I am 79 years old, bought a condo & spent a lot of money on it. this winter my first bill was 450.00. had my furnace checked out, which is on the roof. it was old rusted out & leeking oil. i talked to owner & had new unit installed. they came out to clean ducks & they were split & worn out. there is no crawl space because theres a unit above me. my real estate lady or this company will not help me fix this problem.
I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.

Duct cleaning is a band aid, like washing you hands is. Under your description, why wash your hands more than once? If it gets cleaned once, it shouldn't get dirty again. Well that is, unless they touch something dirty. Keeping your hands completely clean is virtually impossible. Same as keeping dust out of your home. You clean your ducts and over a 3-5 year span they get dirty again. Also, duct cleaners are not licensed but should be certified by NADCA(National Air Duct Cleaning Association).
We are a hvac company that provide air duct cleaning service are minimum charge $400 to do a proper air duct cleaning with 2 techs avg 3-6 hours that includes sanitizing. I get phone calls all day about the $99 your not going to get much of a cleaning for that price it for them to get there foot in the door and up sell that the only way for them to stay in business. Just from my 15 years of duct cleaning experience.
Since most states and municipalities don’t license air duct cleaners, you need to check their professional credentials instead, such as NADCA membership. EPA recommends all duct cleaners follow NADCA standards. Member companies must keep at least one technician on staff who has passed a NADCA test. “They have to pass rigorous testing to earn the certificate, and our code of ethics is very important,” Vinick says.

Duct cleaning generally refers to the cleaning of various heating and cooling system components of forced air systems, including the supply and return air ducts and registers, grilles and diffusers, heat exchangers heating and cooling coils, condensate drain pans (drip pans), fan motor and fan housing, and the air handling unit housing (See diagram).

We are all getting migraines several times a month. I have asthma but not ever as bad as it has been and my 2 year olds dr just informed me she potentially has asthma too. We all get sinus infections regularly and eczema and contact dermatitis. None of us have been this way until recently in our apartment. A roof leak with mold was repaired recently mold was sealed off not removed. We also had lead paint removed from a few window trims this year. I wasn’t here to see if they covered the vents. We had mice too. I vacuum everyday we have hardwood floors no one wears shoes past the font door and I’m getting over a cup full of dirt every time I vacuum. Dust on everything daily. White dust. It’s a 4 room apartment with 1 intake. They are filthy from what I can see when I change the filters. The filters are black after a few months. I feel bad to ask the homeowner to get the system cleaned, can’t afford to move (we live in the city & it’s expensive). I am going to try the shop vac to remove what I can. Any experienced hvac people please give your opinion. Should I just get it done and pay for it myself? We have lived here for 13 years. It’s never been cleaned since ive been here. Is it something I can do with a shop vac? Can i use a wet rag to get the powder dust on the inside of the vents off. One vent has what looks like chunks of dry wall or thick paint sitting in the vent and none of the vents screw into the wall, the screws just fall out. No one ever reinforced the area so the wall just basically crumbles. Kind of useless to spend the money on filters since the air and dust just blows out around the sides of the vents and one of the vents just falls right out of the wall when the heat is turned on. I don’t know why the owner doesn’t fix it. He’s been here to replace filters and saw the condition.


Rheem's RRNL features a scroll compressor with fewer moving parts and less noise than traditional reciprocating compressors. A louvered compressor compartment protects the compressor from the elements and from debris that can shorten the life of the compressor. The Classic series continues to be one of their best sellers, with the addition of the Comfort Alert diagnostics module integrated to assist technicians in the event your system needs repair. 2-5 tons, 13 SEER, 80% AFUE.
The EPA is so far behind on useful knowledge because of the lack of funding so don't be mislead. The Hvac old timers were left at the dock so to speak and missed out on the IAQ movement. The ones that are savvy and up to date on the information do Air Duct Cleaning, even tho that will lead to a few less service calls its the right thing to do for their customer. Please take a look into a return duct that has never been cleaned, I dare anyone to say it does not need to be cleaned.

Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. Make sure to shop around and get written estimates first.
Important Tip: Don’t just pay attention to the high-end of the price range! – which is what I know you are all looking at, but also look at the low range. If a contractor is cheaper than this, ask “why?” Usually it is because they don’t have liability insurance, workman’s compensation insurance, are unlicensed, all of the above, or worst yet, they don’t use HVAC technicians. You are spending a lot of money.  Make sure that they are licensed (In California, check here at CSLB License Checker) and insured.
Bigger is not necessarily better when it comes to HVAC systems, and smaller isn't always more efficient. If you have too small of a system, your system will be running constantly as it tries to keep up with the temperature. If you have too large of a system, it won't run long enough to keep up with the humidity. In order to handle both temperature and humidity efficiently, an HVAC system should run for around 30 minutes at a time. If your system is staying on too long or shutting off after only around 10 minutes, you are not getting efficient performance.

