My point is that the brand of equipment you choose is going to affect your HVAC installation cost greatly. People often call us for an air conditioning installation job and say, “I would like to install Carrier equipment.” Now, if you are a future client of ours, I’ll have to warn you – I can be a bit of a smart-ass. Why can’t work be fun? Besides…I was in the Navy for 11 years, what do you expect. 
My heat pump/hvac system is not blowing cold air anymore, got checked out was told compressor broken. was told it cost  almost the same to repair/replace they recommend whole system. It's the same company that installed it 18 years ago, telling me that system is old and it will cost $9-10k for new system, because furnace has to be replaced with new hvac. what to do, need answers thanks????
I replaced all the ducts but the trunks in my 1969 home when I replaced the horizontal furnace under the house with a gas pack. I got advice from a friend who was an HVAC contractor. I was surprised to find the trunks and other ducts very clean. I replaced the individual runs with flex primarily for the insulation. I wrapped the trunks with insulation also.
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.

You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 
Humidifiers/Dehumidifiers: Humidifiers add needed moisture to the air in winter and very dry climates. Dehumidifiers remove dampness any time of the year. Central air conditioners dehumidify too, but in very humid climates, you might want to remove humidity without also cooling the air. You have a good range of options for both of these HVAC accessories. Whole-house humidifiers cost $350 to $800 installed, while dehumidifiers are $1,250 to $2,000 or slightly more.
An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]

Be careful with HVAC change-outs.  Change-outs are only about 15-20% of the HVAC installation industry. Decrease HVAC installation cost by investing in new ductwork now if needed. Your ducts wear out too, and make sure that your ducts are in fantastic shape if you do this. Many contractors push this because it’s easy and cheap for them, with good pay-off. Do your research and replace them if you need to in order to avoid doing it later, as well as avoid potential health hazards from using old, broken ductwork.


Our Fort Smith, Arkansas area restoration services are available at your convenience. We provide emergency services after devastating property damage and work hard to restore and clean as much of the contents and structure as possible. We'll Work With You and Your Insurance Company to cover costs and expedite the process. If you need cleaning and restoration services or are looking for ways to create a healthier, more efficient environment, contact McMahon's Cleaning & Restoration, LLC to get started.
Some systems include an "economizer mode", which is sometimes called a "free-cooling mode". When economizing, the control system will open (fully or partially) the outside air damper and close (fully or partially) the return air damper. This will cause fresh, outside air to be supplied to the system. When the outside air is cooler than the demanded cool air, this will allow the demand to be met without using the mechanical supply of cooling (typically chilled water or a direct expansion "DX" unit), thus saving energy. The control system can compare the temperature of the outside air vs. return air, or it can compare the enthalpy of the air, as is frequently done in climates where humidity is more of an issue. In both cases, the outside air must be less energetic than the return air for the system to enter the economizer mode.
As for the price I think my review was fair in stating what value we got for what I deemed to be a slightly higher price than others might charge.  I did not take any stars off for the price, and still am not, but I am taking another star off because of Alberto's comments, which are deceptive and not the same thing he told me in person.  Alberto, I suggest you stick with the high road in the future.
Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.
To qualify for a tax credit from the federal government, you must save the manufacturer's certificate from your system. The IRS won't require the certificate at the time you file your federal tax forms, but they recommend keeping it with your records in case of an audit. It proves that you purchased a qualifying product. The government offers tax credits for:

Some of the research I have done suggests to have your ducts cleaned when you first purchase a new home to remove drywall dust. Maintain your system well and you shouldn't have to do it again until you want to sell. Those are the two times cleaning was suggested. So for peace of mind maybe it is a good idea to do it even if you buy a used home and then maybe every 5-10 years.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!

