Sounds like your first hvac company was ripping you off. Ask your new company to go to your coil and see if there is a leak. If there isn't the last company was just lining their pockets. If you have had ducts unhooked for a long time I would recommend duct cleaning, trust me I'm not a fan of duct cleaning myself. I have done hvac for 20 yrs. in GA. When I just bought a home built in 1996, we had all the ducts replaced immediately.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!
I guess, I will start with saying that air duct cleaning is almost never needed. It is not a scam, but it is certainly something that uneducated homeowners get suckered into. In regards to air flow, a well balanced HVAC system should be able to deliver more than enough air flow. If you are not getting good air flow, it's because your system may be out of balance. Additionally, regular cleaning/changing of the air filters will solve about 95% of your problem. Though you would be surprised how many people either a. don't have a filter or b. don't know about it and leave it there for 10+years. a washable one should be cleaned every 6 months(spring and fall) and a disposable one should be replaced every 3-4 months.

BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.
Be careful with HVAC change-outs.  Change-outs are only about 15-20% of the HVAC installation industry. Decrease HVAC installation cost by investing in new ductwork now if needed. Your ducts wear out too, and make sure that your ducts are in fantastic shape if you do this. Many contractors push this because it’s easy and cheap for them, with good pay-off. Do your research and replace them if you need to in order to avoid doing it later, as well as avoid potential health hazards from using old, broken ductwork.
On the other hand, if family members are experiencing unusual or unexplained symptoms or illnesses that you think might be related to your home environment, you should discuss the situation with your doctor. EPA has published the following publications for guidance on identifying possible indoor air quality problems and ways to prevent or fix them.
From Day 1, Alberto walked us through the process, and present us with a variety of options based our budget for the project. His customer service is the best as he did not oversell any services and did not nudge us towards buying a unit that would stretch our budget. On installation day, HVAC Services sent out a crew of 6-7 guys, all of whom were very polite and kept their work areas clean, and installed the whole system the same day.
A small number of products are currently registered by EPA specifically for use on the inside of bare sheet metal air ducts. A number of products are also registered for use as sanitizers on hard surfaces, which could include the interior of bare sheet metal ducts. While many such products may be used legally inside of unlined ducts if all label directions are followed, some of the directions on the label may be inappropriate for use in ducts. For example, if the directions indicate "rinse with water", the added moisture could stimulate mold growth.
I agree, if you replace (or wash depending on type) your air filters regularly AND vaccum, then you probably don't need the ducts or air coils cleaned. However, if you purchase a pre-owned home, and the previous owners did not regularly change the air filter or vaccum the home, then duct cleaning is worth the expense especially if you are sensitive to allergens. Especially if the previous owners had pets.
Excalibur Water Systems helps solve the water challenges around the globe with water solutions for any possible water concerns in: water hardness, filtration of any contaminant, bacteria removal and high purity water needs and also comes with a warranty of up to 20 years at no extra cost. The best warranty for the water treatment equipment industry.
A small number of products are currently registered by EPA specifically for use on the inside of bare sheet metal air ducts. A number of products are also registered for use as sanitizers on hard surfaces, which could include the interior of bare sheet metal ducts. While many such products may be used legally inside of unlined ducts if all label directions are followed, some of the directions on the label may be inappropriate for use in ducts. For example, if the directions indicate "rinse with water", the added moisture could stimulate mold growth.

I had my ducts somewhat cleaned December 22, 2014. The hose of the machine the technitian used did not fit in some of my vents, therefore, he did not clean them. But I still paid $428.00 for the service. I will be calling the company on Monday, and kindly ask them to come back and clean the ducts they did not as they did not fullfill their part of the service.
In addition, the black dust was found in most of the heat registers. He could rub it off on his fingers but did nothing but spray compressed air on it which didn’t make it disappear since it wasn’t loose. Also, in the register in the basement he described the black dust as being oily. The reality of that situation is that I had the AC on until the morning of the service and minutes after he snaked the hoses in my back door it started raining. The basement register had condensation from the humidity all over it. It was not oily but wet. He asked for an old towel and wiped it out. Never saw anything so black – because I never had to clean soot. That is what I have in my ducts. Soot from years of the old coal furnace.

You've probably noticed many appliances boasting an Energy Star Certification. What this means is that manufacturer voluntarily built the product to help reduce greenhouse gases and meet non-regulatory guidelines offered by the Environmental Protection Agency. To earn an Energy Star rating, a product or system must be tested by a third party that has been recognized by the EPA for meeting their testing qualifications.
Many homes have a forced-air HVAC system. Both the heating and the central air conditioning units share a ductwork system where they either push in or pull out warm or cooled air. There are also heating and cooling systems that don’t require ductwork — such as ductless mini-splits — but work on the same principles of heat exchange. The national average to hire an HVAC specialist is $2,920-$3,670, with costs varying depending on the work you need done and the equipment you are installing.
Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.

