful information? I will very grateful for your help. Links I add for understanding my problem. They are random and not for advertising.
I took off stars for two reasons. Minus one star for issues trying to use the $50 for $25 voucher I purchased through Yelp. Although there was no minimum stipulated, the office wouldn't take it for the initial $59 diagnostic fee. If I used the 10% off First service that they offer, then they won't let me use the voucher on the actual repair bill.  I was stuck with paying the full $59 diagnostic fee.

fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.

I had my ducts somewhat cleaned December 22, 2014. The hose of the machine the technitian used did not fit in some of my vents, therefore, he did not clean them. But I still paid $428.00 for the service. I will be calling the company on Monday, and kindly ask them to come back and clean the ducts they did not as they did not fullfill their part of the service.

The HVAC installation costs below are based on residential installations only, and are priced for a single unit. Two units should be about twice the price. “Tim, shouldn’t there be a discount?” If people start giving you discounts, they are probably charging you too much to begin with.  That’s our philosophy anyway. Twice the parts and time should be twice the price from a fair contractor. The prices listed include component parts (with warranty), labor, and all materials for a complete HVAC installation.
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.
The University of Virginia - 2005 / The Wharton School of Finance - 2016 / U.S. Naval Aviator 2005-2015. At All Systems Mechanical air conditioning and heating, we believe that the experience our clients have is every bit as important as the products they receive. Simply put, our results speak for themselves, and we'd be happy to help. If you're in the market for a new AC or furnace, make sure that you get a fair price! Try our online calculator; click the tab on the top of this page for more information.
I paid $49 for a groupon. When the guy came today, he did an inspection first and said the ductwork first needed to be treated for mold; $348 for a spray that would last 8 months or $680 for an UV light purifier that would last 2 years. Also, the furnace needed to be cleaned for another $260. When I told him to just clean the ductwork, he said I would owe an additional $305 because the groupon was only good for 1 return and I had 2. I sent him packing with no services performed. Thankfully I am only out of $49! I will complain to groupon.
Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]
In addition, the black dust was found in most of the heat registers. He could rub it off on his fingers but did nothing but spray compressed air on it which didn’t make it disappear since it wasn’t loose. Also, in the register in the basement he described the black dust as being oily. The reality of that situation is that I had the AC on until the morning of the service and minutes after he snaked the hoses in my back door it started raining. The basement register had condensation from the humidity all over it. It was not oily but wet. He asked for an old towel and wiped it out. Never saw anything so black – because I never had to clean soot. That is what I have in my ducts. Soot from years of the old coal furnace.
I'd have to disagree with all of your statements. Not only are they derived from no experience in the field, you are missing keys facts. Ducts even if air tight will get dirty. If they are not getting dirty, it means they are not working. Your returns side of the duct work is always under negative pressure when the system is operational.Therefore it is always drawing air in. Seeing how dust is made up mostly from dead skin humans shed daily. Around 1.6 Pounds of skin a year per human. Living in your home anything that is air born will be drawn back towards the cold air returns. That is what they are designed for, to draw stale air back to the system to be filtered and sent back through the house.Homes with carpet will actually have cleaner duct work than home with all tile or hardwood. This is because carpets hold onto dust particles and you vacuum them up. Whereas on hardwood or tile, dust can run freely back to the returns. Even if a duct system was sealed 100%, which is next to impossible to achieve 100% would still need to be cleaned. The cleaning may only have to be every 7-10 years for example. Most homes require every 5-7 years. And that's if it was done properly the first time. If you constantly hire people that have no or minimal knowledge of duct cleaning, You home would require cleaning more often. Every 2 years. That's a trade secret, The longer they recommend before the next cleaning, the odds are they did it right. That's not to say there aren't people that lie, because there are. Just have your duct cleaner take pictures before and after cleaning. Not just an outside view. Get in there, picture entire joist liners, Whole main runs and even long round pipes. Also it helps to have a company that guarantees their work. If it's not done right, they will come back and do it until it is. Most companies that do this make sure it is right the first time. Your not getting paid to do the job twice.
Chemical biocides are regulated by EPA under Federal pesticide law. A product must be registered by EPA for a specific use before it can be legally used for that purpose. The specific use(s) must appear on the pesticide (e.g., biocide) label, along with other important information. It is a violation of federal law to use a pesticide product in any manner inconsistent with the label directions.
A house breathes just like you an I.For example every time your clothes dryer comes on it automatically creates a negative pressure inside the home.So if air goes out of the living area it has to be replaced.....now look above the ceiling fan ....you see the cover...underneath that is a hole straight to your attic....Now the stuff on your ceiling fan you call dust...call it insulation,rat fecies or anything else that is in your attic that could be pulled in your due to a negative pressure.
How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .

Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]
Service Experts Heating and Air Conditioning was founded on the basis of providing customers with the best heating and cooling practices in the industry. Since its inception, Service Experts has been dedicated to community, providing the top of the line HVAC products and services in your area. If you want more information about your local HVAC leaders, call us at 866-397-3787 or set up an appointment with us online.