DIY: Most DIY installations go smoothly. The major brands have compatibility checkers to see which of their models will work with the wiring your old thermostat is using. Potential problems involve the need for a C-wire, or common wire, when the existing bundle doesn’t include one. There are solutions discussed in our Thermostat Buying Guide, linked to below.
All of the products discussed above are registered solely for the purpose of sanitizing the smooth surfaces of unlined (bare) sheet metal ducts. No products are currently registered as biocides for use on fiber glass duct board or fiber glass lined ducts, so it is important to determine if sections of your system contain these materials before permitting the application of any biocide.
I am very interested by your post. We recently had a lead inspection on our property and one thing the lead inspector suggested was to get the air ducts cleaned out. We had our ducts cleaned last year after we under went a large renovation project (since we have a toddler in the house). This year we decided to go for lead compliance and had all our lead removed (we moved out for the work). Recently, my son had a false positive lead test, which prompted us to get a lead dust inspection around the house (including having the vents dust-wiped on the inside). The levels inside the ducts weren't crazy high (but more than would be acceptable for a floor). As it turned out my son's lead levels are very low (but not zero). Is it possible however that lead dust from the inside of a vent can come out? Would this be a scenario where you think air duct cleaning would be beneficial?
Had duct cleaned (apartment) however, dust is still settling throughout the apartment. Contractor said no other cleaning necessary until two (2) years. Is there a time period before dust no longer settles prior to that time? Should the vendor had worn a mask? He did not cover his face the vents and dust was blown throughout the apartment (had family help with the cleanup). I had to leave when they left because I have asthma and I couldn’t breathe without coughing. Please help!
This is where i found where the major problem was for the dust problem in my home. I took down the sheet metal that was 16" wide down by taking the screws out that keep it attached and when i took it down i, could not beleive the amountbof dust that was up there, inhad to put on breathing nasks to actually scoop out all the cust with my hads and then i used my shop vac then bleached everything, i would say that i filled up a 5 gallon maybe more not counting all the dust that was attached to the side of the beams that was all wood , because the contractor did not actually build a 16" wide return all out of metal , butvinstead used the sheet metal plate as a short cut to make a suare box using my beams in my basement to make a suare box. I was told contractors do that often and i feel that should be outlawed because it caused my sinus and allery problems,nwhich almost caused me to die. so everyone should make sure their ductwork was made properly. Yes seal it . Cover all openings. So it was not the contractors fault that my vents still had dust, in them, he was afraid tomgetvon top of my pool table to try to get iside the short cut ductwork with the 16" wide sheet metal. To everyone, make sure you clean your vent system. And make sure you could see it visually like i did , neither i or the contractor had no clue the problem was right above my pool table because of the make shift ductwork. The contactor shoul have made a squrae duct like the rest instead of using my beams as a short cut. That could be whyba lot of people start to have major allergy problems and maybe even ashma.so coverall holes to prevent dust to be taken in and all bugs etc. then make sure you clean your ductwork as you see reasonable, they say every 5 years , but i say evry 2 to 3 years, but you can do it yoursely.. You need a good air hose and suction vacum like a shop vac, do a little research. I invented something a while back like 18 to 20 years ago , and now it is on the market to help homeowners such as ourselves with this dust problem. I cannont say anymore because i have to make sure that it was not my research and idea that solved my problem and for all the others that are using what i invented ..there was nothing on the patent search that i hired an invention company to do, back then. Once yor vents are cleaned properly younwill be very happybif you are an allery sufferer. Stop the children for throwing things into the ductwork and sweeping things into the ductwork, keeping your vent system is clean once youbclean it right the first time, just maintain it , you dhould keepmthe hvac system clean such as coils etc it truly helps,people vome into my condo and they cannont beleive how cold it igets and how my system works so well. it is because i have my whole duct system sealed outsid with the duct sealant and my coils i vleaned my self and take the time that the furnase fan is cleaned because that could have a lot of major dust attached to it, mine had a lot of caked on dust it was like hard dirt. Yxounwill save on allergy bills nasal sprays, i wish I could say more because incould say something to really keep your whole duct system clean for years once you do a first good cleaning of intake and return vents. until i email one of the major companies to see where they got my idea from. Intrulybhope it was not from the invention company i hired years ago who did the patent search for my idea. I becam
I to had an odd layer of white'ish dust building up especially during seasonal periods when the HVAC ran a a lot. I carefully swept up the fine dust into a small pile and had it analyzed. Turns out it was very fine fiberglass powder dust. It turns out it is the insulation form the attic! (My attic has blown in insulation). Turns out if you (I) had small gaps around my HVAC registers in the ceiling whee the airs blows into the room. What occurred in my case was that the exiting air at that seam creates a vacuum effect at the grate vent cover and draws and then blows fine insulation dust from the attic into the house. Removing each register grate and sealing each tin outlet gap with calking between the dry wall ceiling and tin fixed the issue. A couple were so bad with bowed gaps I had to screw down the bowed tin to the attaching stud better. Checking the very same glass top desk that catches and shows any dust accumulation now shows only very small amounts of normal house dust build up over several weeks. A big, big improvement. You might have a look by simply removing a couple vent covers yourself.
Heating, ventilation, and air conditioning (HVAC) systems have been shown to act as a collection source for a variety of contaminants that have the potential to affect health, such as mold, fungi, bacteria, and very small particles of dust. The removal of such contaminants from the HVAC system and home should be considered as one component in an overall plan to improve indoor air quality.

The HVAC installation costs below are based on residential installations only, and are priced for a single unit. Two units should be about twice the price. “Tim, shouldn’t there be a discount?” If people start giving you discounts, they are probably charging you too much to begin with.  That’s our philosophy anyway. Twice the parts and time should be twice the price from a fair contractor. The prices listed include component parts (with warranty), labor, and all materials for a complete HVAC installation.


