When water damage strikes, you need to act quickly. Time is of the essence. We're available 24/7 to dispatch trained, certified crews, equipment and inspection tools specializing in water damage. With our national footprint and large coverage areas throughout the country we will arrive on site and begin work quickly, minimizing the damage to your home. 
On the other hand, if a service provider fails to follow proper duct cleaning procedures, duct cleaning can cause indoor air problems. For example, an inadequate vacuum collection system can release more dust, dirt and other contaminants than if you had left the ducts alone. A careless or inadequately trained service provider can damage your ducts or heating and cooling system, possibly increasing your heating and air conditioning costs or forcing you to undertake difficult and costly repairs or replacements.

I was able to get a next day appointment with them last week after multiple other providers did not have availability. The tech was on time and did a good job to diagnose and eventually replace the circuit board and get it up running again. The service itself would be 5 stars, although it did take a week to complete the job due to ordering the part.
A year and a half ago (fall of 2015) we replaced the furnace and air conditioner. From what we could determine this was the third forced air furnace and second air conditioner unit for the house. As part of the installation, we changed out the two 6″ ducts feeding the second floor with 8″ ducts. The idea was to get more cold air to the second floor in the summer. It worked and for the first time the second floor and first floor temperatures were the same when the air conditioner was running. Of course, to make the system work I close down upstairs duct damper doors in the winter and open them up in the summer.
Concrete Blocks -- Concrete blocks are used in foundations and are often found in full basements. Insulating the spaces in the blocks is not the way to insulate them as the heat energy will travel along the concrete itself. The best way to insulate with concrete blocks is to use insulated concrete blocks, which have polystyrene incorporated into them.
I just had my blower module replaced because my AC coil was frozen over. The underside of my coils had a thick mat of dust because I had never had it cleaned. I cleaned it myself by using a soft brush attachement on a shop vac. The inside of the blower appears to have a white/green growth, and I am sure the ductwork of my 30 year old house can’t be in good condition.
Just had my HVAC System restored and working again on a Sunday and before the 104 weather tomorrow!!!! Called Big Mountain Heating and Air and spoke to very helpful woman named Martina. She connected me to a Technician named Josh. He was at my home within a few minutes and tackled my Honey Well system's issues. He is both skilled, personable and better yet, he got my system up and going and safe. He installed a surge suppressor on the system to prevent power surges that can kick off any system, when the electric company has to reduce power, etc.  I will be using Big Mountain in the future. Truly grateful for such good service and people. Thank you!  I recommend this firm to everyone!
Free cooling systems can have very high efficiencies, and are sometimes combined with seasonal thermal energy storage so that the cold of winter can be used for summer air conditioning. Common storage mediums are deep aquifers or a natural underground rock mass accessed via a cluster of small-diameter, heat-exchanger-equipped boreholes. Some systems with small storages are hybrids, using free cooling early in the cooling season, and later employing a heat pump to chill the circulation coming from the storage. The heat pump is added-in because the storage acts as a heat sink when the system is in cooling (as opposed to charging) mode, causing the temperature to gradually increase during the cooling season.
For more than 60 years Stanley Steemer has been perfecting our hot water extraction method to clean carpet with unparalleled results. Take control of the environment in your home and enjoy a cleaner, healthier living space for your family. Every carpet cleaning is Certified to remove an average of 94% of common household allergens. We remove the dirt you can see and the allergens you can't. 
While a lot of people understand the consequences of AC problems throughout the summer, the summer comes with its own set of unique issues that require a call to the plumber, too. Whether it’s a malfunctioning sprinkler system or a sewer line backup, Service Experts can help. We’ve encountered it all, and you won’t have to worry about any of it with our 24/7/365 Emergency Plumbing Service. When you need a plumber, we are here for you. And, just like all of our other services and products, any plumbing repair or work completed by Service Experts is backed by the same 100% Satisfaction Guarantee*.
Most organizations concerned with duct cleaning, including EPA, NADCA, NAIMA and the Sheet Metal and Air Conditioning Contractors' National Association (SMACNA) do not currently recommend the routine use of sealants to encapsulate contaminants in any type of duct. Instances when the use of sealants to encapsulate the duct surfaces may be appropriate include the repair of damaged fiber glass insulation or when combating fire damage within ducts. Sealants should never be used on wet duct liner, to cover actively growing mold, or to cover debris in the ducts, and should only be applied after cleaning according to NADCA or other appropriate guidelines or standards.

