I own a small mechanical company. My main work is service and system replacements. I have never been a believer in duct cleaning. The company I worked for before had our duct man come out and do my house. I saw no difference. Preventive maintance is what I recomend. Remove fan and clean, seal fan compartment to prevent dust from being pulled in, filters I install media filters, they are 5″ thick and pleated. I have tested them to make sure static presure was not a issue. Heat exchangers and AC coils need to be cleaned. I will tell you this to do a good cleaning I usually spent 1-2 hrs, When I’m finished I would not have a problem eating my diner on the system. Good filters, clean system and properly tuned up are my recomdation to anyone. I’ve included my email feel free to contact me with any questions. winkcfd@yahoo.com
While your HVAC filter is designed to trap particulate matter and prevent it from entering your air ducts, particles often still get through. The number of particles your HVAC filter traps is directly connected to the quality of air in your home: the lower the quality of air, the more particles will be present, and the more particles are likely to get through the filter. If these particles are allowed to build up, your HVAC system can become less efficient, operating longer to heat or cool your home. An inefficient HVAC system can result in inconsistent heating or cooling, higher utility costs, and expensive HVAC unit repairs, such as an A-coil or blower motor replacement if the problem is left unchecked. Air duct cleaning from Sears, which focuses on the dirt in your air ducts, can boost the efficiency of a dirty HVAC system, cleaning out the particulate matter that can hinder HVAC effectiveness and affect your health.
I'd have to disagree with all of your statements. Not only are they derived from no experience in the field, you are missing keys facts. Ducts even if air tight will get dirty. If they are not getting dirty, it means they are not working. Your returns side of the duct work is always under negative pressure when the system is operational.Therefore it is always drawing air in. Seeing how dust is made up mostly from dead skin humans shed daily. Around 1.6 Pounds of skin a year per human. Living in your home anything that is air born will be drawn back towards the cold air returns. That is what they are designed for, to draw stale air back to the system to be filtered and sent back through the house.Homes with carpet will actually have cleaner duct work than home with all tile or hardwood. This is because carpets hold onto dust particles and you vacuum them up. Whereas on hardwood or tile, dust can run freely back to the returns. Even if a duct system was sealed 100%, which is next to impossible to achieve 100% would still need to be cleaned. The cleaning may only have to be every 7-10 years for example. Most homes require every 5-7 years. And that's if it was done properly the first time. If you constantly hire people that have no or minimal knowledge of duct cleaning, You home would require cleaning more often. Every 2 years. That's a trade secret, The longer they recommend before the next cleaning, the odds are they did it right. That's not to say there aren't people that lie, because there are. Just have your duct cleaner take pictures before and after cleaning. Not just an outside view. Get in there, picture entire joist liners, Whole main runs and even long round pipes. Also it helps to have a company that guarantees their work. If it's not done right, they will come back and do it until it is. Most companies that do this make sure it is right the first time. Your not getting paid to do the job twice.
When these aren't properly maintained and sanitized, they can build up dust, pollen, and even mold. This means when the air conditioner or heater turns on, the spores are released into the air for you to inhale. While some are less harmful, people who have allergies or sensitivity to certain spores will react negatively. Plus, mold is dangerous for anyone to ingest and should be avoided by regular maintenance.
Some of the research I have done suggests to have your ducts cleaned when you first purchase a new home to remove drywall dust. Maintain your system well and you shouldn't have to do it again until you want to sell. Those are the two times cleaning was suggested. So for peace of mind maybe it is a good idea to do it even if you buy a used home and then maybe every 5-10 years.
The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.