As for the price I think my review was fair in stating what value we got for what I deemed to be a slightly higher price than others might charge.  I did not take any stars off for the price, and still am not, but I am taking another star off because of Alberto's comments, which are deceptive and not the same thing he told me in person.  Alberto, I suggest you stick with the high road in the future.
I noticed a lot of negative feedback, though unfortunately there are many dishonest companies out there. I currently work with a company that cleans duct work and we DO NOT use any scare tactics or up sell services or equipment. Once every 10years of course there are exceptions. We clean supply, returns, air handler, housing, motor, and fan. Though be discerning when qualifying anyone to work in your home. I would ask for REAL REFERENCES to contact.
I own a small mechanical company. My main work is service and system replacements. I have never been a believer in duct cleaning. The company I worked for before had our duct man come out and do my house. I saw no difference. Preventive maintance is what I recomend. Remove fan and clean, seal fan compartment to prevent dust from being pulled in, filters I install media filters, they are 5″ thick and pleated. I have tested them to make sure static presure was not a issue. Heat exchangers and AC coils need to be cleaned. I will tell you this to do a good cleaning I usually spent 1-2 hrs, When I’m finished I would not have a problem eating my diner on the system. Good filters, clean system and properly tuned up are my recomdation to anyone. I’ve included my email feel free to contact me with any questions. winkcfd@yahoo.com
I am in need of HVAC ADVICE!! I need a new furnace badly, mine is cracked. I have bought both a 95 % AFUE furnace and a 5 Ton evap coil, I figured it should all be replaced at once for both cost and efficency. My question is with all the negaitive things I have heard about companies ripping you off, what type of price should I pay someone for putting in those two items and bringing everything in my attic up to code? I have been quoted $550 - $ 3300. Wide margin here!! Then of course comes the licencing part!! I know in my heart that I should use a licenced contractor but I have had such bad luck and prices from them that honestly one that was licened in Ga. and just not here in TN and is a tech. which charges 1100 - 2200 less sounds good as so long as I pay some type of Profenial HVAC person say $100 to inspect the work after its done and before I pay them.

Asbestos removal tip.  Don’t trust any HVAC installation company that says that they will remove asbestos for you. They will do either one of two things: remove it and do a horrible job because they don’t know how (an illegal act in California, finable by up to $250,000), or they will say they did and never actually do it, which is dangerous to your health. Any HVAC contractor worth their weight will know not to touch it. Call an asbestos abatement company – it should cost around $500-$1,000, and your HVAC installation company will come in right after them and do the installation to decrease cost and inconvenience.

I read your article with interest and think it is a good start. One service that is always talked about is fogging ductwork for sanitizing. Many companies offer this service for disinfecting or adding a clean smell to the ductwork. Before any chemical or disinfectant is used, please read the MSDS (Material Safety Data Sheet). You might be surprise on what you are putting into the air stream. This is a high profit service and should be explored thoroughly before purchasing,


First of all, I think it is great that there are many companies out there who look out for the customer and protect their interest. Secondly, I think it is also important that customers consider having their HVAC systems checked thoroughly before moving into a new home. I have heard a couple of horror stories where previous owners have not had the best housekeeping skills. Even when the appearance of the home seems it has been well kept, keep in mind that surface clean only goes so far. You can never tell what lies underneath.
They were quick to come out and diagnose the problem with my furnace, but I thought the estimate of $549 a bit high to replace the circuit board.  So called around and found Leo's Appliance in Concord that sells appliance parts and the circuit board was only $90.49 - that is the retail cost to me, so I imagine the wholesale cost is a lot less.  So BEWARE of this company since they wanted $500!!! to replace the circuit board which is located right in the front of the furnace - extremely easy to access.  I hate it that you cannot trust repair companies.

Having evaporator and condenser coils cleaned could cost between $100 and $400. If your coils can be accessed in-place, you'll be looking at a lower service cost. If your technician needs to remove the them first, the cost should be around $400. Having the evaporator and condenser coils cleaned can have a significant impact on the efficiency of your system. If your coils are excessively dirty, they won't be able to do their job and your system will have to work harder. Keeping up with the hygiene of these components can save you money in both the short and long-term. For example, replacing evaporator coils can cost anywhere from $650 to $1200.


HVAC equipment is estimated to last about 15 to 20 years. Yet over the years, parts go out and need to be repaired. Heat sensors, exchangers, and ducts can become worn out. Air conditioning motors may need repairing from time to time. For repairs to your heating and air conditioning systems, and even general maintenance, let HomeAdvisor help. Enter your zip code and let us connect you with prescreened HVAC repair services near you.
×