Whether you’re starting your air conditioner for the first time this year, or a unit isn’t running properly and you need to service an air conditioner, following a few simple steps can save you time and money. While some service jobs should be left to a professional, there are several do-it-yourself fixes you can do to keep your air conditioner cooling all summer long.
Multiple inventions within this time frame preceded the beginnings of first comfort air conditioning system, which was designed in 1902 by Alfred Wolff (Cooper, 2003) for the New York Stock Exchange, while Willis Carrier equipped the Sacketts-Wilhems Printing Company with the process AC unit the same year. Coyne College was the first school to offer HVAC training in 1899.[12]

Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.


A BTU is the amount of energy required to heat or cool one pound of water by one degree Fahrenheit. So a 1-ton air conditioner can cool 12,000 pounds of water by one degree every hour. That’s all it means, so don’t let yourself be lost in jargon! How this affects your HVAC installation cost is that the larger your house is, the more tons will be required to heat and cool it.

The Environmental Protection Agency says that “duct cleaning services typically – but not always – range in cost from $450 to $1000 per heating and cooling system, depending on the services offered, the size of the system to be cleaned, system accessibility, climactic region, and level of contamination” and type of duct material. Consumers should beware of air duct cleaning companies that making sweeping claims about the health benefits of duct cleaning – such claims are unsubstantiated. Consumers should also beware of “blow-and-go” air duct cleaning companies. These companies often charge a nominal fee and do a poor job of cleaning the heating and cooling system. These companies may also persuade the consumer into unneeded services with and/or without their permission. (If you have knowledge of a practicing “blow-and-go” air duct cleaner, contact your local Better Business Bureau to report the company, and your local, federal, and state elected officials to demand legislation.)
Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  

Had duct cleaned (apartment) however, dust is still settling throughout the apartment. Contractor said no other cleaning necessary until two (2) years. Is there a time period before dust no longer settles prior to that time? Should the vendor had worn a mask? He did not cover his face the vents and dust was blown throughout the apartment (had family help with the cleanup). I had to leave when they left because I have asthma and I couldn’t breathe without coughing. Please help!
There are many interesting comments from several informed individuals. The question that has not been answered is how do duct systems get dusty and dirty? As a RESNET Home Energy Rater, I perform pressure tests on homes and duct systems, and the one common thread is . . . most air delivery sytems have large amounts of air leakage. The solution is to seal the duct system, and pay particular attention to the return duct system and ductwork near the air handler (the 'blower'). As others have said, a captive (sealed) duct system with proper filter maintenance should be more then adequate for most occupants. For those who have allergy, asthma, or other breathing problems, a filter with a higher MERV rating (number should be listed on the package) or a HEPA filter are good choices. These filters will capture smaller particulates and should improve the indoor air quality. Again, make certain that the entire duct system is sealed, preferably with mastic, second choice UL-181 foil tape - never use cloth duct (also known as duck) tape.
Interesting. Giuliano Cuete and Carlo Olcese have the exact same post about pretenders and being NADCA certified, word for word. So how do you become NADCA certified? And does that mean you are not a scam artist or a "blow and do" ripoff? hmmm, interesting. The EPA says that under normal conditions, a properly maintained system should NEVER need it's ducts cleaned.
We installed a TRANE XL18 HVAC with a TRANE HV80 furnace 16 years ago and it still works great in Tucson, AZ.  We inquired into a replacement for the future since the R-22 refrigerant will be off market at the end of this year.  Our maintenance folks want to sell me a new system anyway (even though the TRANE works great).  We are considering the BOSCH Inverter heat pump as a lower cost option down the road.  Watch out for the tricky salesmen trying to sell beer at champagne prices though. Get estimates on whether you need to replace your current system and how much it could cost.  And if they are factory certified.
You may be familiar with air ducts that are constructed of sheet metal. However, many modern residential air duct systems are constructed of fiber glass duct board or sheet metal ducts that are lined on the inside with fiber glass duct liner. Since the early 1970's, a significant increase in the use of flexible duct, which generally is internally lined with plastic or some other type of material, has occurred.
Having evaporator and condenser coils cleaned could cost between $100 and $400. If your coils can be accessed in-place, you'll be looking at a lower service cost. If your technician needs to remove the them first, the cost should be around $400. Having the evaporator and condenser coils cleaned can have a significant impact on the efficiency of your system. If your coils are excessively dirty, they won't be able to do their job and your system will have to work harder. Keeping up with the hygiene of these components can save you money in both the short and long-term. For example, replacing evaporator coils can cost anywhere from $650 to $1200.
There are many interesting comments from several informed individuals. The question that has not been answered is how do duct systems get dusty and dirty? As a RESNET Home Energy Rater, I perform pressure tests on homes and duct systems, and the one common thread is . . . most air delivery sytems have large amounts of air leakage. The solution is to seal the duct system, and pay particular attention to the return duct system and ductwork near the air handler (the 'blower'). As others have said, a captive (sealed) duct system with proper filter maintenance should be more then adequate for most occupants. For those who have allergy, asthma, or other breathing problems, a filter with a higher MERV rating (number should be listed on the package) or a HEPA filter are good choices. These filters will capture smaller particulates and should improve the indoor air quality. Again, make certain that the entire duct system is sealed, preferably with mastic, second choice UL-181 foil tape - never use cloth duct (also known as duck) tape.
If there is stuff in the ducts, the fact that it’s laying there and not being blown into the rooms is proof positive that it is hurting no-one. The 5-6 exceptions you cite in this article I’ll buy, but only with the caveat that at least some of those could have been avoided by proper protection (during remodeling for example) – and if asbestos/lead/whatever winds up in your ducts- the remodeling contractor should be the one paying to remove it.
I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.

