I own a small mechanical company. My main work is service and system replacements. I have never been a believer in duct cleaning. The company I worked for before had our duct man come out and do my house. I saw no difference. Preventive maintance is what I recomend. Remove fan and clean, seal fan compartment to prevent dust from being pulled in, filters I install media filters, they are 5″ thick and pleated. I have tested them to make sure static presure was not a issue. Heat exchangers and AC coils need to be cleaned. I will tell you this to do a good cleaning I usually spent 1-2 hrs, When I’m finished I would not have a problem eating my diner on the system. Good filters, clean system and properly tuned up are my recomdation to anyone. I’ve included my email feel free to contact me with any questions. winkcfd@yahoo.com
1). Busy companies: The company is so busy, it doesn’t need the work. It will add 70% to 100% profit, and if the customer accepts the estimate, it will move that high-margin customer to the front of the line. This often happens in the worst heat of summer when overburdened ACs and heat pumps quit and the dead of winter when furnaces give up. This is a good reason to consider pre-emptively replacing your system once it’s about 15 years old and/or has had major repairs.
PickHVAC Tips: First, see the PickHVAC tip above about sizing a central air conditioner. It applies to heat pumps just as much. Secondly, Even if the line set for the new heat pump is the correct size, we recommend replacing the set or at least the fittings. Old lines and fittings are a major source of leaks. When refrigerant leaks out, the heat pump efficiency suffers. Eventually, the unit stops providing heating and air conditioning, and it might break down.

An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]
I've been in business in Florida for 25 years and purchased a $12,000 duct cleaning system 4 years ago. In the last four years I've cleaned 5 duct systems charging around $400 each. Not a very good return on investment. What I have been doing most the time is I get a call by someone panicked because they called some low priced company to inspect their system and were told they have dangerous black mold. Then they call me to have a look. Most the time they don't have mold, ducts look very clean. However the coils are dirty and the inside of the air handler cabinet needs cleaning. Keep in mind not every system can handle supper high efficiency filters! These filters can block air flow quite a bit right out of the package. Many older systems can't handle pleated filters due to increased static pressure. "Back rooms with low air flow". I have taken many hours of classroom study on indoor air quality. Never got any certification because I don't want to pay another organization dues yearly. I think the problem with duct / system cleaning is most people are suckers for low priced scams that are rip- offs . People call me all the time and ask how much? When I tell them average $400 they hang up. I know I do the job correctly and honestly, and they are going to get racked over the coals by the scam artists by calling $79 whole house duct cleaning guys. People need to check internet, angies list and BBB reviews. But keep in mind even reviews need to be sifted through your rational person filter.
Bigger is not necessarily better when it comes to HVAC systems, and smaller isn't always more efficient. If you have too small of a system, your system will be running constantly as it tries to keep up with the temperature. If you have too large of a system, it won't run long enough to keep up with the humidity. In order to handle both temperature and humidity efficiently, an HVAC system should run for around 30 minutes at a time. If your system is staying on too long or shutting off after only around 10 minutes, you are not getting efficient performance.
20 yrs ago I bought the house I am in and a Central H/A was installed at that time. At the beginning of ea season I have the unit serviced. Every yr since I have owned the house I have had to have freon added and been told that I must have a freon leak. Fast forward to this yr when I hired a new company to do the service. They went up into the attic as part of their overall servicing. Nobody else has ever done that. He came down showing me pics on his camera phone of ducts that were not even connected to anything and in my estimation have probably been laying there for 20 yrs. Of course he fixed this. I have not needed freon this year either. I have been complaining to friends about the huge amount of dust and how I can't keep up with the cleaning away of it for a long time. Now it makes so much sense.To me it is like that duct work was just up there laying around and every time my unit was blowing, all the insulation, debris, dust and whatever else over the years was just randomly filling up those ducts. What now that they are re-connected? Will it be better? Or am I someone that needs to have my ducts cleaned? I am so confused after reading all these comments. Can one of you experts tell me what you would do before I spend a bunch of money that I don't really have? Thank you for any input you can provide. Also, feel free to respond to email address denise@digitalflak.com
The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.

A do-it-yourself approach will only scratch the surface because it is hard to reach some of the ventilation running underneath the floor or into the wall. Although it may help in clearing some of the dust and debris, you really need a professional to guarantee your system is truly spotless. The proper procedure involves the use of a powerful vacuum system with multi-brush attachments designed to loosen debris and feed into the suction. Particles are then blown outside of the house or passed through a HEPA filter inside.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!
A year and a half ago (fall of 2015) we replaced the furnace and air conditioner. From what we could determine this was the third forced air furnace and second air conditioner unit for the house. As part of the installation, we changed out the two 6″ ducts feeding the second floor with 8″ ducts. The idea was to get more cold air to the second floor in the summer. It worked and for the first time the second floor and first floor temperatures were the same when the air conditioner was running. Of course, to make the system work I close down upstairs duct damper doors in the winter and open them up in the summer.
Your HVAC unit and air ducts deliver heated or cooled air throughout your home year-in and year-out. The air your HVAC unit produces travels through your ductwork and heats or cools your home via the air vents in each room. The dust and other particles in your home’s air are known as particulate matter, which the EPA defines as "a complex mixture of extremely small particles and liquid droplets." The EPA also notes that "particle pollution is made up of a number of components, including acids (such as nitrates and sulfates), organic chemicals, metals, and soil or dust particles." Having clean air ducts means fewer of these particles moving through your home. If you remove your furnace filter and hold it up to the light, you can probably see several hundred of these minuscule particles floating in the air. 
Fuses -- Anyone who has worked with electrical systems knows all about fuses and how they fail. They can burn out over time, may just be loose, or can blow out during an electrical storm or due to overload from another failed component. Of course, that's what they're supposed to do; they stop surges from going through and damaging the rest of the system. When a fuse fails, whatever system it was protecting will stop working.

NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.
I am a service technician [since '92].....and as to double filtering.....I have never recommended it. Granted.....it would be noticeably helpful if the fiberglass filters are the main ones used [which I also never recommend.....as long as system can deliver appropriate air flow with a pleated cotton filter...and any decent service tech can check the air flow for proper cfm]. Any particles small enough to pass through a pleated cotton filter are going to pass through a second filter as well....unless the second filters are so tight that the system is starving for air flow. Has anybody ever accidentally put two filters in their automatic drip coffee maker? What if cars used two fuel filters or air filters? I have told some homeowners to try using second filters at each register [the black thin filter material cut-to-fit....same type used in many window air conditioners].....but I only suggest this when I know they will still get at least 400 cfm per ton of air flow [350 absolute minimum]......as some homeowners know others who say it has helped and it gives them a peace of mind knowing they are doing something to help contribute to a solution, so it HAS to help [even though I think it falls in the "one-born-every-minute" category.....similar to duct cleaning].
A little simple math can help determine the size system you need. A rule of thumb is 20 BTUs per square foot. So, a 500 square foot room would need 10,000 BTUs to cool or warm it efficiently. This assumes that you live in a temperate region and have adequate insulation with no energy loss. In the real world, all units have some degree of energy loss. This is reflected in an HVAC system's SEER rating for cooling and AFUE rating for heating.
Your cleaning service should involve all aspects of your duct work to maximize energy efficiency and air quality. This includes attending to the heat exchanger, blower, drain pan, plenum and coils as well. In the process, your service provider may find that you're facing larger issues than debris and build-up. The professional may recommend having your furnace repaired if they notice, for example, damage to your heat exchanger or blower motor. Generally, a furnace repair costs between $130 and $500. They may also find that an A/C coil needs to be replaced rather than cleaned and would then recommend A/C repair.
If you want to get some of the dust and debris out of your ventilation system, you can mix household cleaners like bleach with water, dip a cloth in the mix and then the wipe out the system. This will remove a layer of the spores, which could increase the quality of air a bit and help with the flow of air throughout the house until a pro can come out.
I recently replaced my 44 year old furnace. Over the years we have had several construction projects inside the home. For many years breathing the heated air from the duct work caused excessive sneezing, sinus issues, and lung irritation. . The heat smelled like dust. To maximize air quality I added a humidifier, MERV-11 filter, and UV light onto the new furnace. To further improve air quality, I had the ducts cleaned and sanitized. I took before and after pictures of the inside of each return and output duct. They were filthy before, and sparkling clean and fresh after the procedure. Now when running the system, clean sanitized air flows through my whole house. A huge difference. It will make sleeping and being indoors during the winter months far more tolerable. I use window air conditioners, and run the system in the summer to keep the house air clean and fresh on hot summer days too. It works! Great decision!
If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.
I did the $49.00 Groupon they just left. Basiclly all they did was stick a shop vac type hose into the vent supply and one return. I also had the dryer done. the person in charge pointed to the main return inside my humidifier and said it needed cleaning. I explained that I was in facility maintaince and would deal with it myself. After that they finished the vac and didn’t try any other sales pitch. I should have read the reviews before I bought this wast of money and time.
We have provided Arkansas families and businesses with quality HVAC products and services for 42 years. Offering reasonable rates and personalized service, we are a dedicated team of experts equipped to handle any service requirement. Your source for modern heating, cooling, and ventilation equipment and servicing, Wilson's Heating & Air Conditioning is the HVAC specialist in Van Buren.
Feel perfectly comfortable at home with our innovative Lennox Residential heating, cooling and air quality systems. Lennox manufactures high-efficiency HVAC systems including furnaces and air conditioners designed to conserve energy and save money. Our complementing air filtration systems, humidifiers and dehumidifiers help keep indoor air quality healthy and clean.
I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
What if you move into a 20 year old house and find that the people who owned it previously NEVER replaced the filter? It was so dirty that the HVAC system did not work at all. For most people - duct cleaning is NOT a waste of time or money. You must not have allergies. I have very bad ones plus asthma. It makes it very hard for me if I don't get it done every few years. By the way - the ducts get dusty just sitting there - especially without air going through them. Dust settles on them just like it does the furniture.
Moisture can enter the duct system through leaks or if the system has been improperly installed or serviced. Research suggests that condensation (which occurs when a surface temperature is lower than the dew point temperature of the surrounding air) on or near cooling coils of air conditioning units is a major factor in moisture contamination of the system. The presence of condensation or high relative humidity is an important indicator of the potential for mold growth on any type of duct. Controlling moisture can often be difficult, but here are some steps you can take:
×