I was told that 15 out vents would be cleaned and one main vent. the guy came over and gave me an estimate of $500. I had acquired a groupon for $49. the guy said just doing the out vents and one main vent would accomplish nothing. Now I am in dispute with the groupon people for a refund which they won’t give and have to go ahead and waste the money and let them do it. Is their doing the 15 outvents and one main one going to accomplish anything?
SEER is useful for comparing one model to another much in the same way that a car's calculate MPG is useful. It's not an accurate prediction of exactly how efficient the system is, but it can tell you which one is more efficient. Also, since SEER is based on a "cooling season", what region you live in will determine how long or short your cooling season is.
If you’re anything like most of our readers, you’ve spent hours online researching HVAC information in preparation for replacing your old heater or air conditioner. I’m the same way; it’s a big investment! You may want to consider saving yourself some time and money by getting an HVAC-Facts Report from this online HVAC installation cost calculator.  Take a look:
Important Tip: Don’t just pay attention to the high-end of the price range! – which is what I know you are all looking at, but also look at the low range. If a contractor is cheaper than this, ask “why?” Usually it is because they don’t have liability insurance, workman’s compensation insurance, are unlicensed, all of the above, or worst yet, they don’t use HVAC technicians. You are spending a lot of money.  Make sure that they are licensed (In California, check here at CSLB License Checker) and insured.
With today’s consistently rising energy costs, improperly sealed windows, ductwork, and poor insulation can pose serious problems for many home and business owners in Arkansas. Wilson's Heating & Air Conditioning provides complete HVAC system servicing including sales, installation, maintenance and repair, and offers numerous practical solutions that will reduce your energy costs.
HELP is am drowing in LENT . It has been noticed in the master bedroom there is lent all over the furniture and the floors. I have dark brown/black furniture and same for the wooden floors. There are wods of lent every day. My furniture covered in lent. The rest of the house is fine just the tipical dust. I am sure my lungs are also full of lent. I looks like if my dryer vent was in my bedroom. Please help
An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.
#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
For more than 60 years Stanley Steemer has been perfecting our hot water extraction method to clean carpet with unparalleled results. Take control of the environment in your home and enjoy a cleaner, healthier living space for your family. Every carpet cleaning is Certified to remove an average of 94% of common household allergens. We remove the dirt you can see and the allergens you can't. 
Is duct cleaning worth it? There is not a yes or no answer that suits everyone. On an Air Force base, the system was not air tight and there was leakage around the filters. The system got dirty. A professional company was called out. The Duct was big enough that a technician could go inside the metal duct and clean it. There was a new Air Handler installed and things were sealed up better. in this case it was worth it.
Fast forward 1 year and 1 week and the circuit board that HVAC Service had installed has failed again. They came out and said that it failed from water condensation dripping onto it, so we needed to replace it and reroute the pipes to prevent future water damage.  That would cost double what I paid last year.  Why didn't they fix the problem last year at the initial repair instead of putting in a circuit board that was bound to fail again?!? They were strongly recommending that the furnace be completely replace for a huge fee to avoid the same thing happening again.  I paid $59 for them to tell me they didn't fix it right last year. This didn't feel right, so I sought a second opinion.
Energy efficiency can be improved even more in central heating systems by introducing zoned heating. This allows a more granular application of heat, similar to non-central heating systems. Zones are controlled by multiple thermostats. In water heating systems the thermostats control zone valves, and in forced air systems they control zone dampers inside the vents which selectively block the flow of air. In this case, the control system is very critical to maintaining a proper temperature.

In modern buildings, the design, installation, and control systems of these functions are integrated into one or more HVAC systems. For very small buildings, contractors normally estimate the capacity and type of system needed and then design the system, selecting the appropriate refrigerant and various components needed. For larger buildings, building service designers, mechanical engineers, or building services engineers analyze, design, and specify the HVAC systems. Specialty mechanical contractors then fabricate and commission the systems. Building permits and code-compliance inspections of the installations are normally required for all sizes of building.

Demonstrate visible evidence of microbial growth in your duct work. Some service providers may attempt to convince you that your air ducts are contaminated by demonstrating that the microorganisms found in your home grow on a settling plate (i.e., petri dish). This is inappropriate. Some microorganisms are always present in the air, and some growth on a settling plate is normal. As noted earlier, only an expert can positively identify a substance as biological growth and lab analysis may be required for final confirmation. Other testing methods are not reliable.