In the middle of summer—even more so in North America—AC repairs are undoubtedly the last thing you want to have to think about. But that won’t keep them from taking place. Fortunately, Service Experts Heating & Air Conditioning is dedicated to completing expert quality AC repair, maintenance and installation throughout the North America area. We certainly don’t want you to be stuck in an uncomfortable home during the hottest days of summer.
Vinick calls air duct cleaning an essential part of home maintenance, akin to mopping and vacuuming. "It’s like changing the oil in your car,” he says. “If you don’t change the oil, you’re going to have a problem. When your components are loaded up with debris, the system has to work harder. When you remove that debris, you get energy consumption savings.”

Furnace cleaners are mostly young men, I know this, I have been one for 15 years or so……so heres the truth, if there are any allergies, children, older people with health issues, we are GOING to make money. do not tell the company you have hired about any health complication. they are salesmen. and they don’t care about you. or your money. make sure they do a good job, then kick them out. you don’t need all the bells and whistles they wanna sell you. any idiot can clean duct work, like I said, I am one of them. I am very good at it, but I don’t have the back bone to sell a widowed old lady a humidifier that she doesn’t need for 500 bucks, overall, if you think you need this service done, which you probably don’t, get it done, do not spend anything over 300$ and do not do it again for at least ten years.


They work less jobs, thus increasing profits – think about it…if they got only half of the jobs, then they only pay half of the money required to pay employees, expenses, etc., but still have the same amount of net profit. In fact, if you do the math, they actually make more profit that their competitors do…twice as much, once you factor in their savings form only doing half of the jobs at the same amount of profit (Total Revenue – (half the normal expenses) = twice the profit). In other words, they save money by doing half of the jobs as others, for the same profit, thus increasing their overall profits.
1). Busy companies: The company is so busy, it doesn’t need the work. It will add 70% to 100% profit, and if the customer accepts the estimate, it will move that high-margin customer to the front of the line. This often happens in the worst heat of summer when overburdened ACs and heat pumps quit and the dead of winter when furnaces give up. This is a good reason to consider pre-emptively replacing your system once it’s about 15 years old and/or has had major repairs.
I always get a laugh at anyone claiming to be in the business for any length of time that doesnt understand the importance of cleaning out a ventilation system. Not only for better indoor air quality but for maintaining your heating equipment. I guess it makes more sense to some people that the furnace will just run better with a ton of dust and debris and maybe this wont be a big cause of sytem breakdown and malfunction. I mean really? Maybe this guy got a bad company and or cleaning and is a little jaded but to advise cleaning your grills , which does nothing, and replacing a filter....come on guy.
Hi guys if your not convinced yet that duct cleaning is a waste of time. I’m a HVAC business owner install heaters and air conditioners. Simple facts if you have an old system get a new return air fitted with a filter it will catch all the dirt and dust. If you still have as many do black flecks and stuff coming through it is the lining inside your ducting that has perished. So somewhere you have a hole or very old ducting. If you had rats etc its a hole somewhere. To clean, stick your vacuum in the outlet and push the hose as far as it will go this gets 99% of toys and coins fur and alike. Think about it if the object is not heavy it will come out the duct when unit is on. Service the heaters or air con units but not the ducting. I would go further to say that duct cleaning actually damages the ducting in my opinion.
These factors are included in a "Manual J" calculation. Contractors who make these calculations before recommending a size can take a couple of hours collecting the information and making the calculation. If your contractor doesn't do it, there are services that will do it for around $99. If you're feeling particularly on the ball, there are also free online calculators.
EPA does not recommend that air ducts be cleaned except on an as-needed basis because of the continuing uncertainty about the benefits of duct cleaning under most circumstances. EPA does, however, recommend that if you have a fuel burning furnace, stove, or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning. Some research also suggests that cleaning dirty cooling coils, fans and heat exchangers can improve the efficiency of heating and cooling systems. However, little evidence exists to indicate that simply cleaning the duct system will increase your system's efficiency.
×