Some systems include an "economizer mode", which is sometimes called a "free-cooling mode". When economizing, the control system will open (fully or partially) the outside air damper and close (fully or partially) the return air damper. This will cause fresh, outside air to be supplied to the system. When the outside air is cooler than the demanded cool air, this will allow the demand to be met without using the mechanical supply of cooling (typically chilled water or a direct expansion "DX" unit), thus saving energy. The control system can compare the temperature of the outside air vs. return air, or it can compare the enthalpy of the air, as is frequently done in climates where humidity is more of an issue. In both cases, the outside air must be less energetic than the return air for the system to enter the economizer mode.
Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport
Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.

In reading through all this about duct cleaning, THE ONE preventative measure people need to realize is that a poorly installed HVAC system that is not sealed and air tight to ensure that ALL indoor air passes through a GOOD air filtration system IS THE best means of ensuring your ducts remain clean. Duct cleaning does not now and will NEVER improve an HVAC systems efficiency. Proper maintenance and installation are the key just as improper installation practices allow for dust infiltration into the duct system. I am a state licensed contractor in Texas, and unless people have their hvac system sealed and/or properly installed, duct cleaning is an absolute waste of money. My duct system is 12 years old as is as clean today as the day I installed the system with ductwork. SO before ANYONE jumps on the bandwagon of duct cleaning, get with your hvac professional FIRST.
A small number of products are currently registered by EPA specifically for use on the inside of bare sheet metal air ducts. A number of products are also registered for use as sanitizers on hard surfaces, which could include the interior of bare sheet metal ducts. While many such products may be used legally inside of unlined ducts if all label directions are followed, some of the directions on the label may be inappropriate for use in ducts. For example, if the directions indicate "rinse with water", the added moisture could stimulate mold growth.

In some older homes, there was a grey Mylar flexible duct. After years of use, it started to decompose. A duct cleaning company can come out and find why your air is so dirty and why your building doesn’t heat or cool like it used to. This is a savings on your part. You could also be sucking in Hot, dirty attic air. However, sometimes when a duct cleaning company comes out to clean it, the old duct can be destroyed and have to be replaced. Someone with little experience can replace this ductwork but if it isn’t done right it can ruin a lot of things and cost a lot in repairs.


Once i received a call from a Person he Named Steve and He told me that he is from some like GTA Home services and providing Air duct Cleaning in around 105$ and i booked an appointment because he convince me in very will mannered so i agree the services i placed an order and i don't think that they guyz do a great job as he describe but they do same as he told me on phone i'm just surprised that they do a great job and they provide me free inspections of furnace and A/C as well and they really do a great job and they don't waist my money and time. thanks Adam Stevenson and GTA home service Team.
Prices for central-air HVAC systems will vary. The national average to hire an HVAC specialist is $2,920-$3,670 but can run as high as $5,000 or even $12,000 depending on the capacity you need and other factors. Installing central air conditioning requires an entire system that works together to draw hot air out of your home. The system includes an outdoor unit, which houses the condenser and compressor, and the evaporator coils. If you don’t have an existing duct system, ductwork will need to be installed, which will affect labor and material costs. Leaking or damaged ducts will also need to be replaced.

I originally took off one star because of the SNAFU with getting the part ordered.  When Alberto called me on the phone he admitted the person had "gotten busy with other things" and apologized.  THAT was taking the high road and I was impressed by that.  Sadly, for reasons I won't guess at, Alberto has decided to take the low road in his comments and imply that they got the part as quickly as possible.  Well, we called at 2:30 so did someone spend six and a half hours finding the part??  That seems very doubtful.
With the split system, the evaporator coil is connected to a remote condenser unit using refrigerant piping between an indoor and outdoor unit instead of ducting air directly from the outdoor unit. Indoor units with directional vents mount onto walls, suspended from ceilings, or fit into the ceiling. Other indoor units mount inside the ceiling cavity, so that short lengths of duct handle air from the indoor unit to vents or diffusers around the rooms.

If not properly installed, maintained and operated, these components may become contaminated with particles of dust, pollen or other debris. If moisture is present, the potential for microbiological growth (e.g., mold) is increased and spores from such growth may be released into the home's living space. Some of these contaminants may cause allergic reactions or other symptoms in people if they are exposed to them. If you decide to have your heating and cooling system cleaned, it is important to make sure the service provider agrees to clean all components of the system and is qualified to do so. Failure to clean a component of a contaminated system can result in re-contamination of the entire system, thus negating any potential benefits. Methods of duct cleaning vary, although standards have been established by industry associations concerned with air duct cleaning. Typically, a service provider will use specialized tools to dislodge dirt and other debris in ducts, then vacuum them out with a high-powered vacuum cleaner.
×