I read your article with interest and think it is a good start. One service that is always talked about is fogging ductwork for sanitizing. Many companies offer this service for disinfecting or adding a clean smell to the ductwork. Before any chemical or disinfectant is used, please read the MSDS (Material Safety Data Sheet). You might be surprise on what you are putting into the air stream. This is a high profit service and should be explored thoroughly before purchasing,
Preventing against air leakage is great, but the only way to keep dust and debris out of a duct system would be to completely seal off the return-air side of the system, which would render the system useless. Cold-air returns will always pull dust and other particles into the system. A high-MERV rated filter is definitely a good idea, but it does nothing to keep the return side of the system clean. Definitely agree though to use foil tape to seal seams, etc. Duct tape dries out over time and as it does can actually add more particles to the air.
They were quick to come out and diagnose the problem with my furnace, but I thought the estimate of $549 a bit high to replace the circuit board.  So called around and found Leo's Appliance in Concord that sells appliance parts and the circuit board was only $90.49 - that is the retail cost to me, so I imagine the wholesale cost is a lot less.  So BEWARE of this company since they wanted $500!!! to replace the circuit board which is located right in the front of the furnace - extremely easy to access.  I hate it that you cannot trust repair companies.
Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]
NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.
So, naturally I respond with, “you don’t tell your doctor which medication to prescribe you, do you?” The point is, on the residential level, who you get to install your HVAC unit is far more important than which unit you choose.  Keep your options open and let your HVAC contractor make a few recommendations – that’s why you spent time finding a reputable contractor!

At Airco Heating and Air Conditioning, we’re proud of our years of service to the Van Buren area and look forward to helping you with your air conditioning and heating needs. We’re pleased to serve both residential and commercial customers; our team is prepared to help you with the sales, service, and installation of the comfort system that is ideal for your home or business. And be sure to ask Airco Heating and Air Conditioning for a free estimate. Whether it’s a new installation or routine service, our factory-trained technicians provide the expertise your comfort depends on. And at Airco Heating and Air Conditioning, we repair all makes and models.

If you are replacing your air conditioning system, make sure that the unit is the proper size for your needs and that all ducts are sealed at the joints. A unit that is too big will cycle on and off frequently, resulting in poor moisture removal, particularly in areas with high humidity. Also make sure that your new system is designed to manage condensation effectively.
An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]
An air conditioning system's SEER is especially important if you live in a climate that changes temperature dramatically. The SEER is determined by the cooling output during the winter divided by its electric input during the winter. The higher the rating, the more efficient it will be. In January of 2006, the U.S. put standards in place for cooling units which are still in effect today. They must have a minimum SEER of 13. So, if you live in a home with a system installed before the new standards went into effect, consider having it replaced. SEER 13 units increase home efficiency by 30 percent.

Compressor -- Compressors are outdoor components in your system. The compressor is the pump that circulates the refrigerants through the air-conditioner. You can hear it when it's running so you'll know if it's working just by listening. If it starts getting louder, your compressor is about to fail. If it makes no sound when it should be on, it has already failed. Compressors fail for a number of reasons. Most often they fail due to strain from another failed part such as the fan motor. Electrical storms can also damage compressors. If the sound from the compressor gets louder or if you see a decrease in performance, you should have your compressor checked. A failed compressor will not heat or cool your house.
You can adjust for seasons: During the summer, you can have the air conditioner stay off during the cooler morning hours and start cooling the house as everyone gets up and starts moving around. During the winter, you can have your heater stay off while you are away at work and turn on about a half hour or so before you get home so that you are coming home to a nice, warm house.
Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.
I was able to get a next day appointment with them last week after multiple other providers did not have availability. The tech was on time and did a good job to diagnose and eventually replace the circuit board and get it up running again. The service itself would be 5 stars, although it did take a week to complete the job due to ordering the part.
The EPA is so far behind on useful knowledge because of the lack of funding so don't be mislead. The Hvac old timers were left at the dock so to speak and missed out on the IAQ movement. The ones that are savvy and up to date on the information do Air Duct Cleaning, even tho that will lead to a few less service calls its the right thing to do for their customer. Please take a look into a return duct that has never been cleaned, I dare anyone to say it does not need to be cleaned.
My Carrier furnace occasionally (one-two times a day) does not start. It shows error code 15 ("BLOWER MOTOR LOCKOUT -This status code indicates the blower failed to reach 250 RPM or the blower failed to communicate to the variable speed furnace control within 30 seconds after being turned ON in two successive heating cycles."). However, when I turn off and on the furnace power switch it starts and runs fine for a while. Sometimes it runs fine all day, but does not start only once in the evening or in the night. It is 13 years old I was thinking to replace whole thing if repair cost is too high. But I am not ready to pay $10,000. 
WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.
Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
Yes, ducts can look terribly dusty. However, that dust will not become aerosolized during the normal operation of your furnace. There is an easy way to test this. Rent a particle counter and test the air flowing out of your registers before and after cleaning. You will not see any improvement in the air quality or any reduction in the airborne dust level. Think of it this way. Duct cleaning companies tell you that you need to clean your ducts when you can see a layer of dust in your ducts. Yet that very layer of dust is proof that duct cleaning is unnecessary, because that dust proves that the air movement in your furnace is not fast enough to re-aerosolize the dust.

