With today’s consistently rising energy costs, improperly sealed windows, ductwork, and poor insulation can pose serious problems for many home and business owners in Arkansas. Wilson's Heating & Air Conditioning provides complete HVAC system servicing including sales, installation, maintenance and repair, and offers numerous practical solutions that will reduce your energy costs.
I agree, if you replace (or wash depending on type) your air filters regularly AND vaccum, then you probably don't need the ducts or air coils cleaned. However, if you purchase a pre-owned home, and the previous owners did not regularly change the air filter or vaccum the home, then duct cleaning is worth the expense especially if you are sensitive to allergens. Especially if the previous owners had pets.

To find companies that provide duct cleaning services, check your Yellow Pages under "duct cleaning" or contact the National Air Duct Cleaners Association (NADCA) at the address and phone number in the information section located at the end of this guidance. Do not assume that all duct cleaning service providers are equally knowledgeable and responsible. Talk to at least three different service providers and get written estimates before deciding whether to have your ducts cleaned. When the service providers come to your home, ask them to show you the contamination that would justify having your ducts cleaned.
1/27/2015Jim, we are committed to 100% satisfaction so every customer is very important to us.  Unfortunately, with all companies, there will be times when a customer may feel they have been let down.  If that happens with us, we certainly want to hear from you.  To better address your concerns, please contact Steve, our Customer Relations Specialist, directly by email at steve@hvacserviceinc.net... or give him a call at 925-318-4795. Hopefully we will hear from you soon so that we can promptly understand your issue and address the issue! Thanks Jim
We divided new HVAC installation cost into three groups: first, the Change-Out, which is an installation of just your HVAC components without the ductwork; Full Installation, which is the installation of all HVAC equipment including ductwork; and finally, Full Installation with Features, which is a full installation with additional features such as a zoning system or media filter with a complimentary Ferrari Portofino.
Compressor -- Compressors are outdoor components in your system. The compressor is the pump that circulates the refrigerants through the air-conditioner. You can hear it when it's running so you'll know if it's working just by listening. If it starts getting louder, your compressor is about to fail. If it makes no sound when it should be on, it has already failed. Compressors fail for a number of reasons. Most often they fail due to strain from another failed part such as the fan motor. Electrical storms can also damage compressors. If the sound from the compressor gets louder or if you see a decrease in performance, you should have your compressor checked. A failed compressor will not heat or cool your house.
As a homeowner and an owner of rental property I can tell you that the air ducts sometimes need to be cleaned. If you have had pets or anyone smoking in your home (even a visitor) for any length of time, having the ducts cleaned is really good idea. I had a tenant who did not smoke, but got married to a smoker more than year after moving in. When I realized someone was smoking I had them move out, but the smell was awful. I had the ducts cleaned and sanitized (it was a bit extra). The ducts were shiny like new afterwards. I left the windows open for a few days and we cleaned the place super clean and then replaced the carpets. The duct cleaning was worth every penny because the house looked, smelled, and felt new afterward. I plan to have my own house ducts cleaned again this year as we have two cats. We had them cleaned about 12 years ago and they found building materials in the ducts! If you move into a house that has never had them cleaned, it is good to do it. If you have allergies, clean the ducts to see if it helps. You never know what is in your ducts if you have never had them cleaned.

I can’t believe I got ripped off by this Air Duct Cleaners. I called them for this $63 coupon per furnace unlimited vents then when they came after he checked it all I hear is I have molds and leak all is worth $499, $799, $899 per furnace but I told him to just clean the duct and patch the single leak per furnace worth $38 each. Still eanding $899 total. All the work he done is in less than an hour he didnt even go to each vent to clean it. All he did is to path the air leak on that entry pipe to the furnace and open the main venting system, vacuum it, and wash the floor of the vent with a solution. Overall time is about 20 mins talking with me discussing all the option which thinking they made me think I don’t really have an option and 40 mins wash and vacuum he took pictures of before and after of only one furnace. He gave me a receipt without the details on what he has done in the house just the name and price. I think we may need a strict law to punish and control all this companies who do this so other company who do good will despise them.
