I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
Internal insulation provides better acoustical (noise) control. Flexible duct is very low cost. These products are engineered specifically for use in ducts or as ducts themselves, and are tested in accordance with standards established by Underwriters Laboratories (UL), the American Society for Testing and Materials (ASTM), and the National Fire Protection Association (NFPA). Many insulated duct systems have operated for years without supporting significant mold growth. Keeping them reasonably clean and dry is generally adequate. However, there is substantial debate about whether porous insulation materials (e.g., fiber glass) are more prone to microbial contamination than bare sheet metal ducts. If enough dirt and moisture are permitted to enter the duct system, there may be no significant difference in the rate or extent of microbial growth in internally lined or bare sheet metal ducts. However, treatment of mold contamination on bare sheet metal is much easier. Cleaning and treatment with an EPA-registered biocide are possible. Once fiberglass duct liner is contaminated with mold, cleaning is not sufficient to prevent re-growth and there are no EPA-registered biocides for the treatment of porous duct materials. EPA, NADCA and NAIMA all recommend the replacement of wet or moldy fiber glass duct material.

Ventilating or ventilation (the V in HVAC) is the process of exchanging or replacing air in any space to provide high indoor air quality which involves temperature control, oxygen replenishment, and removal of moisture, odors, smoke, heat, dust, airborne bacteria, carbon dioxide, and other gases. Ventilation removes unpleasant smells and excessive moisture, introduces outside air, keeps interior building air circulating, and prevents stagnation of the interior air.
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.
We hope you found this article on a fair HVAC installation cost helpful. In the end, you’ll be alright so don’t worry too much. Do your research on reputable air conditioning contractors in your area, and spend time making sure that you have a company that you can trust – it will cost you less in the long-run, trust me. Take your time, follow the tips above, and you will end up with an HVAC installation cost that is more than reasonable, keeping your family comfortable for years to come. For more on topics like this, see: ASM’s Air Conditioning Blog.

Air conditioner size is measured in “tons.” However, the tonnage of an HVAC unit is not actually based on its weight. A “ton” is simply a measure of an air conditioner’s ability to cool your home. One ton is the ability of your air conditioning system to cool 12,000 BTUs (BTU stands for British Thermal Unit) in an hour. Likewise, a “2-ton” central air conditioner is able to cool 24,000 BTUs per hour.


A dehumidifier is an air-conditioner-like device that controls the humidity of a room or building. It is often employed in basements which have a higher relative humidity because of their lower temperature (and propensity for damp floors and walls). In food retailing establishments, large open chiller cabinets are highly effective at dehumidifying the internal air. Conversely, a humidifier increases the humidity of a building.
i got angies list deal for 109 air duct clenaing, dryer vent cleaning, and furnace inspection, {healthy duct cleaning} i call the company, they arrive on time. did excellent service what ever i purches i got. they give me furnace inspection and the told me that my furnace is very dirty and they offer me to clean that for 250 extra. i paid and i am very happy from this service. i try before 2 diffrent company that i got deal from them as well the just give me estimate and don’t even do the job. so guys don’t spend time if you need deep cleaning just cal this guy the offer free estimate as well.
The fact is if they are dirty why not clean them. As for the Dr’s comment about if it is not disrupted it is fine. As a pet owner sometimes un disrupted pet hair will sit in the corner of a room or under a counter un disrupted but I still clean it when I notice it. Just because you cant see it doesn’t mean you should leave it there to collect more and more. The people that don’t want there air ducts clean either simply cant afford it but would like it done. OR! the crowd that are to cheap.. You should Clean all portions of your house.
Feel perfectly comfortable at home with our innovative Lennox Residential heating, cooling and air quality systems. Lennox manufactures high-efficiency HVAC systems including furnaces and air conditioners designed to conserve energy and save money. Our complementing air filtration systems, humidifiers and dehumidifiers help keep indoor air quality healthy and clean.
Interesting. Giuliano Cuete and Carlo Olcese have the exact same post about pretenders and being NADCA certified, word for word. So how do you become NADCA certified? And does that mean you are not a scam artist or a "blow and do" ripoff? hmmm, interesting. The EPA says that under normal conditions, a properly maintained system should NEVER need it's ducts cleaned.
Multiple inventions within this time frame preceded the beginnings of first comfort air conditioning system, which was designed in 1902 by Alfred Wolff (Cooper, 2003) for the New York Stock Exchange, while Willis Carrier equipped the Sacketts-Wilhems Printing Company with the process AC unit the same year. Coyne College was the first school to offer HVAC training in 1899.[12]
PICKHVAC Terms of Use: Some of the products seen on our site are delivered through a relationship with outside suppliers like Networx.com, Google, and others. We may or may not be compensated for purchased you make as a result of our recommendation. This will NEVER affect our opinion of a product or service! PickHVAC is also a participant in the Amazon Services LLC Associates Program, an affiliate advertising program designed to provide a means for sites to earn advertising fees by advertising and linking to amazon.com
I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.
I agree, if you replace (or wash depending on type) your air filters regularly AND vaccum, then you probably don't need the ducts or air coils cleaned. However, if you purchase a pre-owned home, and the previous owners did not regularly change the air filter or vaccum the home, then duct cleaning is worth the expense especially if you are sensitive to allergens. Especially if the previous owners had pets.