I'd have to disagree with all of your statements. Not only are they derived from no experience in the field, you are missing keys facts. Ducts even if air tight will get dirty. If they are not getting dirty, it means they are not working. Your returns side of the duct work is always under negative pressure when the system is operational.Therefore it is always drawing air in. Seeing how dust is made up mostly from dead skin humans shed daily. Around 1.6 Pounds of skin a year per human. Living in your home anything that is air born will be drawn back towards the cold air returns. That is what they are designed for, to draw stale air back to the system to be filtered and sent back through the house.Homes with carpet will actually have cleaner duct work than home with all tile or hardwood. This is because carpets hold onto dust particles and you vacuum them up. Whereas on hardwood or tile, dust can run freely back to the returns. Even if a duct system was sealed 100%, which is next to impossible to achieve 100% would still need to be cleaned. The cleaning may only have to be every 7-10 years for example. Most homes require every 5-7 years. And that's if it was done properly the first time. If you constantly hire people that have no or minimal knowledge of duct cleaning, You home would require cleaning more often. Every 2 years. That's a trade secret, The longer they recommend before the next cleaning, the odds are they did it right. That's not to say there aren't people that lie, because there are. Just have your duct cleaner take pictures before and after cleaning. Not just an outside view. Get in there, picture entire joist liners, Whole main runs and even long round pipes. Also it helps to have a company that guarantees their work. If it's not done right, they will come back and do it until it is. Most companies that do this make sure it is right the first time. Your not getting paid to do the job twice.

Equipment used to clean ducts varies widely. The cheaper the equipment used the more you are just wasting money. This is why it's typically not worth doing. In some situations it may be beneficial, but only after determining and investigating the duct system. This should be done by a licensed HVAC contractor and not a duct cleaner that typically do not hold and HVAC license. (Duct cleaners aren't required to be licensed in HVAC in many areas.)
The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.
The average cost of keeping your residential ductwork orderly is going to vary greatly from that of a commercial building. This is because commercial air ducts are often larger and more extensive. Residential cleanings can cost an average of about $20-$30 per vent. For commercial buildings, service providers must do an estimate of your space before they can provide an accurate quote. Before factoring in the materials and the number A/C and furnace units, you can expect a commercial project to cost at least $35-$50 per hour.
My 48 yr old house (mine for the last 4 yrs) has considerable dust in the return plenum (fiber duct). I’m remodeling and recently re-sealed the return plenum AND the site-fabbed transition built when the new unit was installed, 2013. The return was leaky no doubt drawing musty, dusty air from the crawl space due to the Red-Neck fab & seal job! Pitiful craftsmanship! It took me 7 hours to fix the new transition piece. Anyway, the dust in the house is the same “color” as whats in the return duct and I’m getting way too much & too often in the house. I’ve also cleaned my coils, which were not that dirty.

My vent covers have lots of mildew. They look bad! I live in a very humid climate in a condo. The handyman here has offered to take those down, wash them, sand, & then spray paint them with a mildew resistant paint. He said that he will leave them off overnight to dry. I am wondering if this is safe to breath the AC blowing out into the open all night??. ! Guess it is better than the mildew!?
My father started in the business of home comfort back in 1968, an I around 1986. We still don't have a duct cleaning machine. I am sure there are always applications for all tools in this industry. However I missed where anyone talked about where dust even comes from..........We do not have these little dust machines sitting in a corner puffing out little clouds of dust....soooo where does it come from?
Your contractor will do a load calculation to determine the proper central air conditioning unit for your home. This calculation accounts for the climate, size, shape and orientation of your home, as well as its square footage. A professional will also look at the insulation, windows, walls, floors and other materials that compose your home. He/she will then examine any leaks, seals and existing ducts or vents.
And if you have flex duct and/or fiberglass ductboard in your home- the last thing you want is a big brush or anything abrasive running through it. Even high-pressure air can erode ductboard so I wouldn’t clean it with anything. If it becomes contaminated, get rid of it and install real ductwork. If your ductwork is accessible in the basement – the best thing to do is take it down and manually clean it if it’s full of junk. It’s not going to cost a nickel more to do that than to pay $500-1000 for a ‘duct cleaning machine” AKA big blower and vacuum – to do the job.
Duct cleaning generally refers to the cleaning of various heating and cooling system components of forced air systems, including the supply and return air ducts and registers, grilles and diffusers, heat exchangers heating and cooling coils, condensate drain pans (drip pans), fan motor and fan housing, and the air handling unit housing (See diagram).
×