 The A/C System Cleaning and restoration industry has become a very lucrative bait and switch industry that many Carpet cleaning companies, Maid services, as well as plumbing or handyman service companies are adding on to there services. These add-ons are not fully certified, trained or even have any experience in the HVAC industry. These companies are the reason prices and quality of work are all over the place. If you are looking to make a smart decision for your home a professional Duct Cleaning service will protect you for 5-7 years. This info comes from NADCA (National Air Duct Cleaning Association) which is the closest thing to a license we have for duct cleaning. They have a great site that explains this process and pricing much more in depth and factual than what has been written here. This organization is working very hard to get these bad companies exposed and out of this industry. So in saying that do your research! Green Duct Decontamination is a certified company with certified technicians that take this work very seriously. We can not have these low rated unprofessional companies paste a bad name for an entire industry. Stay away from anything under 250$ for a full duct clean this is not feasible, go look at NADCA.com and you will understand why and what these companies are doing to rob you of your dollar.

When water damage strikes, you need to act quickly. Time is of the essence. We're available 24/7 to dispatch trained, certified crews, equipment and inspection tools specializing in water damage. With our national footprint and large coverage areas throughout the country we will arrive on site and begin work quickly, minimizing the damage to your home. 
yes get a good company and pay the price, I found so much dust and dirt and wood and paint chips and bugs and even bottle caps in my ductwork. I hired a major plumbing company who cleaned ductwork and i will say they did an excellent job cleaning my vent. they did miss one point in my ductwork because i still started to see dust all over my furniture and i realized that my retunduct work that was connected with a piece of sheet metal beam which was 16" across , the contractor that built my condo used a 16" wide sheet of sheet metal to connect the vent system to my return for the air to return back into my condo. The contractor should have built a 8" x16" square duct by 6 feet long to connect my intake to my return instead of using a sheet of sheet metal 16" wide by using two 3' sections by 16 inches wide. That was a shor cut which caused a major problem fir me.
I agree, if you replace (or wash depending on type) your air filters regularly AND vaccum, then you probably don't need the ducts or air coils cleaned. However, if you purchase a pre-owned home, and the previous owners did not regularly change the air filter or vaccum the home, then duct cleaning is worth the expense especially if you are sensitive to allergens. Especially if the previous owners had pets.
I know it has to have a new concentric venting system installed, I believe it needs new plenums ( mine are rusty but both of these require extra work , so someHVAC persons are saying I do not need either!! RED FLAG THERE. Also, it will need a new drain using PVCP ?? Piping run maybe two, depending on where my evep coil drain is conected (here in TN they use to run them in with the septic lines, now they cannot be run through that way), Lastly I am not where or what these things do beides hold water but I was told It needs a filter rack and new filter base safety pan. THATSSS it that is all I know about this stuff aside from the fact that nothing up there is to code thus far LOL. !!
Stick with a maximum of 16 SEER units in most cases.  Like I said above, contractors push higher SEER units because they make more money, but these units can be expensive at this stage of development, and can drive up your HVAC installation cost.  21 SEER units run about twice the price of a 14 SEER unit, so unless you live in a desert and plan on being there for 30 more years... Likewise, a 16 SEER unit typically costs only about $600-$1,000 more than a 14 SEER, and will usually pay for itself over the lifetime of the unit.
Excalibur Water Systems helps solve the water challenges around the globe with water solutions for any possible water concerns in: water hardness, filtration of any contaminant, bacteria removal and high purity water needs and also comes with a warranty of up to 20 years at no extra cost. The best warranty for the water treatment equipment industry.

An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]
Although i love to burn candles, depending on the type your asking for problems big ones! At work one day i had been talking with co workers about these black shadows that were appearing on my ceilings and higher wall areas. They seemed to in the corners and along the stud supports , i could even see what i thought to be where all had been nailed. There would be dark shadows perfectly straight across my ceiling and then real dark circels every few inches within the lines. I thought it was the propane heat but learned quickly that oil heat will do that but not normally propane. A co worker brought me a magazine with a huge article about candles and what actually burns off them when lit, an ashy soot that is attracted to the areas on walls and ceilings that omit the most heat or warmth, of course where the drywall and studs meet and corners of the room. Its been about 8 years since i painted the entire house. I started bending to my love for candles again in the last 3 years, surprise i will be spending part of my summer re painting again!! No more candles ,well maybe at the holidays LOL
Heaters exist for various types of fuel, including solid fuels, liquids, and gases. Another type of heat source is electricity, normally heating ribbons composed of high resistance wire (see Nichrome). This principle is also used for baseboard heaters and portable heaters. Electrical heaters are often used as backup or supplemental heat for heat pump systems.

Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]
Duct cleaning has never been shown to actually prevent health problems. Neither do studies conclusively demonstrate that particle (e.g., dust) levels in homes increase because of dirty air ducts. This is because much of the dirt in air ducts adheres to duct surfaces and does not necessarily enter the living space. It is important to keep in mind that dirty air ducts are only one of many possible sources of particles that are present in homes. Pollutants that enter the home both from outdoors and indoor activities such as cooking, cleaning, smoking, or just moving around can cause greater exposure to contaminants than dirty air ducts. Moreover, there is no evidence that a light amount of household dust or other particulate matter in air ducts poses any risk to your health.
×