The number of years an HVAC system lasts depend on the type and brand of components that make up your system. The lifespan of an air conditioner averages between 15 and 20 years. The life expectancy of a tankless water heater is approximately 20 years, while a storage water heater is closer to 10-15 years. Ducts may need replacing within 10-15 years. Your equipment will have a longer life if you have regular tuneups and maintenance to keep everything in good working order. If you’re having repair problems and your HVAC system is over 10 years old, it’s a good time to consider the costs and benefits of repairing vs. replacing. Energystar.gov provides the following tips to help you decide whether to repair or replace:


#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
Though this installation is not always complicated, it's best to work with an air conditioning contractor to ensure it's done correctly. Permits are usually required for this type of work and can be obtained by a state-licensed contractor. You should not attempt to install central air conditioning on your own since you need a license to handle the refrigerant chemicals (Freon) involved.
I was told that 15 out vents would be cleaned and one main vent. the guy came over and gave me an estimate of $500. I had acquired a groupon for $49. the guy said just doing the out vents and one main vent would accomplish nothing. Now I am in dispute with the groupon people for a refund which they won’t give and have to go ahead and waste the money and let them do it. Is their doing the 15 outvents and one main one going to accomplish anything?
If not properly installed, maintained and operated, these components may become contaminated with particles of dust, pollen or other debris. If moisture is present, the potential for microbiological growth (e.g., mold) is increased and spores from such growth may be released into the home's living space. Some of these contaminants may cause allergic reactions or other symptoms in people if they are exposed to them. If you decide to have your heating and cooling system cleaned, it is important to make sure the service provider agrees to clean all components of the system and is qualified to do so. Failure to clean a component of a contaminated system can result in re-contamination of the entire system, thus negating any potential benefits. Methods of duct cleaning vary, although standards have been established by industry associations concerned with air duct cleaning. Typically, a service provider will use specialized tools to dislodge dirt and other debris in ducts, then vacuum them out with a high-powered vacuum cleaner.
These are the prices for a proper installation from a professional – as a word to the wise, HVAC systems require fine tuning and the custom fabrication of parts during installation to work properly, otherwise they will likely fail prematurely. But there are plenty of people who will do it for cheaper than this, using substandard, used, or stolen equipment (stolen from construction sites and new housing developments). Or, they are using unskilled laborers with no experience, etc. But HVAC is not a “we’ll figure it out trade;” there is a right way and a wrong way to do things. There are just too many predatory companies out there, so be careful. I’d highly recommend not skimping on your HVAC contractor. If you go cheap, you will typically pay more in the long run...and in California, that will be a lot!
The heat pump gained popularity in the 1950s in Japan and the United States.[13] Heat pumps can extract heat from various sources, such as environmental air, exhaust air from a building, or from the ground. Heat pumps transfer heat from outside the structure into the air inside. Initially, heat pump HVAC systems were only used in moderate climates, but with improvements in low temperature operation and reduced loads due to more efficient homes, they are increasing in popularity in cooler climates.
Vinick calls air duct cleaning an essential part of home maintenance, akin to mopping and vacuuming. "It’s like changing the oil in your car,” he says. “If you don’t change the oil, you’re going to have a problem. When your components are loaded up with debris, the system has to work harder. When you remove that debris, you get energy consumption savings.”
If you want to get some of the dust and debris out of your ventilation system, you can mix household cleaners like bleach with water, dip a cloth in the mix and then the wipe out the system. This will remove a layer of the spores, which could increase the quality of air a bit and help with the flow of air throughout the house until a pro can come out.
I to had an odd layer of white'ish dust building up especially during seasonal periods when the HVAC ran a a lot. I carefully swept up the fine dust into a small pile and had it analyzed. Turns out it was very fine fiberglass powder dust. It turns out it is the insulation form the attic! (My attic has blown in insulation). Turns out if you (I) had small gaps around my HVAC registers in the ceiling whee the airs blows into the room. What occurred in my case was that the exiting air at that seam creates a vacuum effect at the grate vent cover and draws and then blows fine insulation dust from the attic into the house. Removing each register grate and sealing each tin outlet gap with calking between the dry wall ceiling and tin fixed the issue. A couple were so bad with bowed gaps I had to screw down the bowed tin to the attaching stud better. Checking the very same glass top desk that catches and shows any dust accumulation now shows only very small amounts of normal house dust build up over several weeks. A big, big improvement. You might have a look by simply removing a couple vent covers yourself.
I took off stars for two reasons. Minus one star for issues trying to use the $50 for $25 voucher I purchased through Yelp. Although there was no minimum stipulated, the office wouldn't take it for the initial $59 diagnostic fee. If I used the 10% off First service that they offer, then they won't let me use the voucher on the actual repair bill.  I was stuck with paying the full $59 diagnostic fee.