I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.

Professional cleaning involves getting the dust and debris outside, so they use outdoor ventilation equipment. It is so important that homeowners make sure the professional contractor is using good equipment then, as they could otherwise spread the spores into the home and further agitate sensitive family members. In the case of mold, a cleaner will only be able to tell you it is there, followed by needing an additional mold professional to come out and test or remove the mold. Air duct cleaning industries do not require state licensing, so make sure to check for a company with references.
Did not realize cost had gone up so much for this service. Two years ago I had furnace and ducts cleaned at my old house and it was under $400. Now the cost is $700 for this house. I will keep looking for someone to offer a lower price, check them out, and have it done. Or will find the paperwork to see who did it before. I liked this article and did learn some things. Thanks.
Lennox, on the other hand, is probably the most expensive unit out there and I can’t stand them.  In our (humble?) experience, they have a horrible logistics chain, making repair parts difficult to come by (sometimes taking weeks), poor customer service, and the parts cost three times as much. That’s not what this article is about, so read more in: Carrier vs. Lennox Furnace Review.
Pay particular attention to cooling coils, which are designed to remove water from the air and can be a major source of moisture contamination of the system that can lead to mold growth. Make sure the condensate pan drains properly. The presence of substantial standing water and/or debris indicates a problem requiring immediate attention. Check any insulation near cooling coils for wet spots.
I hired duct cleaning company out of "Service Magic" website. I did not realize the name of his company was Duck cleaning of Central Florida...that should have given me a hint.. The guy did a very poor, incomplete job, and ruined a closet full of clothes when he sprayed up to clean a vent instead of taking it down and cleaning it outside. He left me with more than 1/2 dirty vents and ducts, did not do the air handler in the garage and failed to fog the system. He spent 6 useless hours at my residence and now his insurance is denying coverage..very disappointed in Service Magic....
Most organizations concerned with duct cleaning, including EPA, NADCA, NAIMA and the Sheet Metal and Air Conditioning Contractors' National Association (SMACNA) do not currently recommend the routine use of sealants to encapsulate contaminants in any type of duct. Instances when the use of sealants to encapsulate the duct surfaces may be appropriate include the repair of damaged fiber glass insulation or when combating fire damage within ducts. Sealants should never be used on wet duct liner, to cover actively growing mold, or to cover debris in the ducts, and should only be applied after cleaning according to NADCA or other appropriate guidelines or standards.
I think that the coding and permit industry is a joke!! They will not allow the homeowner to apply for the permit it has to be the licenced contractor. It would make since to allow the homeowner to apply for this. But it is all about money!! They really don't care if its up to code because if they did then they wouldnt care who applied and payeed for it, but they want the contractor to do it so if they do something wrong they can fine them instead of just pointing it out and allowing them to do it right.
Here in Frisco, TX…just had a tech come out to clean vents. I used a 30 bucks groupon for “complete vent cleaning”. He told me I have 3 AC units and groupon covers only 1. I told him to do the unit upstairs where the kids sleep. He decided on his own to do the downstairs unit. I yelled at him why he is not doing the unit I told him to do! He said they are all connected. I will clean two for you for the price of one… Oh really?
Consider what kind of heating and cooling system you want installed for the square footage of your home. Do you want a full system with a thermostat or a specific machine for the summer like a swamp cooler? Do you need a new furnace just for the winter? For any of these projects, the cost will vary depending on the quality, style and machine size you choose. If you have a tight budget, think of going smaller and upgrading over time. For example, if you can't afford to convert your entire home to solar power, you may want to consider only utilizing it to heat your water. Some other types of heating systems are:
The sky is the limit. I am a big fan of adding zoning systems, but realize that this will typically add $2,300 to $3,500 (or more) to the price. “Why a price range, isn’t it just a part?” No, the part then has to be installed, and the customized ductwork required will vary based on the difficulty of the job and layout of your attic. It is very labor intensive, and most people don’t do it right. It should also include a bypass damper and ductwork! Simply put, the more you add, the more it will affect your HVAC installation cost.
Unfortunately, manufacturers and contractors don’t publish this information…it’s a secret. Why? Who knows…but we have access to a full contractor pricing database of 1,000’s of different units in our online HVAC installation cost calculator, so let’s choose one for our example calculation. We’ll go with Carrier equipment, since our readers always bother us about them (despite us telling them that they are overpriced):
I recently replaced my 44 year old furnace. Over the years we have had several construction projects inside the home. For many years breathing the heated air from the duct work caused excessive sneezing, sinus issues, and lung irritation. . The heat smelled like dust. To maximize air quality I added a humidifier, MERV-11 filter, and UV light onto the new furnace. To further improve air quality, I had the ducts cleaned and sanitized. I took before and after pictures of the inside of each return and output duct. They were filthy before, and sparkling clean and fresh after the procedure. Now when running the system, clean sanitized air flows through my whole house. A huge difference. It will make sleeping and being indoors during the winter months far more tolerable. I use window air conditioners, and run the system in the summer to keep the house air clean and fresh on hot summer days too. It works! Great decision!
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
HVAC is an important part of residential structures such as single family homes, apartment buildings, hotels and senior living facilities, medium to large industrial and office buildings such as skyscrapers and hospitals, vehicles such as cars, trains, airplanes, ships and submarines, and in marine environments, where safe and healthy building conditions are regulated with respect to temperature and humidity, using fresh air from outdoors.
I took off stars for two reasons. Minus one star for issues trying to use the $50 for $25 voucher I purchased through Yelp. Although there was no minimum stipulated, the office wouldn't take it for the initial $59 diagnostic fee. If I used the 10% off First service that they offer, then they won't let me use the voucher on the actual repair bill.  I was stuck with paying the full $59 diagnostic fee. 