I am very interested by your post. We recently had a lead inspection on our property and one thing the lead inspector suggested was to get the air ducts cleaned out. We had our ducts cleaned last year after we under went a large renovation project (since we have a toddler in the house). This year we decided to go for lead compliance and had all our lead removed (we moved out for the work). Recently, my son had a false positive lead test, which prompted us to get a lead dust inspection around the house (including having the vents dust-wiped on the inside). The levels inside the ducts weren't crazy high (but more than would be acceptable for a floor). As it turned out my son's lead levels are very low (but not zero). Is it possible however that lead dust from the inside of a vent can come out? Would this be a scenario where you think air duct cleaning would be beneficial?


Manufacturers of products marketed to coat and encapsulate duct surfaces claim that these sealants prevent dust and dirt particles inside air ducts from being released into the air. As with biocides, a sealant is often applied by spraying it into the operating duct system. Laboratory tests indicate that materials introduced in this manner tend not to completely coat the duct surface. Application of sealants may also affect the acoustical (noise) and fire retarding characteristics of fiber glass lined or constructed ducts and may invalidate the manufacturer's warranty.

I own an HVAC company. Dirt in your ducts stays there and hurts no one. It is like dirt on the ground outside. This industry was infiltrated by a bunch of money grubbing low lifes years ago. As a credible company, we do not clean air ducts. Some who were credible probably signed on not knowing what else to do or to try to make a buck another way. These companies, because they also do HVAC work not only rip off private homeowners, they are ripping off legitimate HVAC company's customers and the integrity of what can and should as a rule be a great service industry. Some probably have gotten into this to simply offer what competitors who were ripping off their customers were offering. Anyone cleaning ducts is in my opinion raising a big red flag that they cannot and should not be trusted. Political pressure from NADCA, advertising dollars, manufacturers and marketers of duct cleaning equipment, and intense competition for the customers is the only reason the government and adverstising companies have not run them out of business and that this cancer perpetuates itself.
The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.

Concealed behind your walls and mostly ignored, your air ducts serve as vital pathways that deliver warm and cool air throughout your home. While they may be unseen, your air ducts are working whenever you have your air conditioner or furnace running–nearly year round. Attached to your HVAC, air ducts transfer the air from these systems throughout your home. What many homeowners don't realize is that your air ducts, in nearly constant use, continually accumulate dust, grime, debris, pet dander, and allergens throughout the year. A professional air duct cleaning is necessary for better indoor air quality and the health of your family.
Free cooling systems can have very high efficiencies, and are sometimes combined with seasonal thermal energy storage so that the cold of winter can be used for summer air conditioning. Common storage mediums are deep aquifers or a natural underground rock mass accessed via a cluster of small-diameter, heat-exchanger-equipped boreholes. Some systems with small storages are hybrids, using free cooling early in the cooling season, and later employing a heat pump to chill the circulation coming from the storage. The heat pump is added-in because the storage acts as a heat sink when the system is in cooling (as opposed to charging) mode, causing the temperature to gradually increase during the cooling season.
When these aren't properly maintained and sanitized, they can build up dust, pollen, and even mold. This means when the air conditioner or heater turns on, the spores are released into the air for you to inhale. While some are less harmful, people who have allergies or sensitivity to certain spores will react negatively. Plus, mold is dangerous for anyone to ingest and should be avoided by regular maintenance.
When water damage strikes, you need to act quickly. Time is of the essence. We're available 24/7 to dispatch trained, certified crews, equipment and inspection tools specializing in water damage. With our national footprint and large coverage areas throughout the country we will arrive on site and begin work quickly, minimizing the damage to your home. 