Had our ducts cleaned late April, 2016. Sodium Chlorite was sprayed into ducts after cleaning. Ever since, we have been bothered with eye and nasal passage irritation because of a “chemical” and “musty” odor. This odor is present whether or not a/c is on.) We are told the sodium chlorite (“EnviroCon, manufactured by Bio-Cide International) is used in hospital and nursing home settings and is not hazardous to health. The air duct company’s suggestion is that they come out and spray even more sodium chlorite…we absolutely don’t want this done! Have had various other recommendations about what we need to have done to remedy our problem. We will be unable to stay in our home if a resolution cannot be found. We’d be willing to replace the ductwork if necessary. (One professional suggested that the cleaning may have “knocked something loose” inside the ductwork and that is the source of the irritant.) This home was built in 1920…no idea when the present ductwork was installed. Any suggestions would be appreciated.
Duct system installation and repairs affect HVAC installation cost. If you’re installing a new forced air heating or cooling system, your home must have ductwork – if you don’t have ducts installed, a new duct system will need to be designed and installed. Your existing duct system may require air sealing to eliminate air loss, helping your new heating and cooling system operate efficiently.
I hired duct cleaning company out of "Service Magic" website. I did not realize the name of his company was Duck cleaning of Central Florida...that should have given me a hint.. The guy did a very poor, incomplete job, and ruined a closet full of clothes when he sprayed up to clean a vent instead of taking it down and cleaning it outside. He left me with more than 1/2 dirty vents and ducts, did not do the air handler in the garage and failed to fog the system. He spent 6 useless hours at my residence and now his insurance is denying coverage..very disappointed in Service Magic....
The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.
Excalibur Water Systems helps solve the water challenges around the globe with water solutions for any possible water concerns in: water hardness, filtration of any contaminant, bacteria removal and high purity water needs and also comes with a warranty of up to 20 years at no extra cost. The best warranty for the water treatment equipment industry.
Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.
Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.

Be careful with HVAC change-outs.  Change-outs are only about 15-20% of the HVAC installation industry. Decrease HVAC installation cost by investing in new ductwork now if needed. Your ducts wear out too, and make sure that your ducts are in fantastic shape if you do this. Many contractors push this because it’s easy and cheap for them, with good pay-off. Do your research and replace them if you need to in order to avoid doing it later, as well as avoid potential health hazards from using old, broken ductwork.
Chemical biocides are regulated by EPA under Federal pesticide law. A product must be registered by EPA for a specific use before it can be legally used for that purpose. The specific use(s) must appear on the pesticide (e.g., biocide) label, along with other important information. It is a violation of federal law to use a pesticide product in any manner inconsistent with the label directions.
I think that the coding and permit industry is a joke!! They will not allow the homeowner to apply for the permit it has to be the licenced contractor. It would make since to allow the homeowner to apply for this. But it is all about money!! They really don't care if its up to code because if they did then they wouldnt care who applied and payeed for it, but they want the contractor to do it so if they do something wrong they can fine them instead of just pointing it out and allowing them to do it right.
Engineers have pointed out some areas where efficiency of the existing hardware could be improved. For example, the fan blades used to move the air are usually stamped from sheet metal, an economical method of manufacture, but as a result they are not aerodynamically efficient. A well-designed blade could reduce electrical power required to move the air by a third.[28]
Despite Bergendahl's experience, Vinick says NADCA's certification standards have improved the situation. "A lot of [service companies] weren't going about it the correct way," he says. “We have an anti-fraud task force, and we’ve gone after some fraudulent duct cleaners with the help of state attorneys general.” He suggests that in addition to NADCA membership, homeowners make sure their cleaners are an established business, have appropriate insurance and are registered to do business in their state and locality.
I originally took off one star because of the SNAFU with getting the part ordered.  When Alberto called me on the phone he admitted the person had "gotten busy with other things" and apologized.  THAT was taking the high road and I was impressed by that.  Sadly, for reasons I won't guess at, Alberto has decided to take the low road in his comments and imply that they got the part as quickly as possible.  Well, we called at 2:30 so did someone spend six and a half hours finding the part??  That seems very doubtful.