While your HVAC filter is designed to trap particulate matter and prevent it from entering your air ducts, particles often still get through. The number of particles your HVAC filter traps is directly connected to the quality of air in your home: the lower the quality of air, the more particles will be present, and the more particles are likely to get through the filter. If these particles are allowed to build up, your HVAC system can become less efficient, operating longer to heat or cool your home. An inefficient HVAC system can result in inconsistent heating or cooling, higher utility costs, and expensive HVAC unit repairs, such as an A-coil or blower motor replacement if the problem is left unchecked. Air duct cleaning from Sears, which focuses on the dirt in your air ducts, can boost the efficiency of a dirty HVAC system, cleaning out the particulate matter that can hinder HVAC effectiveness and affect your health.
Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!
EPA does not recommend that air ducts be cleaned except on an as-needed basis because of the continuing uncertainty about the benefits of duct cleaning under most circumstances. EPA does, however, recommend that if you have a fuel burning furnace, stove, or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning. Some research also suggests that cleaning dirty cooling coils, fans and heat exchangers can improve the efficiency of heating and cooling systems. However, little evidence exists to indicate that simply cleaning the duct system will increase your system's efficiency.
PickHVAC Tips: Installing the right size central air conditioner is extremely important. Have a load calculation done to ensure proper sizing. ACs that are too big aren’t as energy-efficient as they should be, and they cycle on and off too much. This creates over-cooling and temperature imbalance. Units that are too small run constantly in very hot weather and can’t keep your home cool. When an air conditioner is properly sized, it runs at optimal efficiency and indoor comfort.
Professional cleaning involves getting the dust and debris outside, so they use outdoor ventilation equipment. It is so important that homeowners make sure the professional contractor is using good equipment then, as they could otherwise spread the spores into the home and further agitate sensitive family members. In the case of mold, a cleaner will only be able to tell you it is there, followed by needing an additional mold professional to come out and test or remove the mold. Air duct cleaning industries do not require state licensing, so make sure to check for a company with references.
How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .
I’m a heating and air conditioning contractor. I’ve been in the trade for over 15 years. I’ve witnessed numerous duct cleaning projects and talked with many duct cleaners. Duct cleaning as it’s usually promoted is a fraud. Most duct cleaners claim to deliver cleaner air. They deliver exactly the opposite. The studies on duct cleaning prove it, including a May 1998 study sponsored by NADCA and the EPA! The stories are compelling, but they can come up with stories that “prove” anything they want. Internet searches are dominated by results from those who are paid to tell you that duct cleaning is worthwhile. Search a little more and you’ll find the truth.
I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.
Dehumidification (air drying) in an air conditioning system is provided by the evaporator. Since the evaporator operates at a temperature below the dew point, moisture in the air condenses on the evaporator coil tubes. This moisture is collected at the bottom of the evaporator in a pan and removed by piping to a central drain or onto the ground outside.
Just had my HVAC System restored and working again on a Sunday and before the 104 weather tomorrow!!!! Called Big Mountain Heating and Air and spoke to very helpful woman named Martina. She connected me to a Technician named Josh. He was at my home within a few minutes and tackled my Honey Well system's issues. He is both skilled, personable and better yet, he got my system up and going and safe. He installed a surge suppressor on the system to prevent power surges that can kick off any system, when the electric company has to reduce power, etc.  I will be using Big Mountain in the future. Truly grateful for such good service and people. Thank you!  I recommend this firm to everyone!
