Furnace Circuit Board -- The furnace circuit board controls a variety of functions. It not only handles the regular operation of the furnace, it also monitors the furnace's various safety circuits. Over time, vibrations from the furnace can weaken solder point and cause them to separate. Dirt and debris can cause short-circuits that damage the board. Failure of the circuit board can cause a variety of effects ranging from the fan not turning on to the complete shutdown of the furnace.
Lennox, on the other hand, is probably the most expensive unit out there and I can’t stand them.  In our (humble?) experience, they have a horrible logistics chain, making repair parts difficult to come by (sometimes taking weeks), poor customer service, and the parts cost three times as much. That’s not what this article is about, so read more in: Carrier vs. Lennox Furnace Review.
Venice warns homeowners to beware of air duct cleaning scams, especially the sort where unscrupulous cleaners offer a $49 special deal but start piling on extra fees. “It’s a bait and switch scam where they say they’ll offer unlimited cleaning, but then they throw around terms you might not understand, such as extra fees for a ‘main duct line,’” he says. “And many times, these cleaners end up walking out the door with twice the amount of money a reputable duct cleaner would charge. They’ve gotten very sophisticated at upselling.”
In variable climates, the system may include a reversing valve that switches from heating in winter to cooling in summer. By reversing the flow of refrigerant, the heat pump refrigeration cycle is changed from cooling to heating or vice versa. This allows a facility to be heated and cooled by a single piece of equipment by the same means, and with the same hardware.
Some of the research I have done suggests to have your ducts cleaned when you first purchase a new home to remove drywall dust. Maintain your system well and you shouldn't have to do it again until you want to sell. Those are the two times cleaning was suggested. So for peace of mind maybe it is a good idea to do it even if you buy a used home and then maybe every 5-10 years.
HVAC services is our go to contractor when it comes to our HVAC needs. Back in 2013, we were dealt some unforeseeable home projects, as our  HVAC was failing and needed to replace the whole system, e.g. Furnace, Blower, A/C, Condenser, Vents, etc... We reached out to a few HVAC companies (Contra Costa Heating and Air, EP builders, High Performance Heating and Air) so we could compare the bids for the job. We have had some issues with past contractors and after thoroughly screening a few of the above mentioned HVAC contractors, we awarded the bid to HVAC services because of their superior customer service and very reasonable pricing.
Indoor Fan Motor -- Indoor fans circulate the air from your house and through the system. Age and dust buildup are the two biggest contributing factors to their failure. When they are starting to fail they will often make noise. Failure of the fan will result in no heating or cooling, and if it is not repaired soon, it can cause other components to fail.

My point is that the brand of equipment you choose is going to affect your HVAC installation cost greatly. People often call us for an air conditioning installation job and say, “I would like to install Carrier equipment.” Now, if you are a future client of ours, I’ll have to warn you – I can be a bit of a smart-ass. Why can’t work be fun? Besides…I was in the Navy for 11 years, what do you expect. 


Hi guys if your not convinced yet that duct cleaning is a waste of time. I’m a HVAC business owner install heaters and air conditioners. Simple facts if you have an old system get a new return air fitted with a filter it will catch all the dirt and dust. If you still have as many do black flecks and stuff coming through it is the lining inside your ducting that has perished. So somewhere you have a hole or very old ducting. If you had rats etc its a hole somewhere. To clean, stick your vacuum in the outlet and push the hose as far as it will go this gets 99% of toys and coins fur and alike. Think about it if the object is not heavy it will come out the duct when unit is on. Service the heaters or air con units but not the ducting. I would go further to say that duct cleaning actually damages the ducting in my opinion.
Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.
Despite Bergendahl's experience, Vinick says NADCA's certification standards have improved the situation. "A lot of [service companies] weren't going about it the correct way," he says. “We have an anti-fraud task force, and we’ve gone after some fraudulent duct cleaners with the help of state attorneys general.” He suggests that in addition to NADCA membership, homeowners make sure their cleaners are an established business, have appropriate insurance and are registered to do business in their state and locality.