He proceeded to clean each heat register by removing the grille and blasting it with an air pressure hose toward the duct opening thinking that the dust would magically be sucked inside. In one room this caused a ceiling smoke detector to go off because the excess dust fooled it into thinking there was smoke. I put my hand in front of a register he wasn’t working on and could hardly feel a suction. Although we discussed how I open and close damper doors, I realized later that he never checked, opened or adjusted them during the cleaning. He could have closed all but the one he was working on in order to increase suction results. His next step was to blast air into the duct and then attach a “squid-like” device that slapped around inside the duct as far as he could reach. This is important! In a newer house, ducts have long straight runs from the furnace. In older houses like mine they can turn and twist. In fact, the duct we have a problem with runs straight up from the basement inside a wall and turns 90 degrees into a soffit for three feet then into two 90 degree turns to get into the floor joist area for another two feet and finally a 90 degree turn up to the second floor register. When he cleaned this one he could only get three feet into the register with the hose or squid because of the turns. That was the case with most. Hardly what could be described as a decent cleaning.
The Environmental Protection Agency says that “duct cleaning services typically – but not always – range in cost from $450 to $1000 per heating and cooling system, depending on the services offered, the size of the system to be cleaned, system accessibility, climactic region, and level of contamination” and type of duct material. Consumers should beware of air duct cleaning companies that making sweeping claims about the health benefits of duct cleaning – such claims are unsubstantiated. Consumers should also beware of “blow-and-go” air duct cleaning companies. These companies often charge a nominal fee and do a poor job of cleaning the heating and cooling system. These companies may also persuade the consumer into unneeded services with and/or without their permission. (If you have knowledge of a practicing “blow-and-go” air duct cleaner, contact your local Better Business Bureau to report the company, and your local, federal, and state elected officials to demand legislation.)
I own and live in a mobile home and was told to install a mobile home air condition well I did not want one because the ones for moblie homes are to small,so I install a home air-condidtion and its good for heating and cooling the only thing I do is change is the filter every month or two,What I want to know is how does dirt and dust comes from????
I’m a heating and air conditioning contractor. I’ve been in the trade for over 15 years. I’ve witnessed numerous duct cleaning projects and talked with many duct cleaners. Duct cleaning as it’s usually promoted is a fraud. Most duct cleaners claim to deliver cleaner air. They deliver exactly the opposite. The studies on duct cleaning prove it, including a May 1998 study sponsored by NADCA and the EPA! The stories are compelling, but they can come up with stories that “prove” anything they want. Internet searches are dominated by results from those who are paid to tell you that duct cleaning is worthwhile. Search a little more and you’ll find the truth.
Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
Natural ventilation is a key factor in reducing the spread of airborne illnesses such as tuberculosis, the common cold, influenza and meningitis. Opening doors, windows, and using ceiling fans are all ways to maximize natural ventilation and reduce the risk of airborne contagion. Natural ventilation requires little maintenance and is inexpensive.[19]
A do-it-yourself approach will only scratch the surface because it is hard to reach some of the ventilation running underneath the floor or into the wall. Although it may help in clearing some of the dust and debris, you really need a professional to guarantee your system is truly spotless. The proper procedure involves the use of a powerful vacuum system with multi-brush attachments designed to loosen debris and feed into the suction. Particles are then blown outside of the house or passed through a HEPA filter inside.
I guess, I will start with saying that air duct cleaning is almost never needed. It is not a scam, but it is certainly something that uneducated homeowners get suckered into. In regards to air flow, a well balanced HVAC system should be able to deliver more than enough air flow. If you are not getting good air flow, it's because your system may be out of balance. Additionally, regular cleaning/changing of the air filters will solve about 95% of your problem. Though you would be surprised how many people either a. don't have a filter or b. don't know about it and leave it there for 10+years. a washable one should be cleaned every 6 months(spring and fall) and a disposable one should be replaced every 3-4 months.
You can install the greatest HVAC system ever built, but if your house is not insulated well, it's only going to end up costing you more money. Older homes may have fiberglass insulation that has broken down due to pests, moisture, or improper installation. Spray foam insulation can be damaged by careless repair or modification work or can be improperly installed. If your insulation in compromised, your attempts to save money and be comfortable will be in vain.

PickHVAC Tips: Installing the right size central air conditioner is extremely important. Have a load calculation done to ensure proper sizing. ACs that are too big aren’t as energy-efficient as they should be, and they cycle on and off too much. This creates over-cooling and temperature imbalance. Units that are too small run constantly in very hot weather and can’t keep your home cool. When an air conditioner is properly sized, it runs at optimal efficiency and indoor comfort.
And if you have flex duct and/or fiberglass ductboard in your home- the last thing you want is a big brush or anything abrasive running through it. Even high-pressure air can erode ductboard so I wouldn’t clean it with anything. If it becomes contaminated, get rid of it and install real ductwork. If your ductwork is accessible in the basement – the best thing to do is take it down and manually clean it if it’s full of junk. It’s not going to cost a nickel more to do that than to pay $500-1000 for a ‘duct cleaning machine” AKA big blower and vacuum – to do the job.