Yes, ducts can look terribly dusty. However, that dust will not become aerosolized during the normal operation of your furnace. There is an easy way to test this. Rent a particle counter and test the air flowing out of your registers before and after cleaning. You will not see any improvement in the air quality or any reduction in the airborne dust level. Think of it this way. Duct cleaning companies tell you that you need to clean your ducts when you can see a layer of dust in your ducts. Yet that very layer of dust is proof that duct cleaning is unnecessary, because that dust proves that the air movement in your furnace is not fast enough to re-aerosolize the dust.
We moved to a house built in 1965 from a 1915 house with a dirt basement. Against what I anticipated, the 1965 house was much dustier. It was like felt on top of everything. I cleaned and cleaned and it did become less dusty over time. We then found out a cat lady with over 2 dozen cats lived in the house in the past. We then had to get our furnace replaced and I was able to look down some of the duct work, the dirt and debris was 3-5 inches deep. Additionally, the basement ducts were entirely plugged with debris including dirt, seeds, ants, toys, etc. I had already removed what I could from those. We had our ducts cleaned last year, and the dust in the house is greatly reduced. Also have lost the runny nose I got after moving here. There are duct cleaning con artists out there, but ours did a good job.
If you are using existing ducting, it will have to be inspected. Proper ducting loses around 2% to 5% of your energy. Old, leaking ducts can lose 50% or more. A contractor will need to have the ducts inspected and replace any parts ahead of time. If you are changing the size of your HVAC system because of significant changes to your home, you might need to replace the ductwork regardless.
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.
I need a complete system replacement , before I was trying to get an evaporator coil replaced , of course the price is between $2200 an $2800 , then get told it probably will over tax my ac unit within months , so now and like everyone else what do you buy 14 ,15 16 17 seer units ,price and how do we know its reasonable  why can't there be '" a estimated price ,in the ball park, a range of prices ,so we can at least go from their .....  Now it's from 7500 to 15000. Frustrating  from the start so everybody good LUCK.   Draw a # from the hat    Unregulated  and who do you BELIEVE, just like on NCIS go with your gut feelin   
#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
Internal insulation provides better acoustical (noise) control. Flexible duct is very low cost. These products are engineered specifically for use in ducts or as ducts themselves, and are tested in accordance with standards established by Underwriters Laboratories (UL), the American Society for Testing and Materials (ASTM), and the National Fire Protection Association (NFPA). Many insulated duct systems have operated for years without supporting significant mold growth. Keeping them reasonably clean and dry is generally adequate. However, there is substantial debate about whether porous insulation materials (e.g., fiber glass) are more prone to microbial contamination than bare sheet metal ducts. If enough dirt and moisture are permitted to enter the duct system, there may be no significant difference in the rate or extent of microbial growth in internally lined or bare sheet metal ducts. However, treatment of mold contamination on bare sheet metal is much easier. Cleaning and treatment with an EPA-registered biocide are possible. Once fiberglass duct liner is contaminated with mold, cleaning is not sufficient to prevent re-growth and there are no EPA-registered biocides for the treatment of porous duct materials. EPA, NADCA and NAIMA all recommend the replacement of wet or moldy fiber glass duct material.
×