1. Ducts need cleaning mostly because they were not installed properly. There should be regulatory inpection and approval of clean and proper duct works on new houses. I was extremely unpset when I looked and found significant amounts of construction dust in parts of the ducts in my new house. There is apparently no way to hold the bullder to be responsible for clean ducts.
If you want to get some of the dust and debris out of your ventilation system, you can mix household cleaners like bleach with water, dip a cloth in the mix and then the wipe out the system. This will remove a layer of the spores, which could increase the quality of air a bit and help with the flow of air throughout the house until a pro can come out.
Do you live in a historic home and want to tie your new system in to work with existing features? The price will go up to do the job right. All of these things add up to slow down the HVAC company, which takes more time, which costs more money for labor and parts. This is especially true if they are a legitimate company which is licensed, bonded and insured. Simply put, this is the “X-Factor” in your HVAC installation cost. Again, you could get people to do it for cheaper…but you won’t be happy with the results, I promise.
I am very interested by your post. We recently had a lead inspection on our property and one thing the lead inspector suggested was to get the air ducts cleaned out. We had our ducts cleaned last year after we under went a large renovation project (since we have a toddler in the house). This year we decided to go for lead compliance and had all our lead removed (we moved out for the work). Recently, my son had a false positive lead test, which prompted us to get a lead dust inspection around the house (including having the vents dust-wiped on the inside). The levels inside the ducts weren't crazy high (but more than would be acceptable for a floor). As it turned out my son's lead levels are very low (but not zero). Is it possible however that lead dust from the inside of a vent can come out? Would this be a scenario where you think air duct cleaning would be beneficial?
EPA does not recommend that air ducts be cleaned except on an as-needed basis because of the continuing uncertainty about the benefits of duct cleaning under most circumstances. EPA does, however, recommend that if you have a fuel burning furnace, stove, or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning. Some research also suggests that cleaning dirty cooling coils, fans and heat exchangers can improve the efficiency of heating and cooling systems. However, little evidence exists to indicate that simply cleaning the duct system will increase your system's efficiency.
Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]
In most modern homes with up-to-date heating and air conditioning systems, filters are changed regularly through the year, so you may not even need to hire a professional. However, keep your eyes open for the accumulation of dust, dirt, dander and mold. If you see it despite regularly changing your filters it could be an indication you need a high-pressure cleaning.
Vinick calls air duct cleaning an essential part of home maintenance, akin to mopping and vacuuming. "It’s like changing the oil in your car,” he says. “If you don’t change the oil, you’re going to have a problem. When your components are loaded up with debris, the system has to work harder. When you remove that debris, you get energy consumption savings.”
Sounds like your first hvac company was ripping you off. Ask your new company to go to your coil and see if there is a leak. If there isn't the last company was just lining their pockets. If you have had ducts unhooked for a long time I would recommend duct cleaning, trust me I'm not a fan of duct cleaning myself. I have done hvac for 20 yrs. in GA. When I just bought a home built in 1996, we had all the ducts replaced immediately.
Asking how much an HVAC installation costs is kind of like asking, “how much does a new car cost?”  Well, are you buying a Porsche or a Honda? Is it a 911 or just a Boxster, and are you going to get the leather seats? Likewise, are you going to get a Carrier or a Goodman air conditioner? Does the ductwork need to be replaced? These are all questions that will affect your HVAC installation cost, so let’s take a closer look.
1). Busy companies: The company is so busy, it doesn’t need the work. It will add 70% to 100% profit, and if the customer accepts the estimate, it will move that high-margin customer to the front of the line. This often happens in the worst heat of summer when overburdened ACs and heat pumps quit and the dead of winter when furnaces give up. This is a good reason to consider pre-emptively replacing your system once it’s about 15 years old and/or has had major repairs.
I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
The Environmental Protection Agency says that “duct cleaning services typically – but not always – range in cost from $450 to $1000 per heating and cooling system, depending on the services offered, the size of the system to be cleaned, system accessibility, climactic region, and level of contamination” and type of duct material. Consumers should beware of air duct cleaning companies that making sweeping claims about the health benefits of duct cleaning – such claims are unsubstantiated. Consumers should also beware of “blow-and-go” air duct cleaning companies. These companies often charge a nominal fee and do a poor job of cleaning the heating and cooling system. These companies may also persuade the consumer into unneeded services with and/or without their permission. (If you have knowledge of a practicing “blow-and-go” air duct cleaner, contact your local Better Business Bureau to report the company, and your local, federal, and state elected officials to demand legislation.)
If you’re purchasing from a big-box store, you can expect to pay approximately $120-$1,000 for a window unit. Window units are appealing for their quick setup and relatively low cost, but they can use more energy over time than central air and only cool the room in which they’re installed. The price will vary depending on the type of air conditioner you buy and its cooling capacity. Window units, which require minimal installation, are one of the most affordable options on the market. Portable air conditioners don’t have the cooling power of a window unit, but they do have the perk of being transportable from room to room. Expect to pay between $225 and $800 for a portable air conditioner, on average. The cost of an air conditioning system with coils, condenser and line (not including installation or ductwork) can range from approximately $2,000 to $4,000 or more. If you don’t have (and don’t want to put in) ducts, a ductless mini-split air conditioner is a good option, although pricey up front. Pricing can range from $650 to $4,250 per unit on average; you’ll need one unit for each room in which you want temperature control.
Sounds like your first hvac company was ripping you off. Ask your new company to go to your coil and see if there is a leak. If there isn't the last company was just lining their pockets. If you have had ducts unhooked for a long time I would recommend duct cleaning, trust me I'm not a fan of duct cleaning myself. I have done hvac for 20 yrs. in GA. When I just bought a home built in 1996, we had all the ducts replaced immediately.
Pro Tips: Before you buy one of the learning thermostats available, you should beware of their shortcomings. First, many require a c-wire to work properly. A common problem is that the old thermostat might not use a c-wire, and this makes it confusing when swapping wires to the new thermostat. Secondly, if you change your thermostat setting often, you might become frustrated with a nest thermostat or other learning thermostat. It will be constantly trying to learn patterns in your random setting changes, and will therefore change your home’s temperature when you don’t want it to. If you have a fairly consistent schedule or don’t mind overriding the unit either manually or via the app on your way home or when leaving, then you won’t experience this issue.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.