PICKHVAC Terms of Use: Some of the products seen on our site are delivered through a relationship with outside suppliers like Networx.com, Google, and others. We may or may not be compensated for purchased you make as a result of our recommendation. This will NEVER affect our opinion of a product or service! PickHVAC is also a participant in the Amazon Services LLC Associates Program, an affiliate advertising program designed to provide a means for sites to earn advertising fees by advertising and linking to amazon.com
One of the difficulties encountered by many air duct cleaning service companies is that their attention is not really on air duct cleaning. For example, many heating and cooling companies offer duct cleaning as a supplemental service, but of course their primary business is installing and servicing heating and cooling equipment. For these companies, air duct cleaning is not always given the attention it deserves and is often done by less experienced employees whose interest is not in duct cleaning but in repairs and installs. And it is almost always done with inferior air duct cleaning equipment. Still other firms (like carpet cleaners) offer a large variety of services and claim to “do everything.” Because of their lack of focus they may not actually be very good at many, if any, of the services they offer. They cannot simply buy an attachment for their carpet cleaning machine and magically become a great duct cleaner.
AC installation in Fort Smith, AR is vital to comfort, safety, and quality of life. The region is infamous for the unbearable heat that can often become debilitating. This is why investing into an AC to improve the overall lifestyle of your family is well worth the cost. Avoid the constant frustration by seeking the assistance of a professional team.
If you’re anything like most of our readers, you’ve spent hours online researching HVAC information in preparation for replacing your old heater or air conditioner. I’m the same way; it’s a big investment! You may want to consider saving yourself some time and money by getting an HVAC-Facts Report from this online HVAC installation cost calculator.  Take a look:
Heating, ventilation, and air conditioning (HVAC) systems have been shown to act as a collection source for a variety of contaminants that have the potential to affect health, such as mold, fungi, bacteria, and very small particles of dust. The removal of such contaminants from the HVAC system and home should be considered as one component in an overall plan to improve indoor air quality.
Well, I had the cleaning done. The handler is definitely much quieter. It was explained to me that with the coils clean, the condensation will be able to sweat off instead of sticking to the dust and dirt, therefore the humidity (lots of humidity in florida) will be removed better. I feel as if it was worth it, but, I will definitely change that filter every 3 weeks or so from now on. I don’t want to pay that cost again.
Indoor Coil -- The indoor coil is a heat transfer device. It absorbs the heat from the inside of the house and passes it on to the refrigerant and is pumped outside. Dust that builds up on the coil can hamper its ability to absorb heat. High heat transference coils use very thin metal. Airborne chemicals can cause corrosion which leads to leaks. The constant vibration of the compressor can also cause solder joints to weaken and leak. An indoor coil may operate for weeks with a tiny leak, and you may not notice the loss in performance right away. As soon as a leak is made known, it should be replaced or repaired immediately.
I thought the price advertised at 129.95 for duct cleaning was great and called to clean our ducts. When they came in to do the the job I could not be home and my wife dealt with them. My wife ended up paying 954.00. They convinced my wife that there was 1.5 inches of mold built up on the Evaporators and coils. It is not the money, my wife could not go to the basement to witness the mold build up or the coil fouling. We have not cleaned our ducts for at least 10 years. The last price we paid for our duct cleaning was 150.00. My concern is that they told my wife not to turn on the heat for 2 hours due the strong chemicals they used to kill the mold. Are these chemicals approved as safe?
PickHVAC Tips: First, see the PickHVAC tip above about sizing a central air conditioner. It applies to heat pumps just as much. Secondly, Even if the line set for the new heat pump is the correct size, we recommend replacing the set or at least the fittings. Old lines and fittings are a major source of leaks. When refrigerant leaks out, the heat pump efficiency suffers. Eventually, the unit stops providing heating and air conditioning, and it might break down.
Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.

I purchased one of those Amazon air duct cleaning coupons for 49.99. When the company showed up, they removed the vent closest to the air intake and immediately told me I needed $1800.00 for all new duct work. They said they could not clean the system until new duct work was installed. I thanked them and said I would give them a call. The only call I made was to Amazon to get a refund. I know I didn’t need new duct work. Be careful to not fall for unscrupulous salesmen and their pitches and scare tactics.

A thorough visual inspection is the best way to verify the cleanliness of your heating and cooling system. Some service providers use remote photography to document conditions inside ducts. All portions of the system should be visibly clean; you should not be able to detect any debris with the naked eye. Show the Post-Cleaning Consumer Checklist to the service provider before the work begins. After completing the job, ask the service provider to show you each component of your system to verify that the job was performed satisfactorily.
×