I just had my Air ducts “cleaned”. The person who came to my house works for an air duct cleaning company who uses a professional vacuum. He said the company would charge me about $900 but he can do it aside on his own and charge me half of that. However, when he came over the house, he brought the rotary brush along with his domestic vacuum cleaner that it’s hose was about 5 feet long, I ask him that the wasnt strong enough to pull dust out, and he said, it’s similar to what companies use. I was in doubt and he didnt cover the vents so im thinking all dust must have come out from every air vents. Could this vacuum have taking the debris out of the air ducts? Or how can I myself find out if the inside of the air ducts have been cleaned and no debris is sitting there? I have dust all over my house.
Is there a such thing as a PQ-15 valve? No…but how do we know? And oh, by the way, there are only two types of line-sets: 3/4 inch, and 7/8 inch. All modern equipment runs on a 7/8 inch line-set, so the only time they’ll have to change something is if you have antiquated 3/4 inch line-set from the 60’s or 70’s. I’m digressing though…the point is that they can easily prey on uninformed consumers…like you, baby bird! Don’t worry though…you’ll be flying by the end of this article.
Our unit is 16 years old and we've had it checked out recently since it seems to be running excessively. Over all the tech says it is putting out well; it's the correct size, we have no shade and we've been having extreme heat with high humidity. The info you provided is very helpful and will help us make an informed decision when the time comes. Thank you so much.
My Carrier furnace occasionally (one-two times a day) does not start. It shows error code 15 ("BLOWER MOTOR LOCKOUT -This status code indicates the blower failed to reach 250 RPM or the blower failed to communicate to the variable speed furnace control within 30 seconds after being turned ON in two successive heating cycles."). However, when I turn off and on the furnace power switch it starts and runs fine for a while. Sometimes it runs fine all day, but does not start only once in the evening or in the night. It is 13 years old I was thinking to replace whole thing if repair cost is too high. But I am not ready to pay $10,000. 
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.
Ok what you said is true but in most cases ducts are in a duct flex format, and knowing that the dust in people's flex duct is just surface dust, any real debris that are in the duct itself will result in very little to no air flow which will keep your unit from performing properly, but if it is true allergy reasons then replacing your duct system is better for overall better air quality, plus if you do pay attention to the warranty on flexible duct is that it only has a 10 year warranty and typically only lasts for 20 years so do your research before having a duct cleaning, and to add one more thing if your duct work is completely metal and you can't see visible insulation then your duct on the inside has insulation inside of it, if you replace that with duct work that is clean metal on the inside and wrapped with insulation on the outside then it will further reduce the air bourne fiberglass and dust.
A small number of products are currently registered by EPA specifically for use on the inside of bare sheet metal air ducts. A number of products are also registered for use as sanitizers on hard surfaces, which could include the interior of bare sheet metal ducts. While many such products may be used legally inside of unlined ducts if all label directions are followed, some of the directions on the label may be inappropriate for use in ducts. For example, if the directions indicate "rinse with water", the added moisture could stimulate mold growth.

An air conditioning system, or a standalone air conditioner, provides cooling and humidity control for all or part of a building. Air conditioned buildings often have sealed windows, because open windows would work against the system intended to maintain constant indoor air conditions. Outside, fresh air is generally drawn into the system by a vent into the indoor heat exchanger section, creating positive air pressure. The percentage of return air made up of fresh air can usually be manipulated by adjusting the opening of this vent. Typical fresh air intake is about 10%.

Air duct cleaning service providers may tell you that they need to apply a chemical biocide to the inside of your ducts to kill bacteria (germs) and fungi (mold), and prevent future biological growth. Some duct cleaning service providers may propose to introduce ozone to kill biological contaminants. Ozone is a highly reactive gas that is regulated in the outside air as a lung irritant. However, there remains considerable controversy over the necessity and wisdom of introducing chemical biocides or ozone into the duct work.
×