We are all getting migraines several times a month. I have asthma but not ever as bad as it has been and my 2 year olds dr just informed me she potentially has asthma too. We all get sinus infections regularly and eczema and contact dermatitis. None of us have been this way until recently in our apartment. A roof leak with mold was repaired recently mold was sealed off not removed. We also had lead paint removed from a few window trims this year. I wasn’t here to see if they covered the vents. We had mice too. I vacuum everyday we have hardwood floors no one wears shoes past the font door and I’m getting over a cup full of dirt every time I vacuum. Dust on everything daily. White dust. It’s a 4 room apartment with 1 intake. They are filthy from what I can see when I change the filters. The filters are black after a few months. I feel bad to ask the homeowner to get the system cleaned, can’t afford to move (we live in the city & it’s expensive). I am going to try the shop vac to remove what I can. Any experienced hvac people please give your opinion. Should I just get it done and pay for it myself? We have lived here for 13 years. It’s never been cleaned since ive been here. Is it something I can do with a shop vac? Can i use a wet rag to get the powder dust on the inside of the vents off. One vent has what looks like chunks of dry wall or thick paint sitting in the vent and none of the vents screw into the wall, the screws just fall out. No one ever reinforced the area so the wall just basically crumbles. Kind of useless to spend the money on filters since the air and dust just blows out around the sides of the vents and one of the vents just falls right out of the wall when the heat is turned on. I don’t know why the owner doesn’t fix it. He’s been here to replace filters and saw the condition.
The amount of time it takes to clean a residential HVAC system depends on many variables such as the size of the home, the number of systems, the extent of the contamination and the number of HVAC cleaners performing the job. Ask at least two contractors to inspect your system and give you a time estimate for your particular system. This will give you a general idea of how long the job should take as well as an idea of how thoroughly the contractor plans to do the job.
Here in Atlanta we get 6 to 10 $49 coupons in the mail weekly…I have always consider them a complete scam….just had my master bathroom& bedroom and guest bath completely remodeled down to the studs…Had my 3 returns nearest the area sealed to prevent sheet rock dust to spread…it worked and I personally cleaned all 7 returns when a 5 HP , new Rigid shop Vac($99 from HD)…took one hour and I found little evidence that “I need my ducts cleaned” Had quotes from $400 to $600…I use the best air filters for my air handler and change it every 2 to 3 months…..any dust is trapped in it and I believe the Air Duct folks are all cons….
These factors are included in a "Manual J" calculation. Contractors who make these calculations before recommending a size can take a couple of hours collecting the information and making the calculation. If your contractor doesn't do it, there are services that will do it for around $99. If you're feeling particularly on the ball, there are also free online calculators.
The original furnace was a coal fired “octopus” design which had no blower to circulate the air but relied upon warm air rising to distribute the heat. That also means that the system breathed air in from the basement and most of this type did not have a cold air return system. At some point (probably in the 1940’s) the system was upgraded to a forced air gas furnace. The upgrade included replacing the 12″ diameter air ducts exposed in the basement with 6″ ducts and a cold air return system of ducts from the two (only two) air returns on the first floor.
What you might not know is that the brand you choose is one of the most important factors in determining a fair HVAC installation cost. So, before delving in-depth, let’s take a quick look at the average prices of a new air conditioner and matching coil by brand…keep in mind, these are the average prices (by brand) that contractors pay for your AC equipment, and it is meant to give you a rough guideline until you are closer to buying:
They are also often harder to install. A proper location on the roof must be selected that can support the weight of the unit. Then a platform must be built and a drain pipe for the unit must be run along the roof to avoid problems with mold and corrosion. A crane must be used to lift the unit onto the roof while a team guides it into place and hooks it up.
Did you know that cleaning your ducts and vents can help airflow and increase energy efficiency? According to the Environmental Protection Agency (EPA), keeping your air ducts and vents clear can increase energy efficiency and indoor air quality. While the cost to clean ducts and vents might sound high, the benefits to homeowners–especially those sensitive to allergens–is worth considering.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.
The liquid refrigerant is returned to another heat exchanger where it is allowed to evaporate, hence the heat exchanger is often called an evaporating coil or evaporator. As the liquid refrigerant evaporates it absorbs energy (heat) from the inside air, returns to the compressor, and repeats the cycle. In the process, heat is absorbed from indoors and transferred outdoors, resulting in cooling of the building.
Most people are now aware that indoor air pollution is an issue of growing concern and increased visibility. Many companies are marketing products and services intended to improve the quality of your indoor air. You have probably seen an advertisement, received a coupon in the mail, or been approached directly by a company offering to clean your air ducts as a means of improving your home's indoor air quality. These services typically — but not always — range in cost from $450 to $1,000 per heating and cooling system, depending on:
×