Internal insulation provides better acoustical (noise) control. Flexible duct is very low cost. These products are engineered specifically for use in ducts or as ducts themselves, and are tested in accordance with standards established by Underwriters Laboratories (UL), the American Society for Testing and Materials (ASTM), and the National Fire Protection Association (NFPA). Many insulated duct systems have operated for years without supporting significant mold growth. Keeping them reasonably clean and dry is generally adequate. However, there is substantial debate about whether porous insulation materials (e.g., fiber glass) are more prone to microbial contamination than bare sheet metal ducts. If enough dirt and moisture are permitted to enter the duct system, there may be no significant difference in the rate or extent of microbial growth in internally lined or bare sheet metal ducts. However, treatment of mold contamination on bare sheet metal is much easier. Cleaning and treatment with an EPA-registered biocide are possible. Once fiberglass duct liner is contaminated with mold, cleaning is not sufficient to prevent re-growth and there are no EPA-registered biocides for the treatment of porous duct materials. EPA, NADCA and NAIMA all recommend the replacement of wet or moldy fiber glass duct material.

All of you have dentists, you have doctors, you have preachers, you have mechanics. You don’t have to know everything about everything but you have to have people in your life that you can trust. Don’t just open up the phone book and pick a mechanical (HVAC) contractor. Call your friends and family and ask for referrals. There are no black and white (scam or not a scam) answers here.
Clean the condenser fan blades before the start of the cooling season. Brush any dust or debris off gently and then uncover the condenser coils, gently cleaning the dirty side. Then wrap the motor and other electrical components in plastic bags and gently spray from the inside with a hose. Now check the base pan under the unit and clear it out of any debris that has gathered.
Our heater went out last Saturday, which was a cold day.  Called a few different places and they were the only ones that called back.  The technician Tony came out and after a little testing said the main control board needed to be replaced.  He quoted us a total of $489 which seemed on the high side but it was cold and we were somewhat desperate, so we agreed and paid a parts deposit.
Despite such anecdotal experiences, there's no scientific evidence that regular residential air duct cleaning improves air quality, according to a 1997 brochure published by the Environmental Protection Agency. Laureen Burton, senior scientist in the EPA Indoor Environments Division, says that while the document is nearly two decades old, the science hasn't changed and the agency stands by its recommendations.
Our unit is 16 years old and we've had it checked out recently since it seems to be running excessively. Over all the tech says it is putting out well; it's the correct size, we have no shade and we've been having extreme heat with high humidity. The info you provided is very helpful and will help us make an informed decision when the time comes. Thank you so much.
I am NADCA Certified Air Systems Cleaning Specialist. Over the years I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
Concrete Blocks -- Concrete blocks are used in foundations and are often found in full basements. Insulating the spaces in the blocks is not the way to insulate them as the heat energy will travel along the concrete itself. The best way to insulate with concrete blocks is to use insulated concrete blocks, which have polystyrene incorporated into them.
I was told that 15 out vents would be cleaned and one main vent. the guy came over and gave me an estimate of $500. I had acquired a groupon for $49. the guy said just doing the out vents and one main vent would accomplish nothing. Now I am in dispute with the groupon people for a refund which they won’t give and have to go ahead and waste the money and let them do it. Is their doing the 15 outvents and one main one going to accomplish anything?
Your HVAC unit and air ducts deliver heated or cooled air throughout your home year-in and year-out. The air your HVAC unit produces travels through your ductwork and heats or cools your home via the air vents in each room. The dust and other particles in your home’s air are known as particulate matter, which the EPA defines as "a complex mixture of extremely small particles and liquid droplets." The EPA also notes that "particle pollution is made up of a number of components, including acids (such as nitrates and sulfates), organic chemicals, metals, and soil or dust particles." Having clean air ducts means fewer of these particles moving through your home. If you remove your furnace filter and hold it up to the light, you can probably see several hundred of these minuscule particles floating in the air. 
On the other hand, if a service provider fails to follow proper duct cleaning procedures, duct cleaning can cause indoor air problems. For example, an inadequate vacuum collection system can release more dust, dirt and other contaminants than if you had left the ducts alone. A careless or inadequately trained service provider can damage your ducts or heating and cooling system, possibly increasing your heating and air conditioning costs or forcing you to undertake difficult and costly repairs or replacements.
×