I need a complete system replacement , before I was trying to get an evaporator coil replaced , of course the price is between $2200 an $2800 , then get told it probably will over tax my ac unit within months , so now and like everyone else what do you buy 14 ,15 16 17 seer units ,price and how do we know its reasonable  why can't there be '" a estimated price ,in the ball park, a range of prices ,so we can at least go from their .....  Now it's from 7500 to 15000. Frustrating  from the start so everybody good LUCK.   Draw a # from the hat    Unregulated  and who do you BELIEVE, just like on NCIS go with your gut feelin   
Did you know that cleaning your ducts and vents can help airflow and increase energy efficiency? According to the Environmental Protection Agency (EPA), keeping your air ducts and vents clear can increase energy efficiency and indoor air quality. While the cost to clean ducts and vents might sound high, the benefits to homeowners–especially those sensitive to allergens–is worth considering.
As you can see, if we know what the contractor is actually paying for specific equipment, we know what their labor rates are, and we know what they bid the project for, then we can also use some basic algebra (or just let the program do it for us because we’re lazy) to figure out how much of a profit they are making off of us (you) at different bid prices:
Our heater went out last Saturday, which was a cold day.  Called a few different places and they were the only ones that called back.  The technician Tony came out and after a little testing said the main control board needed to be replaced.  He quoted us a total of $489 which seemed on the high side but it was cold and we were somewhat desperate, so we agreed and paid a parts deposit.
Air conditioning units are prone to the pitfalls of wear and tear. You can prolong this, however, with proper maintenance procedures. Without regular maintenance even an immaculate AC installation in Fort Smith, Arkansas cannot guarantee performance. Our maintenance service is thorough, leaving no area unattended. If there’s a problem, we’ll catch it early and prevent avoidable breakdowns and costly repairs.
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.
Fast forward 1 year and 1 week and the circuit board that HVAC Service had installed has failed again. They came out and said that it failed from water condensation dripping onto it, so we needed to replace it and reroute the pipes to prevent future water damage.  That would cost double what I paid last year.  Why didn't they fix the problem last year at the initial repair instead of putting in a circuit board that was bound to fail again?!? They were strongly recommending that the furnace be completely replace for a huge fee to avoid the same thing happening again.  I paid $59 for them to tell me they didn't fix it right last year. This didn't feel right, so I sought a second opinion.
This is to Blueberry who.wrote.about home rental dust problems on 12/ 06/2016. If you’ve been there 13 years.your landlord has made enough money to have those problems repaired.I would call your city property standards dept. And let them know what.conditions you are having to live.There is no excuse for living in those conditions when most problems like that are easy fixes.Especially if your kids are getting sick. Tell your landlord your.calling City Health Inspector if he doesn’t fix.the problems.

After one company just took a cursory glance at our A/C and found nothing wrong, I called HVAC. I called them mostly based on Michael W's post on 8/10/14 where he told us the owner, Alberto, took his feedback and took it SERIOUSLY. That speaks VOLUMES to anyone who has been around long enough to know the characteristics of the serious players are and those who are the wannabes.
I recently did some remodeling and figured I’d get the air ducts cleaned in our 12 year old home. After obtaining 4 estimates between $572 and a whopping $3,075 for 25 vents and 2 air handlers, I knew I was in for a ride. I read through this blog and decided to use a $79 inspection camera I just found online (Home Depot) to take a look at all my ducts by removing the ceiling grilles first and then try to get into the ducts from the other end. From what I have just learned here, I believe that will take care of my “concerns”.
Did you know that cleaning your ducts and vents can help airflow and increase energy efficiency? According to the Environmental Protection Agency (EPA), keeping your air ducts and vents clear can increase energy efficiency and indoor air quality. While the cost to clean ducts and vents might sound high, the benefits to homeowners–especially those sensitive to allergens–is worth considering.

PickHVAC Tips: Installing the right size central air conditioner is extremely important. Have a load calculation done to ensure proper sizing. ACs that are too big aren’t as energy-efficient as they should be, and they cycle on and off too much. This creates over-cooling and temperature imbalance. Units that are too small run constantly in very hot weather and can’t keep your home cool. When an air conditioner is properly sized, it runs at optimal efficiency and indoor comfort.
The jury is out on whether or not cleaning your air ducts and vents has a significant enough impact to be necessary. A proven connection between immaculate duct systems and air quality in the home has not been made. However, if your vents display any of the signs listed above, cleaning would certainly be in your best interest. Allowing mold, debris and bacteria to fester could create bigger problems down the line. If having your system disinfected is within your budget, you may prefer to take care of these issues rather than ignore them.

Heaters are appliances whose purpose is to generate heat (i.e. warmth) for the building. This can be done via central heating. Such a system contains a boiler, furnace, or heat pump to heat water, steam, or air in a central location such as a furnace room in a home, or a mechanical room in a large building. The heat can be transferred by convection, conduction, or radiation.


Many homes have a forced-air HVAC system. Both the heating and the central air conditioning units share a ductwork system where they either push in or pull out warm or cooled air. There are also heating and cooling systems that don’t require ductwork — such as ductless mini-splits — but work on the same principles of heat exchange. The national average to hire an HVAC specialist is $2,920-$3,670, with costs varying depending on the work you need done and the equipment you are installing.
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.

Ventilation is the process of changing or replacing air in any space to control temperature or remove any combination of moisture, odors, smoke, heat, dust, airborne bacteria, or carbon dioxide, and to replenish oxygen. Ventilation includes both the exchange of air with the outside as well as circulation of air within the building. It is one of the most important factors for maintaining acceptable indoor air quality in buildings. Methods for ventilating a building may be divided into mechanical/forced and natural types.[16]
The key to the continued and efficient operation of your heating and cooling system is periodic maintenance. Cleaning the air duct vent system, and servicing you heating and cooling equipment will keep the system operating at its peak performance. Air ducts are cleaned for two reasons. One: to prevent debris from entering furnace and air conditioning components. Two: to prevent debris from cycling through the home. The air duct cleaning contractor needs to employ cleaning methods which successfully removes debris, and ensures that debris does not enter the occupied space. Most contractors can verify the results of the cleaning through video or pictures.
He proceeded to clean each heat register by removing the grille and blasting it with an air pressure hose toward the duct opening thinking that the dust would magically be sucked inside. In one room this caused a ceiling smoke detector to go off because the excess dust fooled it into thinking there was smoke. I put my hand in front of a register he wasn’t working on and could hardly feel a suction. Although we discussed how I open and close damper doors, I realized later that he never checked, opened or adjusted them during the cleaning. He could have closed all but the one he was working on in order to increase suction results. His next step was to blast air into the duct and then attach a “squid-like” device that slapped around inside the duct as far as he could reach. This is important! In a newer house, ducts have long straight runs from the furnace. In older houses like mine they can turn and twist. In fact, the duct we have a problem with runs straight up from the basement inside a wall and turns 90 degrees into a soffit for three feet then into two 90 degree turns to get into the floor joist area for another two feet and finally a 90 degree turn up to the second floor register. When he cleaned this one he could only get three feet into the register with the hose or squid because of the turns. That was the case with most. Hardly what could be described as a decent cleaning.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.
Be careful with HVAC change-outs.  Change-outs are only about 15-20% of the HVAC installation industry. Decrease HVAC installation cost by investing in new ductwork now if needed. Your ducts wear out too, and make sure that your ducts are in fantastic shape if you do this. Many contractors push this because it’s easy and cheap for them, with good pay-off. Do your research and replace them if you need to in order to avoid doing it later, as well as avoid potential health hazards from using old, broken ductwork.
A small number of products are currently registered by EPA specifically for use on the inside of bare sheet metal air ducts. A number of products are also registered for use as sanitizers on hard surfaces, which could include the interior of bare sheet metal ducts. While many such products may be used legally inside of unlined ducts if all label directions are followed, some of the directions on the label may be inappropriate for use in ducts. For example, if the directions indicate "rinse with water", the added moisture could stimulate mold growth.
×